Just finished a job today as a helper and saw this when we were draining the pipes.
Where's the fail?
Image
Robert Aslin
My YouTube Channel | Aslin Fire Safety
If you need to contact me for any reason, you may email me at aslinrobert15(at)gmail.com.
HenBasket
Serious Participant
Serious Participant
Posts: 312
Joined: Tue Apr 05, 2016 11:39 am
YouTube Username: HenBasket

Wed Jun 01, 2016 5:32 pm

Missing cover?
Roses are red, heavy steel beam
I need a rhyme to finish this meme
User avatar
ccs46
Dedicated Participant
Dedicated Participant
Posts: 887
Joined: Sat Mar 08, 2014 7:09 pm
YouTube Username: ccs4646
Location: North Central Florida, USA

Wed Jun 01, 2016 6:41 pm

Last drain date was in 2014? Low water pressure?

Sent from my iPhone using Tapatalk
User avatar
Lambda
Fire Alarm Technician
Fire Alarm Technician
Posts: 159
Joined: Thu Apr 07, 2016 8:40 pm
Location: Eastern Shore, MD

Wed Jun 01, 2016 7:07 pm

My brain must be fried from walking through 76 residential units today staring at sprinkler heads, but I don't visually see anything wrong. The christmas tree of tags annoys me but not really a deficiency. And you don't show a spare head box in the picture, but I would assume it's off to the side.

Unless you are pointing out the closed control valve and chalked waterflow switch - which I wouldn't count as a problem if you're working on the sprinkler system. It's almost SOP for fitters to chalk the flow switch so they don't have to play around with pulling wires in the panel.
User avatar
Robert A
Dedicated Participant
Dedicated Participant
Posts: 909
Joined: Sun May 26, 2013 11:13 pm
YouTube Username: Aslin Fire Safety
Location: Stillwater, OK
Contact:

Wed Jun 01, 2016 8:02 pm

Technically, it's the chalked switch. The pressure was low because we drained it. I was going to ask about shutting off the zone it was hooked on to, but the guy I was helping didn't seem to think I knew anything about fire alarm systems.
He literally pulled a tag off the rider, wadded it up, and wedged it between the paddle.
Robert Aslin
My YouTube Channel | Aslin Fire Safety
If you need to contact me for any reason, you may email me at aslinrobert15(at)gmail.com.
User avatar
Lambda
Fire Alarm Technician
Fire Alarm Technician
Posts: 159
Joined: Thu Apr 07, 2016 8:40 pm
Location: Eastern Shore, MD

Wed Jun 01, 2016 9:01 pm

Yup, that's what they do. I've been called out to a couple of sites just to shut down the alarm system for a fitter that didn't want to deal with it. And hey, I don't blame them. But I have found some switches that were accidently left like that we'll after the job was completed. So it's not fool proof.