 Post subject: Simplex 2098-9201 Help
PostPosted: Fri Jan 26, 2018 4:36 am 
Offline
Casual Participant
Casual Participant

Joined: Wed Sep 17, 2014 9:59 pm
Posts: 208
I've had my 2098-9201 smoke detector for a while now and works great! No problems at all, however when I take the head off, my panel (Simplex 4005) doesn't go into trouble. I am almost certain that's it's supposed to give me an open circuit fault. I don't have a wiring diagram easily accessible for this detector. My guess is I have the EOL resistor at the IDC in terminals and with that in mind, there's no way it's going to know if the detector head is missing. Am I supposed to put the resistor at another terminal or how does that work with this detector?

Thanks


Top
   
PostPosted: Fri Jan 26, 2018 7:46 am 
Offline
Casual Participant
Casual Participant
User avatar

Joined: Mon Nov 27, 2017 11:09 pm
Posts: 172
For any IDC, you put the EOLR (end of line resistor) at the end of a circuit. This way, the panel looks for it's resistance and throws a trouble if it can't find it.

Also, make sure you use all three contacts if you have three. One is ground, and two are positive in the case of a two wire detector. Use one positive for the wire from the panel then use the second one for either the EOLR or the next device. That way, if you take it down, the continuity between the two positives break, and the panel goes into trouble.


Top
   
PostPosted: Fri Jan 26, 2018 7:50 am 
Offline
Moderator
Moderator
User avatar

Joined: Wed Jun 11, 2014 5:22 pm
Posts: 753
Location: west TN
The End Of Line Resistor (EOLR) must go at the end of the circuit. It must not be connected at the panel on a zone that has a circuit of devices connected. The resistor is there for the supervision of the wiring and devices so a trouble will be reported if the wire breaks or a detector is removed. The drawing below is from the 4005 Field Wiring Drawings. The 2098-9201 could be installed in several different bases. If you post the number of the base you are using I probably have the detail drawing for that combination.

Image


Top
   
PostPosted: Fri Jan 26, 2018 9:57 am 
Offline
Moderator
Moderator
User avatar

Joined: Wed Jun 11, 2014 5:22 pm
Posts: 753
Location: west TN
Another important item in fire alarm circuits is to wire them correctly. If you have a circuit that goes in multiple directions to connect devices be sure they are wired correctly. The illustrations below show correct and incorrect wiring methods.

Image

Image


Top
   
PostPosted: Fri Jan 26, 2018 10:50 am 
Offline
Casual Participant
Casual Participant

Joined: Wed Sep 17, 2014 9:59 pm
Posts: 208
It's the 2098-9211 base. I just remembered the reason I put the resistor where I did is because I couldn't figure out which terminals were for the next device, plus it's the only device on the zone. I don't have a manual for it. So I left it alone for a while since I was busy the last month.


Top
   
PostPosted: Fri Jan 26, 2018 11:09 am 
Offline
Moderator
Moderator
User avatar

Joined: Wed Jun 11, 2014 5:22 pm
Posts: 753
Location: west TN
Here is a drawing of the 2098-9201 in 2098-9211.

Image

Link to manual on 2098-9201. Includes drawings on all possible bases and accessories.
http://firealarmresources.com/wp-conten ... nual-2.pdf


Top
   
PostPosted: Fri Jan 26, 2018 12:27 pm 
Offline
Casual Participant
Casual Participant

Joined: Wed Sep 17, 2014 9:59 pm
Posts: 208
Thanks for the diagram! Will try later when I get a new pull station in the mail.


Top
   
Display posts from previous:  Sort by  
Post new topic  Reply to topic  [ 7 posts ] 

All times are UTC-04:00


Who is online

Users browsing this forum: Google [Bot] and 6 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
cron
Powered by phpBB® Forum Software © phpBB Limited