Simplex 4100 Legacy - Positive Alarm Sequence

Post here if you need help with something related to fire alarms
Post Reply
ff803
New User
New User
Posts: 1
Joined: Thu Sep 13, 2018 6:33 pm

Thu Sep 13, 2018 6:55 pm

I've tried searching online, but as I expected, not much success.

This need is for a school. Without getting into further detail, the environment at the moment would be greatly improved if the automatic detection devices/zones could be programmed for a positive alarm sequence. However, I know this panel was designed in the 1980's - but was top of the line back back.

Does anyone know if this panel is capable of "selective" (by zone/point) positive alarm sequence operation? As opposed to pre-signal... trying to keep from having to try to deviate from 101 Chapter 15.

Thanks for all who help
User avatar
Retired STR-SG
Moderator
Moderator
Posts: 786
Joined: Wed Jun 11, 2014 5:22 pm
Location: west TN
Contact:

Fri Sep 14, 2018 3:09 pm

Yes, any 4100 system can be programmed for Positive Alarm Sequence. It will take a Simplex (now JCI) technician to do the programming. I looked it up for a customer years ago (pre-4100U) while I was still working, however it was never implemented. A tech can get the documentation on the programming through the Technical Support department.

Positive Alarm Sequence has a number of requirements. Read this article for more information.
https://www.jensenhughes.com/blog/posit ... -sequence/