Bad Ideas
An area to discuss extinguishers and suppression systems.
-SimplexTech2015-
I'm Banned!
I'm Banned!
Bad Ideas
Postby -SimplexTech2015- » Sun May 17, 2015 2:36 pm
So I got to go into the building where a large car company keeps all of the computer servers for all of the world. There are 4 rooms of rows and rows of servers. Anyway, I don't think that it would be smart to have a SPRINKLER system in those rooms. Water damage would take down the servers around the world. Everywhere else in any building that had sensitive equipment had FM 200 so what the heck?
kcin556
Moderator
Moderator
YouTube Username: kcin556
Re: Bad Ideas
Postby kcin556 » Sun May 17, 2015 4:12 pm
Are you sure it wasn't so other form of suppression? Halon, CO2, FM-200, and Inergen pipes can look similar to sprinkler system piping, although the latter three systems have noticeably larger and strangely shaped nozzles. However, Halon systems especially can have nozzles with deflectors that are very reminiscent of water sprinklers.
If it is truly a sprinkler system in a data center like that, it likely has a pre-action system of some sort in place to prevent an accidental discharge or leak. In this case, it would require a manual confirmation of an alarm from a pull station or an automatic confirmation, usually from more than one smoke or heat detector, before the pre-action valve is opened. Then, it would still require the individual sprinkler heads to activate from the heat as well before water could be released.
Nick - Moderator
Please send me a PM if you experience any issues or have any concerns. Thank you!
kcin556 Alarm Website - kcin556 on YouTube - Fire Alarm Sales
-SimplexTech2015-
I'm Banned!
I'm Banned!
Re: Bad Ideas
Postby -SimplexTech2015- » Sun May 17, 2015 8:48 pm
Here's a picture of a bg 12 marked preaction sprinkler, definently not FM 200 because they have those huge bronze novels with holes in the side
kcin556
Moderator
Moderator
Re: Bad Ideas
Postby kcin556 » Sun May 17, 2015 9:26 pm
So you were correct in that it is a sprinkler system. Somebody would have to pull that pull station (or have confirmation from smoke detectors) before the pre-action valve would be opened to allow water into the sprinkler pipes, at least for those server rooms.
It does seem silly to have a destructive water sprinkler system in there when there are so many alternatives to prevent damage to the equipment, but as with most things there must be a reason, whether it makes sense or not, for the system to be as it is.
Nick - Moderator
-SimplexTech2015-
I'm Banned!
I'm Banned!
Re: Bad Ideas
Postby -SimplexTech2015- » Mon May 18, 2015 8:07 am
I didn't see any other visible forms of fire suppression besides those sprinkler heads. I also noticed many screens around the room displaying heat intensity and a scale until it reaches fire alarm. I forgot to take a picture and I didn't think much of it. The rest of the system was the same, Wheelock Speaker Strobes and Simplex Tbars no agent release alarms. I guess it would make for sense if it would be a last resort kind of thing but this I would think wouldn't be enough to stop a fire or severe damage
chris+s
Fire Alarm Technician
Re: Bad Ideas
Postby chris+s » Mon May 18, 2015 9:45 pm
Clean agent systems are typically a one shot thing then it could be out of commission for days while the tanks are refilled. Pre-action systems make excellent backups, it's better to lose a rack than an entire building. Probably required by insurance in most cases. Only one head will go off at a time, and that's when it get's hot enough so there's a really good chance there's burning electronics under it.
We used to put in EPO's that would shut down equipment when FA heat's went off and the pre-action was fired (before the sprinkler heads popped though), so the equipment was at least shut down before it was soaked. Problem with that was, critical servers could accidentally get shut down during FA testing if the inspectors didn't know about them, so I don't see it much anymore.
Also, many modern data centers have clean agent pipped directly into each individual rack or rack system.
chris+s
Re: Bad Ideas
Postby chris+s » Tue May 19, 2015 9:47 pm
Lambda wrote:
chris+s wrote:We used to put in EPO's that would shut down equipment when FA heat's went off and the pre-action was fired (before the sprinkler heads popped though), so the equipment was at least shut down before it was soaked. Problem with that was, critical servers could accidentally get shut down during FA testing if the inspectors didn't know about them, so I don't see it much anymore.
There have been a couple of sites where I make the customer disable their own EPO's, solenoids, horns, etc. I figure the liability is on them if something goes wrong. Especially when you get the ones that tell you "we will lose a million dollars a minute if this equipment goes down".
Or "Our entire north american and european operations will be at a standstill if these servers go down".
it's amazing none of these places have backup data centers for business continuity.
jimmyscotts
New Participant
New Participant
YouTube Username: jimmyscotts
Re: Bad Ideas
Postby jimmyscotts » Wed Jun 14, 2017 5:39 am
What is that in the picture?
kcin556
Moderator
Moderator
Re: Bad Ideas
Postby kcin556 » Wed Jun 14, 2017 9:34 am
Please make sure to double-check the previous post date before replying to a topic. In this case, the last post was made over two years ago.
Thank you!
Nick - Moderator
Return to “Fire Extinguishers & Suppression”