My Home System (Simplex 4005)

Post by jm2014 » Sat Jan 20, 2018 5:24 pm

Since my home fire alarm system is almost near completion, I wanted to share what devices are in and what's to come! The alarm panel is a Simplex 4005 and so far it's handling all my additions and seems very stable! I would've preferred an addressable system but my I'm having trouble with my fs-250 and the 4010 is still fried. However the 4005 seems complicated enough to my liking, plus thanks to it's card based layout, I have more flexibility than any addressable panel I own! Some parts are hard to find though, which concerns me a little since it's no longer manufactured new.

So we start out in the main (original) portion of my house.

The fire alarm panel is a Simplex 4005!
Image

The batteries are powered by 2 power sonic PS-1250F1. I should've used 7 or 8 amp hours but I ordered these before I knew that and well, the panel is happy, so ... good enough for me!
Image

The Front keypad, and yes I did take this on January 1, 1995!
Image

The security room/office has a Simplex 4903-9220 horn/strobe.
Image

There is a pull station in the panel room which is a Simplex 4251-20 and there's another 4251-20 outside the office, which is at the front door.
Image

There is a smoke detector above the fire panel per code, I forget the model number but it's the older 2098 series smokes.
Image

Outside the office, there is a Simplex 4903-9219 horn/strobe.
Image

So making our way to the rec room extension, we have a Siemens ZH-MC-W horn/strobe at the exit door. A ZR-MC-W strobe will be added later. All indoor Siemens horn/strobes and strobes are synced together and horns silence-able over 2 wire!
Image
Image

Back towards the renovated dining room, we have a Faraday re branded (Siemens U-MCS) strobe. It was the only closest Siemens strobe I had plus it works with the Siemens sync protocol.
Image

Into the garage extension, we have a two Siemens U-MHU-MCS horn/strobe. The coding has been fixed to Temporal, I lost a jumper so it was stuck on Siemens March Time (called pulse on most systems) so I replaced it with another jumper so it's all good!
Image

Ok, heading outside the garage rear exit door, we have a Siemens AS-WP-HMC-W horn/strobe.
Image

And going around the garage to the front of the house, a Siemens U-MHU-S110 non sync weatherproof horn/strobe, the horn is a little lower than the indoor U-MHU horn/strobes. Due to this horn not sync-able, all outdoor horn/strobes are free run. As far as I know, NFPA doesn't mandate outdoor sync strobes if multiple strobes are not in the same human field of view. This is the only horn/strobe out front. The AS is on the other side facing the backyard.
Image

Back in the house, going upstairs we have a 2099-9754 which I replaced the 4251-20 with. This is the newer version with the key lock that turns right!
Image

Lastly, the device that powers the sync strobes is a Siemens DSC-W.
Image

Additional devices to be added to the system, mostly smokes and heats. I'm really fascinated by this system and what are your opinions on this? Does this seem like a real world situation, have you ever come across something similar?

Thanks for viewing!

jm2014
Casual Participant
Casual Participant
Posts: 199
Joined: Wed Sep 17, 2014 9:59 pm

Re: My Home System (Simplex 4005)

Post by jm2014 » Sat Jan 20, 2018 5:30 pm

I forgot to mention, there is a Simplex 4903-9427 Truealert horn/strobe upstairs in the guest bedroom/laundry room.
Image

Also the 4903-9219/9220/9427 are coded to temporal by a Siemens PAD-3 Distributed Power Supply in the closet located in the Panel Room.

User avatar
SSmassWKmt
Casual Participant
Casual Participant
Posts: 94
Joined: Tue Jul 26, 2016 5:24 pm
YouTube Username: Siren Freak

Re: My Home System (Simplex 4005)

Post by SSmassWKmt » Sun Jan 21, 2018 2:12 pm

Good job! I'd suggest mounting the backboxes with screws? And maybe using conduit/wiremold? Other wise, nice system.
Just livin' the life.

User avatar
jelimoore
Casual Participant
Casual Participant
Posts: 165
Joined: Tue Nov 28, 2017 12:09 am

Re: My Home System (Simplex 4005)

Post by jelimoore » Sun Jan 21, 2018 10:31 pm

Cool system. I really like the mix of Simplex/Siemens stuff.

Just curious, how do you know if you have a newer 2099-9754? I have a 2099-9754 and the keylock turns left which is really quite annoying.

jm2014
Casual Participant
Casual Participant
Posts: 199
Joined: Wed Sep 17, 2014 9:59 pm

Re: My Home System (Simplex 4005)

Post by jm2014 » Mon Jan 22, 2018 1:16 pm

@jelimoore

If you look at the Simplex logo, it uses a different font than what we're used too, I believe it was updated around 2011. Also the key lock turns to the right, which is on newer simplex pulls.

firefreak57
Serious Participant
Serious Participant
Posts: 550
Joined: Wed Dec 07, 2016 10:02 pm
YouTube Username: firefreak57
Location: Northeastern Ohio

Re: My Home System (Simplex 4005)

Post by firefreak57 » Mon Jan 22, 2018 10:11 pm

jm2014 wrote:@jelimoore

If you look at the Simplex logo, it uses a different font than what we're used too, I believe it was updated around 2011. Also the key lock turns to the right, which is on newer simplex pulls.
Depending on how the person in the factory screwed the lock together, it could turn in a different direction. I have a 4251 which I changed the lock out of because it was assembled upside down causing me to have to turn the key upside down, and it got annoying to the point where I unscrewed the lock myself and put it back on the right way so I didn’t have to turn the key around each time. But as long as the lock works, it works. The way the key turns doesn’t necessarily affect the operation.
The official account of firefreak57! Class of 2019.
Proud Owner of a Simplex 4004 Fire Alarm System
My YouTube Channel

User avatar
jelimoore
Casual Participant
Casual Participant
Posts: 165
Joined: Tue Nov 28, 2017 12:09 am

Re: My Home System (Simplex 4005)

Post by jelimoore » Mon Jan 22, 2018 11:51 pm

How do you change the key direction? Mine's the right way up but spins the wrong way around.

jm2014
Casual Participant
Casual Participant
Posts: 199
Joined: Wed Sep 17, 2014 9:59 pm

Re: My Home System (Simplex 4005)

Post by jm2014 » Mon Jan 29, 2018 6:06 pm

Updates to the system as of today. All smokes shown were tested for functionality with real smoke and function properly.


2098-9201 Smoke added to the living room/main entrance walkway.
Image

2098-9441 Heat Detector added above fire prone area in the kitchen
Image

2098-9201 Smoke added to the top of the stairs by bedrooms.
Image

And lastly a siga2-ps smoke added to the dining room. More of these detectors will be added in the garage, rec room, and upstairs bedrooms.
Image

jm2014
Casual Participant
Casual Participant
Posts: 199
Joined: Wed Sep 17, 2014 9:59 pm

Re: My Home System (Simplex 4005)

Post by jm2014 » Sat Feb 03, 2018 12:25 am

My home system will be completed by next Friday! I finally will finish it! The system is by far, the most advanced any home user will ever have.

Here's the lowdown:
The main panel is the EST iO-1000-R. This monitors all addressable devices.
The secondary panel is the Simplex 4005. This monitors all conventional devices.
The SIGA-CT1 monitors the 4005 for an Alarm Condition.

The system will consist of the following devices:

Horns/Strobes:
(2) Wheelock MT-24-LSM
(1) Simplex 4904-9137.
(1) Simplex 4903-9427. True Alert 4 wire.
(1) EST G1RF-HDVM
(1) EST G1RF-VM
(1) Siemens ZH-MC-W
(2) Siemens ZR-MC-W
(1) Siemens AS-WP-HMC-W
(1) Faraday 2700 (Siemens U-MCS)
(2) Siemens U-MHU-MCS
(1) Siemens U-MHU-S110

Smoke Detectors:
(3) Simplex 2098-9201
(4) EST SIGA2-PS
(1) EST SIGA-PS

Heat Detectors:
(3) Simplex 2098-9440
(4) Edwards 282B-PL

Pull Stations:
(2) Simplex 4251-20
(1) Simplex 2099-9754
(1) Siemens Cerberus Pyrotronics MS-51
(1) Siemens MSM-K
(1) EST SIGA-270

If you want a FULL demonstration of this system, let me know and I'll post a video later this week.

User avatar
jelimoore
Casual Participant
Casual Participant
Posts: 165
Joined: Tue Nov 28, 2017 12:09 am

Re: My Home System (Simplex 4005)

Post by jelimoore » Sat Feb 03, 2018 2:22 am

jm2014 wrote: If you want a FULL demonstration of this system, let me know and I'll post a video later this week.
That would be nice.

jm2014
Casual Participant
Casual Participant
Posts: 199
Joined: Wed Sep 17, 2014 9:59 pm

Re: My Home System (Simplex 4005)

Post by jm2014 » Sat Feb 10, 2018 5:16 pm

Bell Test!


User avatar
jelimoore
Casual Participant
Casual Participant
Posts: 165
Joined: Tue Nov 28, 2017 12:09 am

Re: My Home System (Simplex 4005)

Post by jelimoore » Sun Feb 11, 2018 11:38 pm

Does the 4003 do anything at the minute?

jm2014
Casual Participant
Casual Participant
Posts: 199
Joined: Wed Sep 17, 2014 9:59 pm

Re: My Home System (Simplex 4005)

Post by jm2014 » Wed Feb 14, 2018 11:11 pm

jelimoore wrote:Does the 4003 do anything at the minute?
Not right now. Maybe sometime in the future. The system right now is permanent and the only change will be syncing the alarms together, thus the Truealert will be replaced by a Genesis horn/strobe and the 4904 strobe in the bedroom will be a U-MHU-MCS.

User avatar
Simplex 4051
Dedicated Participant
Dedicated Participant
Posts: 2141
Joined: Sat Mar 31, 2007 12:35 am
YouTube Username: Goldenrod636
Location: Pawtucket, RI
Contact:

Re: My Home System (Simplex 4005)

Post by Simplex 4051 » Thu Feb 15, 2018 5:41 am

Real nice system that you have set up! I'm a bit disappointed that you don't have any electromechanical horns but it is still nice!
I'm exclusively on Skype now. Add me at amazee_dayzee. I don't do voice or video chats though.

jm2014
Casual Participant
Casual Participant
Posts: 199
Joined: Wed Sep 17, 2014 9:59 pm

Re: My Home System (Simplex 4005)

Post by jm2014 » Wed Feb 21, 2018 2:27 pm

The monthly test of my home system.