Quick question about the System Sensor sync protocol

If you set the dial on the back of a SpectrAlert Advance or L-Series to one of the continuous tones, and then connect it to a MDL3 module or a control panel with the System Sensor sync protocol enabled, does it still sound in continuous (with the strobe synced) or does it get coded to code 3? I know Wheelock appliances will do code 3 when synced regardless of the setting on the horn (even the old AS with no code 3 option), so I was wondering if the System Sensor appliances do the same.

The horn will sound in continuous and the strobe will be synchronized. Synchronization and silencing work no matter what tone a SpectrAlert, Advance, or L-Series is set to.