Hello everyone. My panel that I have made goes into alarm when the circuit is closed. How can I use a relay to change the N.C. coming from sensors to N.O. that the panel accepts.
Thanks!
Home Burglar Alarm Relay
Forum rules
Do NOT publicly post default codes for ANY security system or fire alarm panel.
(Rule #8)
Do NOT publicly post default codes for ANY security system or fire alarm panel.
(Rule #8)
- hhenry1234
- Casual Participant
- Posts: 71
- Joined: Thu Dec 25, 2014 8:31 pm
- Location: Cincinnati
Hudson Henry
American Sound & Electronics
PC Telecom
American Sound & Electronics
PC Telecom
- kcin556
- Administrator
- Posts: 1154
- Joined: Thu Jul 11, 2013 2:18 pm
- YouTube Username: kcin556
- Location: Milwaukee, WI
- Contact:
All relays are shown de-energized. When power is applied, the new relay will automatically open and will only close when connectivity through the zone is lost, whether by a device activating or the wires being damaged. Keep in mind that all devices on the zone must be connected in series for the zone to work.
- Attachments
-
- NC to NO.JPG (66.28 KiB) Viewed 1216 times
Nick - Administrator
Please send me a PM if you experience any issues or have any concerns. Thank you!
kcin556 on YouTube
Please send me a PM if you experience any issues or have any concerns. Thank you!
kcin556 on YouTube
- hhenry1234
- Casual Participant
- Posts: 71
- Joined: Thu Dec 25, 2014 8:31 pm
- Location: Cincinnati
Thanks, exactly what I needed 