Vista 20p - Bell Circuit Coding for Fire Zone Activation

Post here if you need help with something related to security systems.
Forum rules
Do NOT publicly post default codes for ANY security system or fire alarm panel.
(Rule #8)
User avatar
Gentex Guy
Casual Participant
Casual Participant
Posts: 56
Joined: Wed Aug 05, 2020 12:50 am
YouTube Username: Gentex Guy
Contact:

Hey everyone. I'm a total novice when it comes to the Vista 20p and security systems in general, but I was curious about something: When I have a zone programmed as a type 9 (fire), the bell circuit is always coded to code 3 when it is activated. I want to use this panel as a primitive fire alarm system, but the alarms I want to use with it are self coding, and don't work well when the bell circuit is coded to code 3.

As of right now, I have the zones programmed as a type 7 (24hr audible) so that the bell circuit outputs a steady coding. This works okay for my purposes of using it as a demo system, but I want to make this a realistic setup. So, I'm interested to know if there's a way to have the bell circuit output a steady coding when a fire zone goes into alarm. Like I said, I'm a complete beginner with this panel, so I apologize if this is something that's blatantly obvious.
Proud owner of a Fire-Lite MS-2 system that drives my parents crazy!
Check out my YouTube channel!
User avatar
MrFireAlarm
New Participant
New Participant
Posts: 13
Joined: Wed Jun 10, 2020 7:59 pm
Location: Phoenix AZ
Contact:

Vista panels cant do that.
I have an alarm that I like to call, "The vertical RSS."
User avatar
MrFireAlarm
New Participant
New Participant
Posts: 13
Joined: Wed Jun 10, 2020 7:59 pm
Location: Phoenix AZ
Contact:

Gentex Guy wrote: Mon Nov 09, 2020 4:52 pm Hey everyone. I'm a total novice when it comes to the Vista 20p and security systems in general, but I was curious about something: When I have a zone programmed as a type 9 (fire), the bell circuit is always coded to code 3 when it is activated. I want to use this panel as a primitive fire alarm system, but the alarms I want to use with it are self coding, and don't work well when the bell circuit is coded to code 3.

As of right now, I have the zones programmed as a type 7 (24hr audible) so that the bell circuit outputs a steady coding. This works okay for my purposes of using it as a demo system, but I want to make this a realistic setup. So, I'm interested to know if there's a way to have the bell circuit output a steady coding when a fire zone goes into alarm. Like I said, I'm a complete beginner with this panel, so I apologize if this is something that's blatantly obvious.
MrFireAlarm wrote: Tue Nov 10, 2020 1:06 pm Vista panels cant do that.
Forget what I said earlier because I just tested my commander 3 with my Vista20p system and It works fine. I recommend you do not set the coding on your device to code 3 when doing a fire alarm.

Note the bell output 12VDC not 24.
I have an alarm that I like to call, "The vertical RSS."
User avatar
Gentex Guy
Casual Participant
Casual Participant
Posts: 56
Joined: Wed Aug 05, 2020 12:50 am
YouTube Username: Gentex Guy
Contact:

MrFireAlarm wrote: Tue Nov 10, 2020 4:22 pm
Gentex Guy wrote: Mon Nov 09, 2020 4:52 pm Hey everyone. I'm a total novice when it comes to the Vista 20p and security systems in general, but I was curious about something: When I have a zone programmed as a type 9 (fire), the bell circuit is always coded to code 3 when it is activated. I want to use this panel as a primitive fire alarm system, but the alarms I want to use with it are self coding, and don't work well when the bell circuit is coded to code 3.

As of right now, I have the zones programmed as a type 7 (24hr audible) so that the bell circuit outputs a steady coding. This works okay for my purposes of using it as a demo system, but I want to make this a realistic setup. So, I'm interested to know if there's a way to have the bell circuit output a steady coding when a fire zone goes into alarm. Like I said, I'm a complete beginner with this panel, so I apologize if this is something that's blatantly obvious.
MrFireAlarm wrote: Tue Nov 10, 2020 1:06 pm Vista panels cant do that.
Forget what I said earlier because I just tested my commander 3 with my Vista20p system and It works fine. I recommend you do not set the coding on your device to code 3 when doing a fire alarm.

Note the bell output 12VDC not 24.
Yeah, I have noticed that alarms like the Commander 3 work fine since they sound as soon as there is power. However, most of my alarms (that can run on 12v) have a 1/2 second delay between when power is applied and when they start sounding. Since they have this delay, they cannot fully sound when the bell circuit is coded to code 3. If it's not possible to change the bell circuit coding, I'll probably just keep it on zone type 7 since it's just going to be used as a demo system.
Proud owner of a Fire-Lite MS-2 system that drives my parents crazy!
Check out my YouTube channel!
User avatar
MrFireAlarm
New Participant
New Participant
Posts: 13
Joined: Wed Jun 10, 2020 7:59 pm
Location: Phoenix AZ
Contact:

Gentex Guy wrote: Tue Nov 10, 2020 6:20 pm
MrFireAlarm wrote: Tue Nov 10, 2020 4:22 pm
Gentex Guy wrote: Mon Nov 09, 2020 4:52 pm Hey everyone. I'm a total novice when it comes to the Vista 20p and security systems in general, but I was curious about something: When I have a zone programmed as a type 9 (fire), the bell circuit is always coded to code 3 when it is activated. I want to use this panel as a primitive fire alarm system, but the alarms I want to use with it are self coding, and don't work well when the bell circuit is coded to code 3.

As of right now, I have the zones programmed as a type 7 (24hr audible) so that the bell circuit outputs a steady coding. This works okay for my purposes of using it as a demo system, but I want to make this a realistic setup. So, I'm interested to know if there's a way to have the bell circuit output a steady coding when a fire zone goes into alarm. Like I said, I'm a complete beginner with this panel, so I apologize if this is something that's blatantly obvious.
MrFireAlarm wrote: Tue Nov 10, 2020 1:06 pm Vista panels cant do that.
Forget what I said earlier because I just tested my commander 3 with my Vista20p system and It works fine. I recommend you do not set the coding on your device to code 3 when doing a fire alarm.

Note the bell output 12VDC not 24.
Yeah, I have noticed that alarms like the Commander 3 work fine since they sound as soon as there is power. However, most of my alarms (that can run on 12v) have a 1/2 second delay between when power is applied and when they start sounding. Since they have this delay, they cannot fully sound when the bell circuit is coded to code 3. If it's not possible to change the bell circuit coding, I'll probably just keep it on zone type 7 since it's just going to be used as a demo system.
Cool. I'm fine with that.
I have an alarm that I like to call, "The vertical RSS."
User avatar
The 4251-13
Casual Participant
Casual Participant
Posts: 30
Joined: Mon Jun 15, 2020 4:38 pm
YouTube Username: TheCrafter1952 Official
Location: La Crosse County, WI
Contact:

Alternatively, you could get a Vista relay (you wire it up just like a keypad) and you could program it to activate on "Any Fire Alarm" and deactivate on disarm. IDK how much the relay costs, though. I automatically assume $50, but will have to look into it. I have a Vista 10SE, but I can't use it due to the transformer not being grounded. I'm going to have to look at the model #s in the manual to give any definitive answer.
-TC1952
My avatar says "Crafter" in the kana system, not "Fire."
"HAVE FUN STORMING THE CASTLE!" - Billy Crystal
Visit my YouTube (If it ever has content...)
I am on GeoFS - Look for my callsign: N1952TC
User avatar
DownsLife+Safety
Casual Participant
Casual Participant
Posts: 149
Joined: Thu Nov 23, 2017 11:49 am
YouTube Username: Bousai Guy
Location: mah house
Contact:

Gentex Guy wrote: Tue Nov 10, 2020 6:20 pm
MrFireAlarm wrote: Tue Nov 10, 2020 4:22 pm
MrFireAlarm wrote: Tue Nov 10, 2020 1:06 pm Vista panels cant do that.
Forget what I said earlier because I just tested my commander 3 with my Vista20p system and It works fine. I recommend you do not set the coding on your device to code 3 when doing a fire alarm.

Note the bell output 12VDC not 24.
Yeah, I have noticed that alarms like the Commander 3 work fine since they sound as soon as there is power. However, most of my alarms (that can run on 12v) have a 1/2 second delay between when power is applied and when they start sounding. Since they have this delay, they cannot fully sound when the bell circuit is coded to code 3. If it's not possible to change the bell circuit coding, I'll probably just keep it on zone type 7 since it's just going to be used as a demo system.
Question: what model are your self-coding alarms? If they have the option to disable the self-code then it would be in your interest to disable it.
Bousai Guy ~ Inspiring to prepare safer lives
Find my YouTube Channel Here!
User avatar
The 4251-13
Casual Participant
Casual Participant
Posts: 30
Joined: Mon Jun 15, 2020 4:38 pm
YouTube Username: TheCrafter1952 Official
Location: La Crosse County, WI
Contact:

I found the models for the relays and they are 4204 and 4229. Also, make sure the bell supervision jumper is cut as well, as fire bell circuits need to be supervised. Nonetheless, great question!
-TC1952
My avatar says "Crafter" in the kana system, not "Fire."
"HAVE FUN STORMING THE CASTLE!" - Billy Crystal
Visit my YouTube (If it ever has content...)
I am on GeoFS - Look for my callsign: N1952TC
User avatar
Gentex Guy
Casual Participant
Casual Participant
Posts: 56
Joined: Wed Aug 05, 2020 12:50 am
YouTube Username: Gentex Guy
Contact:

DownsLife+Safety wrote: Fri Dec 04, 2020 2:19 am
Question: what model are your self-coding alarms? If they have the option to disable the self-code then it would be in your interest to disable it.
Gentex Commander 3, SpectrAlert Advance, Wheelock Exceder/AS, EST Integrity/Genesis

As far as I can tell, none of those have the option to disable self coding. I know 4-wire/horn only models of the Advance series have the option to disable self coding, but my Advance is a two wire horn strobe.
Proud owner of a Fire-Lite MS-2 system that drives my parents crazy!
Check out my YouTube channel!
User avatar
Gentex Guy
Casual Participant
Casual Participant
Posts: 56
Joined: Wed Aug 05, 2020 12:50 am
YouTube Username: Gentex Guy
Contact:

The 4251-13 wrote: Fri Dec 04, 2020 10:32 am I found the models for the relays and they are 4204 and 4229. Also, make sure the bell supervision jumper is cut as well, as fire bell circuits need to be supervised. Nonetheless, great question!
Thank you, I'll look into it!
Proud owner of a Fire-Lite MS-2 system that drives my parents crazy!
Check out my YouTube channel!
User avatar
DownsLife+Safety
Casual Participant
Casual Participant
Posts: 149
Joined: Thu Nov 23, 2017 11:49 am
YouTube Username: Bousai Guy
Location: mah house
Contact:

Gentex Guy wrote: Sun Dec 06, 2020 3:07 pm
DownsLife+Safety wrote: Fri Dec 04, 2020 2:19 am
Question: what model are your self-coding alarms? If they have the option to disable the self-code then it would be in your interest to disable it.
Gentex Commander 3, SpectrAlert Advance, Wheelock Exceder/AS, EST Integrity/Genesis

As far as I can tell, none of those have the option to disable self coding. I know 4-wire/horn only models of the Advance series have the option to disable self coding, but my Advance is a two wire horn strobe.
Spectralert Advance and Wheelock Exceder can definitely disable coding to Code-3. Set the alarms to continuous option - setting it otherwise will give you problematic results.
Bousai Guy ~ Inspiring to prepare safer lives
Find my YouTube Channel Here!
User avatar
Gentex Guy
Casual Participant
Casual Participant
Posts: 56
Joined: Wed Aug 05, 2020 12:50 am
YouTube Username: Gentex Guy
Contact:

DownsLife+Safety wrote: Sun Dec 06, 2020 11:25 pm
Gentex Guy wrote: Sun Dec 06, 2020 3:07 pm
DownsLife+Safety wrote: Fri Dec 04, 2020 2:19 am
Question: what model are your self-coding alarms? If they have the option to disable the self-code then it would be in your interest to disable it.
Gentex Commander 3, SpectrAlert Advance, Wheelock Exceder/AS, EST Integrity/Genesis

As far as I can tell, none of those have the option to disable self coding. I know 4-wire/horn only models of the Advance series have the option to disable self coding, but my Advance is a two wire horn strobe.
Spectralert Advance and Wheelock Exceder can definitely disable coding to Code-3. Set the alarms to continuous option - setting it otherwise will give you problematic results.
Yeah I've had them all set on continuous, but even still, most of them have that 1/2 second delay between when power is applied and when they start sounding. Although I have found that the Exceder, along with the Commander 3, does not have this delay when set on continuous.
Proud owner of a Fire-Lite MS-2 system that drives my parents crazy!
Check out my YouTube channel!
User avatar
DownsLife+Safety
Casual Participant
Casual Participant
Posts: 149
Joined: Thu Nov 23, 2017 11:49 am
YouTube Username: Bousai Guy
Location: mah house
Contact:

Gentex Guy wrote: Mon Dec 07, 2020 12:32 am
DownsLife+Safety wrote: Sun Dec 06, 2020 11:25 pm
Gentex Guy wrote: Sun Dec 06, 2020 3:07 pm

Gentex Commander 3, SpectrAlert Advance, Wheelock Exceder/AS, EST Integrity/Genesis

As far as I can tell, none of those have the option to disable self coding. I know 4-wire/horn only models of the Advance series have the option to disable self coding, but my Advance is a two wire horn strobe.
Spectralert Advance and Wheelock Exceder can definitely disable coding to Code-3. Set the alarms to continuous option - setting it otherwise will give you problematic results.
Yeah I've had them all set on continuous, but even still, most of them have that 1/2 second delay between when power is applied and when they start sounding. Although I have found that the Exceder, along with the Commander 3, does not have this delay when set on continuous.
What strobe setting do you have them on, and how do you have them wired up? The Exceder should sound instantly when power is applied and it's set to continuous.
Bousai Guy ~ Inspiring to prepare safer lives
Find my YouTube Channel Here!
User avatar
VRRyan
New Participant
New Participant
Posts: 14
Joined: Wed Sep 30, 2020 8:42 am
Contact:

Gentex Guy wrote: Mon Nov 09, 2020 4:52 pm Hey everyone. I'm a total novice when it comes to the Vista 20p and security systems in general, but I was curious about something: When I have a zone programmed as a type 9 (fire), the bell circuit is always coded to code 3 when it is activated. I want to use this panel as a primitive fire alarm system, but the alarms I want to use with it are self coding, and don't work well when the bell circuit is coded to code 3.

As of right now, I have the zones programmed as a type 7 (24hr audible) so that the bell circuit outputs a steady coding. This works okay for my purposes of using it as a demo system, but I want to make this a realistic setup. So, I'm interested to know if there's a way to have the bell circuit output a steady coding when a fire zone goes into alarm. Like I said, I'm a complete beginner with this panel, so I apologize if this is something that's blatantly obvious.
I know this is a little late but if you set the zone type as 07 aka 24hr audible alarm, it should just strait up give power and my spectralert advance now works on it correctly as seen in my video here: https://www.youtube.com/watch?v=fkq0MQV ... el=VRRyan6
im no longer active on The Fire Panel forums or discord (banned), if you would like to contact me please email me at: [email protected]
:(
User avatar
Gentex Guy
Casual Participant
Casual Participant
Posts: 56
Joined: Wed Aug 05, 2020 12:50 am
YouTube Username: Gentex Guy
Contact:

DownsLife+Safety wrote: Mon Dec 07, 2020 7:34 pm What strobe setting do you have them on, and how do you have them wired up? The Exceder should sound instantly when power is applied and it's set to continuous.
Yeah I did mention that the Exceder sounds immediately when set on continuous, the Advance does not. I have the strobe on 15cd, and I did see when selecting the candela that it can only do 15cd on 12 volts, but I never set it higher anyways. Also, I have the positive and negative on the panel go directly to the positive and negative of the alarm. I don't have any other devices or an end of line resistor since I'm just using it as a demo system.
Proud owner of a Fire-Lite MS-2 system that drives my parents crazy!
Check out my YouTube channel!