I have an ESL 445DRT (120VAC) Smoke detector and I would like to know how to wire it.
Here’s a photo of it:
Such a large photo… :shock:
Sorry, I’m not sure how to resize photos on here…
Could you post a picture of the terminal connections so we can try to help you?
Whoops… I meant to post a picture of the barrier shield also.
Here the photo of the terminals:
I have one of these detectors. Here is the order of the wires, from right to left (1 to 7).
1 - 120VAC Neutral (White wire)
2- 120VAC Hot (Black wire)
3 & 4- Alarm initiating contacts (Zone wires). These contacts can switch up to 30VDC or 120VAC, 2 Amps.
5, 6, 7- These are the contacts for the auxiliary relay. 5 is Normally Closed, 6 is Common, and 7 is Normally Open. These have the same power rating as the alarm contacts. These are isolated from the alarm initiating contacts and can be used for auxiliary device control.
Thanks for the response!