I have an ESL 445DRT (120VAC) Smoke detector and I would like to know how to wire it.
Here’s a photo of it:

Such a large photo… :shock:

Sorry, I’m not sure how to resize photos on here…

Could you post a picture of the terminal connections so we can try to help you?

Whoops… I meant to post a picture of the barrier shield also.
Here the photo of the terminals:

I have one of these detectors. Here is the order of the wires, from right to left (1 to 7).

1 - 120VAC Neutral (White wire)

2- 120VAC Hot (Black wire)

3 & 4- Alarm initiating contacts (Zone wires). These contacts can switch up to 30VDC or 120VAC, 2 Amps.

5, 6, 7- These are the contacts for the auxiliary relay. 5 is Normally Closed, 6 is Common, and 7 is Normally Open. These have the same power rating as the alarm contacts. These are isolated from the alarm initiating contacts and can be used for auxiliary device control.