why do we have to do fire drills once a month
- Casual Participant
it says that in the nfpa schools have to do fire drills once a month but why not other drills?
- Simplex 4051
- Dedicated Participant
- YouTube Username: Goldenrod636
- Contact:
Because I have to assume it is to do with the fact that a fire is the most common emergency that can happen to a school.
- nightfly287
- Retired Staff
I don't remember where I read it, but I think one of the reasons is as follows. By doing fire drills very frequently, occupants become accustomed to it, to the point where when the alarm sounds, they will automatically assume that it is a fire drill instead of an actual fire. That way, if there is an actual fire in the building, the occupants will remain calm because they think it's just a drill. The only way this will work is if occupants are fined or otherwise punished for not evacuating.
EDIT: I misread the point of your post. In this day and age, I think lockdown drills should probably be as common as fire drills (probably not monthly though).
nightfly287 -- Director of Sarcasm
- YouTube Username: EpicFireAlarms
- Contact:
Also keep in mind that the NFPA has no actual jurisdiction over performing or enforcing fire drills, those are just "suggestions". In most places, it's up to the state, an AHJ, or sometimes the school/school district to come up with an appropriate requirement for how many drills take place each year.
Our Lady of the Angels School is why.
A fire in the 1950's killed almost 100 children because nobody knew what to do in case of a fire, end result of that incident was mandated fire drills in the fire codes.
There are very few other codes like the fire codes... and lock down doesn't really apply to any of the existing codes, however NFPA 3000 was just released recently which specifically addresses active shooter situations so it might be coming soon.
- Simplex 4051
- Contact:
I thought the reason that there was so many fatalities was because school was built with flammable materials and nobody activated the alarm until the fire made it impossible for some classrooms to evacuate?
- DownsLife+Safety
- YouTube Username: Bousai Guy
- Contact:
I currently have a copy of NFPA 3000, which should be noted that it's a provisional standard. (speaking of which I need to read the entire book).chris+s wrote: ↑Tue Apr 30, 2019 9:50 pm Our Lady of the Angels School is why.
The current standard, NFPA 3000 9.5.1 currently states that,
However, that doesn't specify lockdowns, though that may be implemented in the ASHER plan. Therefore, it's probably safe to conclude that any security related drills, especially those relating to active shooter scenarios, must be conducted at least once per year according to this standard.Building owners and operators shall annually exercise [Active Shooter/Hostile Event Response] plans.
That being said, NFPA does clearly state that this is a provisional standard- a standard that is pretty much some of the first standardized guidelines for such incidents. The 2018 version is only effective for two years from 11 April 2018.
- New Participant
NFPA 3000 is a pretty solid standard, as it does a nice job of putting together some key response doctrine. In terms of drills, it depends on how "exercise" is interpreted. An exercise could be a first responder "tabletop" exercise, and not necessarily a drill or full-scale exercise. It also depends on which response "model" any particular institution adopts, as there are some variations among them, as well.DownsLife+Safety wrote: ↑Thu May 02, 2019 11:20 pm
The current standard, NFPA 3000 9.5.1 currently states that,However, that doesn't specify lockdowns, though that may be implemented in the ASHER plan. Therefore, it's probably safe to conclude that any security related drills, especially those relating to active shooter scenarios, must be conducted at least once per year according to this standard.Building owners and operators shall annually exercise [Active Shooter/Hostile Event Response] plans.
I'm originally from the midwest, and I remember we had tornado drills once a month. If I recall, they'd do them and fire drills on the same day - one in the morning and the other in the afternoon. The only "mandated" tornado drill (which wasn't really "mandated," per se) was participation in the statewide drill.
Required in NFPA 101 (Life Safety Code) 15.7.2.3 for educational occupancies:
Emergency egress drills shall be conducted as follows:
(1) Not less than one emergency egress drill shall be conducted every month the facility is in session, unless both of the following criteria are met:
(a) In climates where the weather is severe, the monthly emergency egress drills shall be permitted to be deferred.
(b) The required number of emergency egress drills shall be conducted, and not less than four shall be conducted before the drills are deferred.
(2) All occupants of the building shall participate in the drill.
(3) One additional emergency egress drill, other than for educational occupancies that are open on a year-round basis, shall be required within the first 30 days of operation.
- Simplex 4051
- Contact:
If that is true for colleges then I have REALLY had bad luck with that because every time I was in class I never had any fire drills that happened and the two that I was caught in was because I was there when somebody burned food.
No, it's not just you, these rules don't apply to colleges and universities. NFPA 101 considers them a business or assembly occupancy, which have no fire drill requirements, unless the AHJ says otherwise.
They are required in college dorms however, but it appears there is not a required frequency, just "with sufficient frequency to familiarize all occupants with the drill procedure and to have the conduct of the drill a matter of established routine."
I'm just sharing what's in the code that's pretty universally applied across the US. My personal take is that the single-minded focus on fire drills in K-12 here has become a bit counterproductive.
Maybe it's more necessary in schools without fire sprinklers, but schools are not the death traps that they were a couple generations ago.
So many unannounced drills leads children to think that every alarm is just a drill. Many, including myself when I was younger, dread being startled by the loud alarms, distracting them from lessons.
In other developed countries they are only done once or twice a year, even announced in advance, but the event is a bigger deal with more instruction and discussion. I can't imagine the codes going that direction here, but it seems more sensible to me.
- randomperson
- Serious Participant
- YouTube Username: randomperson Fire Alarms
- Contact:
At my school they happen once a year... but that’s probably because it is in an office building.
The landlord also sends out multiple emails ahead of time.
- Simplex 4051
- Contact:
Do the office occupants also have to evacuate?
- randomperson
- Contact:
Yes. It is buildingwide, and they also do fire drills at the other buildings in this office complex. AFAIK most office buildings do fire drills.
- Simplex 4051
- Contact:
Yeah I can see why it would be done. I guess its just when I think of fire drills I think of schools.