I just watched System Sensor | Honeywell Building Technologies System Sensorās webinar on the L series and basically the 15/75 setting is no longer valid:
WARNING: Deep technical info.
(Copied from the FAQ slide at 39:38)
Prior to 2005 the 15/75 cd rating was relevant since the NFPA 72 and ADAAG had different requirements.
[list=1]
[*]ADAAG referenced ANSI/UL 1638 which only considers strobe performance on-axis
[*]NFPA referenced ANSI/UL 1971 which considered performance at [u]various angles[/u]. A 15/75 cd device is equivalent to a 15 cd device since it only provides 6 cd at 60-degrees
[/list]
As of 2010 the Department of Justice (DOJ) published the 2010 ADA requirements, which harmonized the requirements with the 2002 edition of NFPA 72, thus the 15/75 cd is no longer valid. The 15 cd strobe is the standard setting for typical small spaces like hallways.
Also interestingly, they say the new backplate is flimsier so that if you overtighten it, itāll flex instead of breaking. Iāll leave you to decide whether thatās a feature or an excuse.
I know people have been wondering what is going to happen to the advance and when, but I just received something in System Sensorās newsletter that states that:
-All of the Advance devices that the L Series directly replaces are discontinued
-All Low Frequency Devices, Outdoor Devices, Mini Horns, and MNS Strobe plates and āRelated Devicesā will still be made
Seeing how so many people seem to mindlessly hate the advance, I donāt see why people like it all of a sudden.
The L series sounds the same as the Advance on its default tone; so weāll still be able to hear the ear splitting tone in new installations. There really isnāt a difference besides the changeable lenses and the new tone option and their appearance in general.
Me too. Wouldnāt it be nice to get away from the ear splitting Advance tone? Unfortunately due to the 520hz requirements on all new Fire Alarm signals I donāt think weād see it much and even then the Advance tone is the default and many places donāt even bother changing it. At least I believe 520 zh is now required on all regular signalsā¦maybe that still only applies to low frequency devices.
On a full retrofit it is likely that all the devices will be replaced. It is likely that devices will be added on a full retrofit because the AHJ might require update to current code.
However, on a service call to replace one A/V that failed during inspection, it will be just that device replaced. 4-wire device replaced with 4-wire device is the quickest and easiest. 4-wire devices are still needed.