Home Burglar Alarm Relay

Post by hhenry1234 » Mon Jan 05, 2015 4:54 pm

Hello everyone. My panel that I have made goes into alarm when the circuit is closed. How can I use a relay to change the N.C. coming from sensors to N.O. that the panel accepts.

Thanks!
Hudson Henry
American Sound & Electronics
PC Telecom

chris+s
Fire Alarm Technician
Posts: 710
Joined: Mon Jul 07, 2014 8:37 am

Re: Home Burglar Alarm Relay

Post by chris+s » Mon Jan 05, 2015 6:51 pm

You will probably need to run power through the N/C contact on the fire device to the coil of a N/O relay. When the power to the coil drops the relay should close and set your panel off.

User avatar
kcin556
Moderator
Moderator
Posts: 1123
Joined: Thu Jul 11, 2013 2:18 pm
YouTube Username: kcin556
Location: Chicago, IL
Contact:

Re: Home Burglar Alarm Relay

Post by kcin556 » Mon Jan 05, 2015 7:17 pm

All relays are shown de-energized. When power is applied, the new relay will automatically open and will only close when connectivity through the zone is lost, whether by a device activating or the wires being damaged. Keep in mind that all devices on the zone must be connected in series for the zone to work.
Attachments
NC to NO.JPG
NC to NO.JPG (66.28 KiB) Viewed 837 times
Nick - Moderator
Please send me a PM if you experience any issues or have any concerns. Thank you!
kcin556 on YouTube

User avatar
hhenry1234
Casual Participant
Casual Participant
Posts: 71
Joined: Thu Dec 25, 2014 9:31 pm
Location: Cincinnati

Re: Home Burglar Alarm Relay

Post by hhenry1234 » Mon Jan 05, 2015 8:12 pm

Thanks, exactly what I needed :D