Ok so idk how to change the signal coding on the 4005. Does anybody know how? I have all access codes thanks!
OK, the NAC you want affected by the coding change needs to be set as an Audible NAC or this won’t work.
I will assume you already know your way around the 4005…
- Log in as Level 4.
- Open the Menu and scroll to Programming. Press Enter.
- Scroll to System Options and press Enter.
- Scroll to Audible Evacuation and press Enter.
- Scroll through the various signal coding options.
- Press Enter when you have made your selection.
- Press Exit until you get to a screen saying that the configuration as changed.
- Select “Save CFIG”.
- This is very important… DO NOT POWER DOWN THE PANEL WHILE IT IS SAVING. Doing so will CORRUPT the panel!
- Press Enter to save the configuration.