Exhaust stack fans deenergize whan Fire alarm activates at panel

Post by hingusus » Thu Feb 15, 2018 9:07 am

Why do the fans shutdown verses go to full exhaust when fire alarm system within building sounds?
tim

Old fire alarm guy
Fire Alarm Technician
Posts: 41
Joined: Tue Apr 05, 2016 7:09 am

Re: Exhaust stack fans deenergize whan Fire alarm activates at panel

Post by Old fire alarm guy » Fri Feb 16, 2018 11:19 am

So you don't feed the fire with more air.
I've forgotten more than I remember.

theboginator
Casual Participant
Casual Participant
Posts: 134
Joined: Wed Mar 08, 2017 10:09 am
Location: Central MA

Re: Exhaust stack fans deenergize whan Fire alarm activates at panel

Post by theboginator » Mon Feb 19, 2018 10:56 pm

Even though it's exhaust, it's creating negative air pressure in the area, which draws in more fresh air from the surroundings. Great for clearing smoke after the fact but definitely hazardous in a real fire. Also, the system is shut down to prevent other AHUs from sucking in smoke and blowing it to other areas of a building, since smoke is toxic.