Battery Sizing Code

Hi,

I found an article that talks to this topic in the beginners section, what I would like to know is if anyone can point me to the section of NFPA 72 that has the standby and alarm time frames.

Thank You

If I can recall correctly:

For Standard systems the alarm time battery power is 5 Minutes. and 24 hours standby time. For voice evacuation systems it’s 15 minutes alarm, 24 hours standby.

Edit: Heres the link: http://www.nfpa.org/Assets/files/AboutTheCodes/72/ProposedTIA1188_NFPA%2072_Battery.pdf

ccs46 is right on his numbers.

it’s all in chapter 10 of the nfpa72, under the power supplies section (specifically the capacity of the secondary power supply).

drops to 4 hours when used with a generator

Thank You every one who replied. I found some information, and can dig a little deeper now. much appreciated