Hello,
I am currently using the 4100ES.
I measured 34V from a detector connected to the M5 IDNet card, so I removed DIP 46 detector.
I completely disconnected the wire as well.
34V is measured from the IDNet card, while other cards read between 28-29V.
The jumper is set to Class B.
When I remove one, all connected detectors change to a “No Answer” status.
I confirmed this behavior with detectors connected to other IDNet cards.
However, even after removing the 46 detector on the M5, it still appears to be normal.
In fact, the removed detector 46 is still shown as normal and is being updated with the Current Value and Average Value.
I am confused…