Hello,
I’m looking to add leads to a passive heat detector that comes with 6" leads. The system is composed of thermal-mechanically actuated NO contact “heat detectors” on a 24VDC supervisory system. Each detector is in parallel with the EOL resistor (see image link below). I’m being pushed by my senior engi’s to use a splice box that meets the NEC conductor splicing requirements. The issue is that at this location there is no where to put a box within less than 6" of the device without being an obstruction. I personally don’t see how adding leads via buttsplice/solder w/ shrink wrap to an extremely low current low voltage system would require NEC code compliance so I wanted to get input from experts on Fire Protection installations such as yourselves. My question boils down to: do I need to provide an NEC code complaint splice box to splice extensions to the OEM conductors?
We are installing these heat detectors:
https://kidde-fenwal.com/Public/System_Details/Fenwal-Controls/DETECT-A-FIRE-Fire-and-Overheat-Detectors
Here’s the wiring config: https://i.ibb.co/0GkyBLL/Attach.png