Re: Simplex 4005 Help

Post by Ryanjohncz » Tue Feb 13, 2018 7:52 pm

The horn nac says “coding” and the strobe plate isn’t flashing and says “on”

User avatar
Retired STR-SG
Moderator
Moderator
Posts: 739
Joined: Wed Jun 11, 2014 5:22 pm
Location: west TN
Contact:

Re: Simplex 4005 Help

Post by Retired STR-SG » Tue Feb 13, 2018 8:34 pm

OK. You have determined with a voltmeter that the horn NAC is not supplying signal power. Test one of the spare circuits that has a 10K resistor connected with your voltmeter. With the panel in standby mode there should be supervision polarity present. When the panel is put into alarm the polarity on the meter should switch to alarm mode polarity. If it does move your horn circuit wires to that circuit. Then test the horns.

Is the "strobe plate" you are referring to is the 4050-80?

Ryanjohncz
Casual Participant
Casual Participant
Posts: 31
Joined: Mon Feb 12, 2018 10:40 pm

Re: Simplex 4005 Help

Post by Ryanjohncz » Tue Feb 13, 2018 8:37 pm

No it’s a 4903-9101 strobe plate

User avatar
Retired STR-SG
Moderator
Moderator
Posts: 739
Joined: Wed Jun 11, 2014 5:22 pm
Location: west TN
Contact:

Re: Simplex 4005 Help

Post by Retired STR-SG » Tue Feb 13, 2018 8:54 pm

OK. Have you verified that the circuit the 4903-9101 is connected to is putting out signal power voltage in alarm with the voltmeter?

Are there any troubles on the panel you have not mentioned?

Ryanjohncz
Casual Participant
Casual Participant
Posts: 31
Joined: Mon Feb 12, 2018 10:40 pm

Re: Simplex 4005 Help

Post by Ryanjohncz » Wed Feb 14, 2018 3:53 pm

There isn’t any voltage going to the strobe plate or horn nac whatsoever. I’m guessing that the panel isn’t outputting power to the horn nac because of the short that it’s detecting

User avatar
Retired STR-SG
Moderator
Moderator
Posts: 739
Joined: Wed Jun 11, 2014 5:22 pm
Location: west TN
Contact:

Re: Simplex 4005 Help

Post by Retired STR-SG » Wed Feb 14, 2018 4:09 pm

There is an electronic circuit breaker circuit in the power supply that could be tripped or damaged. That should cause a "Signal Power Trouble Input" condition on the panel.

Here is a test procedure for the signal power circuit. Use it even if the "Signal Power Trouble Input" condition is not present.
Symptoms:
• System Trouble
• Signal Power Trouble Input
• Panel in Trouble
Causes:
• Cause is Associated with the Power Supply
• Signal Power Trouble Input 28-7 Main Supply Overcurrent
Fix:
• See below for possible solutions:
1.) With trouble condition displayed press the Right Arrow Key to verify the trouble point as 28-7.
2.) The Signal Power from Signal +24V and OV are compared through the Power Distribution Board fuses F1 and F2 to a comparator to the CPU.
3.) Check Detector Power on CPU TB-1 terminals 1 & 2 for 24V. This is Resettable Detector Power.
4.) Check the voltage on the right hand Power Distribution Board TB-1 terminals 3 to 5 and terminals 4 to 6, both should have 24VDC. This is Signal Power voltage from the power supply. If there is no voltage check fuses F1 and F2 on the power distribution board.
5.) Check the voltage on the right hand Power Distribution Board TB-1 terminals 1 to 5 and terminals 2 to 6 both should have 24VDC.
6.) If you do not have 24VDC on the Power Distribution board TB-1 terminals 3 to 5 and 4 to 6 and the fuses are good, but you have 24VDC on TB-1 terminals 1 to 5 and terminals 2 to 6, then the OV Signal on the power supply is not turned on.
7.) Go into the programming and make a change in the CFIG (Change: a label or point), and save the CFIG. Check the voltages again. This is intended to provide the system CPU with a Restart signal and the chance to reset internal system software flags.
8.) If steps 1 to 6 fail in identifying the cause of trouble replace the power supply.

Ryanjohncz
Casual Participant
Casual Participant
Posts: 31
Joined: Mon Feb 12, 2018 10:40 pm

Re: Simplex 4005 Help

Post by Ryanjohncz » Wed Feb 14, 2018 4:17 pm

Is there supposed to be wires in that 6 screw terminal block?

User avatar
Retired STR-SG
Moderator
Moderator
Posts: 739
Joined: Wed Jun 11, 2014 5:22 pm
Location: west TN
Contact:

Re: Simplex 4005 Help

Post by Retired STR-SG » Wed Feb 14, 2018 4:30 pm

When a 4005 is new from the factory there were no wires connected to that terminal strip. Whatever wires are there are left from the installation the panel was removed from.

Ryanjohncz
Casual Participant
Casual Participant
Posts: 31
Joined: Mon Feb 12, 2018 10:40 pm

Re: Simplex 4005 Help

Post by Ryanjohncz » Wed Feb 14, 2018 4:33 pm

Okay I’m not getting any power from the resettable detector power

Ryanjohncz
Casual Participant
Casual Participant
Posts: 31
Joined: Mon Feb 12, 2018 10:40 pm

Re: Simplex 4005 Help

Post by Ryanjohncz » Wed Feb 14, 2018 4:48 pm

Or do you think since I’m having a trouble on the one signal circuit that the panel is canceling all operation on that card all together??

User avatar
Retired STR-SG
Moderator
Moderator
Posts: 739
Joined: Wed Jun 11, 2014 5:22 pm
Location: west TN
Contact:

Re: Simplex 4005 Help

Post by Retired STR-SG » Wed Feb 14, 2018 5:11 pm

There is only one circuit on the power supply that can shut down all of the signal power outputs when it is tripped. I would disconnect the wires going to your signals and place 10K resistors on the two circuits you are using. Then follow steps 6 and 7 in the test procedure. If the voltages come back on test the NAC operation with just the resistors connected. If the DET PWR voltage on the CPU and the voltages on the distribution board terminals do not come back on the power supply probably is damaged.

Ryanjohncz
Casual Participant
Casual Participant
Posts: 31
Joined: Mon Feb 12, 2018 10:40 pm

Re: Simplex 4005 Help

Post by Ryanjohncz » Wed Feb 14, 2018 5:15 pm

The voltage on the nac card will only go up to 17ish

User avatar
Retired STR-SG
Moderator
Moderator
Posts: 739
Joined: Wed Jun 11, 2014 5:22 pm
Location: west TN
Contact:

Re: Simplex 4005 Help

Post by Retired STR-SG » Wed Feb 14, 2018 5:35 pm

Is that 17ish volts in standby or alarm? It is normal for the standby (supervisory) voltage to be lower. The NAC card has two 24 volt sources coming to it. The supervisory voltage is from a different 24 volt circuit than the signal power used to sound horns in alarm mode. So there can be supervisory voltage in standby mode but no signal power when in alarm mode.

You have to recheck at the DET PWR terminals and the terminal strip on the distribution card. Those voltages are sourced from the signal power circuit that has the electronic circuit breaker that can shut it off.

Ryanjohncz
Casual Participant
Casual Participant
Posts: 31
Joined: Mon Feb 12, 2018 10:40 pm

Re: Simplex 4005 Help

Post by Ryanjohncz » Wed Feb 14, 2018 5:42 pm

That 17 is alarm voltage is for the circuits without any horns or strobes on it. The circuits with horns and strobe on it is 0 all together

User avatar
Retired STR-SG
Moderator
Moderator
Posts: 739
Joined: Wed Jun 11, 2014 5:22 pm
Location: west TN
Contact:

Re: Simplex 4005 Help

Post by Retired STR-SG » Wed Feb 14, 2018 5:53 pm

With only 17 volts available on unloaded circuits in alarm, my best guess is that the power supply is damaged and needs to be replaced. Sorry.