What if my schools had been built with different fire alarm systems?:
In this post, I want to imagine “alternate realities” where the schools that I attended had different brands of fire alarm systems. This is my second time attempting to write this post, as the first time it got accidentally deleted after multiple hours of research and typing and getting around 2/3rds of the way done, so bear with me.
Daycare/Pre-School (At a church/Catholic school):
This church was built in the late 1800’s with a school being added at some point in the early 1900’s. There was most likely a pull rod system in the school when it was built, and then the school most likely got some sort of AC system in the mid 1900’s. In the late 90’s, the school got a complete fire alarm system overhaul. In 2009, the church was renovated, the FA devices got replaced, and the system was expanded to the church. The first floor of the school was renovated in 2015, and the devices remain mostly the same except for the addition of some new Notification Appliances in rooms that were previously lacking notification. For simplicity, I will only be discussing the 90’s system onwards.
Actual System:
Panel: Simplex 4005 (upgraded to 4010 in 2009)
Notification Appliances: The school has mostly Wheelock NS-24(XX)W-FR horn/strobes and RSS-24(XX)W-FR remote strobes with a few Simplex 4906-9127 TrueAlert horn/strobes added in 2015. The church got Simplex 4906-9127 horn/stobes and a 4906-9102 remote strobe installed in 2009. The horns are coded to continuous.
Pull Stations: The school has Simplex 2099-9001 conventional pull stations that are likely original to the 90’s system. The church has Simplex 4099-9001addressable pull stations that were added in 2009.
Smoke Detectors: The school has Simplex 4098-9601 Conventional TrueAlarms that replaced Simplex 2098-9201s in 2015, while the church has 4098-9714 Addressable TrueAlarms that were added in 2009.
If it was a Cerberus Pyrotronics/Siemens System:
Panel: Cerberus Pyrotronics PXL (upgraded to a Siemens FS-250 in 2009)
Notification Appliances: The school has mostly Cerberus Pyrotronics U-HN-S17S horn/strobes and U-S17S remote strobes with a few Siemens ZH-MC-R horn/strobes added in 2015. The church got Siemens ZH-MC-R horn/stobes and a ZR-MC-CR remote strobe installed in 2009. The horns are coded to continuous.
Pull Stations: The school has Cerberus Pyrotronics MS-51 conventional pull stations that are likely original to the 90’s system. The church has Siemens MSI-10B addressable pull stations that were added in 2009.
Smoke Detectors: The school has conventional Siemens OP121 smoke detectors that replaced Cerberus Pyrotronics PE-3s in 2015, while the church has FP-11 addressable smoke detectors that were added in 2009.
If it was an EST/Edwards System:
Panel: EST LSS4 (upgraded to a QuickStart QS4 in 2009)
Notification Appliances: The school has mostly EST 757-7A-T horn/strobes and 202-7A-001 remote strobes with a few EST G1R-HDVM horn/strobes added in 2015. The church got EST G1R-HDVM horn/stobes and a GCFR-VM remote strobe installed in 2009. The horns are coded to continuous (including the Genesis devices, which have their jumpers cut).
Pull Stations: The school has EST 270-SPO conventional pull stations that are likely original to the 90’s system. The church has EST SIGA-278 addressable pull stations that were added in 2009.
Smoke Detectors: The school has conventional EST 711U smoke detectors that replaced EST 6270Bs in 2015, while the church has SIGA-PS addressable smoke detectors that were added in 2009.
If it was a Fire-Lite System:
Panel: Fire-Lite Sensiscan 2000 (upgraded to an MS-9200UDLS in 2009)
Notification Appliances: The school has mostly System Sensor P2415 horn/strobes and S2415 remote strobes with a few System Sensor P2R horn/strobes added in 2015. The church got System Sensor P2R horn/stobes and an SCR remote strobe installed in 2009. The horns are coded to continuous.
Pull Stations: The school has Fire-Lite BG-10 conventional pull stations that are likely original to the 90’s system. The church has Fire-Lite BG-12LX addressable pull stations that were added in 2009.
Smoke Detectors: The school has conventional System Sensor 2W-B smoke detectors that replaced 2400s in 2015, while the church has SD355 addressable smoke detectors that were added in 2009.
Elementary School:
This building was opened in the fall of 1994. In 2015, the FACP was replaced with an addressable panel and all of the initiating devices were replaced with addressable variants, but the original notification appliances were not replaced. In 2019, a portable building with four classrooms was added. That building received new fire alarm devices when it was brought in. In 2025, the addressable fire alarm initiating devices were removed from the portable building to be used as spares elsewhere, and the portable building was demolished.
Actual System:
Panel: Simplex 4002 (Replaced with a 4007ES in 2015)
Notification Appliances: Mostly Simplex 2901-9838 horns on 4903-9105 strobe plates with 4904-9105 remote strobes in a couple of restrooms. The portable building had Simplex 4906-9127 TrueAlert horn/strobes. The horns are coded to continuous.
Pull Stations: Simplex 2099-9101 conventional pull stations (replaced with 4099-9006 addressable pull stations in 2015) The portable building also had Simplex 4099-9006 addressable pull stations.
Smoke Detectors: Likely originally Simplex 2098-9201 conventional smoke detectors (replaced with 4098-9714 addressable smoke detectors in 2015). The portable building also had 4098-9714s.
If it was a Cerberus Pyrotronics System:
Panel: Cerberus Pyrotronics System3 (Replaced with a Siemens FC922 in 2015)
Notification Appliances: Mostly Cerberus Pyrotronics MTS-15 horn/strobes with S15-SGL remote strobes in a couple of restrooms. The portable building had Siemens ZH-MC-R horn/strobes. The MT horns are set on continuous horn, and the other horns are coded to continuous.
Pull Stations: Cerberus Pyrotronics MS-51 conventional pull stations (replaced with Siemens HMS-D addressable pull stations in 2015) The portable building also had Siemens HMS-D addressable pull stations.
Smoke Detectors: Likely originally Cerberus Pyrotronics PE-3 conventional smoke detectors (replaced with Siemens OP921 addressable smoke detectors in 2015). The portable building also had OP921s.
If it was an EST/Edwards System:
Panel: EST LSS4 (Replaced with an EST iO500 in 2015)
Notification Appliances: Mostly EST 792-5A-006 horn/strobes with 202-5A-001 remote strobes in a couple of restrooms. The portable building had Edwards G1R-HDVM horn/stobes. The horns are coded to continuous, with the Genesis devices having their coding jumpers cut.
Pull Stations: EST 270-SPO conventional pull stations (replaced with EST SIGA-278 addressable pull stations in 2015) The portable building had Edwards SIGA-278 addressable pull stations.
Smoke Detectors: Likely originally EST 6270B conventional smoke detectors (replaced with EST SIGA-PD addressable smoke detectors in 2015). The portable building also had SIGA-PDs.
If it was a Fire-Lite System:
Panel: Fire-Lite Sensiscan 2000 (Replaced with a Fire-Lite MS-9200UDLS in 2015)
Notification Appliances: Mostly System Sensor MASS2415ADA horn/strobes with SS2415ADA remote strobes in a couple of restrooms. The portable building had System Sensor P2RL horn/strobes. The MASS devices are set to 800hz continuous, and the other horns are coded to continuous.
Pull Stations: Fire-Lite BG-10 conventional pull stations (replaced with Fire-Lite BG-12LX addressable pull stations in 2015) The portable building also had Fire-Lite BG-12LX addressable pull stations.
Smoke Detectors: Likely originally Fire-Lite SD400 conventional smoke detectors (replaced with Fire-Lite SD355 addressable smoke detectors in 2015). The portable building had SD365s.
Middle School:
This building was originally opened in the fall of 2008. That section of the school has all wall mount speaker/strobes and remote strobes, and no signals in the classrooms. The 6th grade wing was added a year later in 2009. That area also has wall mount speaker/strobes and remote strobes, but the classrooms have ceiling mount remote strobes. In 2018, a few additions were added onto different sides of the school. Those areas also have wall mount speaker/strobes and remote strobes with ceiling mount remote strobes in the classrooms, but there are also wall mount horn/strobes outside.
Actual System:
Panel: Simplex 4100U with voice evac (possibly upgraded to ES at some point)
Notification Appliances: The 2008 areas have Simplex 4906-9151 TrueAlert speaker/strobes and 4906-9101 TrueAlert remote strobes. The 2009 area has the same devices, but with the addition of 4906-9102 ceiling mount remote strobes in the classrooms. The 2018 areas have the same setup as the 2009 areas, but with the addition of 4906-9131 TrueAlert horn/strobes outside. The speakers play this message and the horns are coded to continuous.
Pull Stations: The 2008 and 2009 areas have Simplex 4099-9001 addressable pull stations. The 2018 areas have 4099-9004 pull stations.
Smoke Detectors: All areas have Simplex 4098-9714 addressable TrueAlam smoke detectors
If it was a Siemens System:
Panel: Siemens FireFinder XLS with voice evac (possibly upgraded to Modular at some point)
Notification Appliances: The 2008 areas have Siemens S-LP70-MCS speaker/strobes and U-MCS remote strobes. The 2009 area has Siemens SEF-MC-R Speaker/Strobes and ST-MC-R remote strobes in most areas, and ceiling mount ST-MC-CR remote strobes in the classrooms. The 2018 areas have Siemens SE-MC-R speaker/strobes and ZR-MC-R remote strobes in most areas, with ZR-MC-CR ceiling mount remote strobes in the classrooms and Siemens AS-HMC-R-WP horn/strobes outside. The speakers play this message and the horns are coded to continuous.
Pull Stations: All areas have Siemens HMS-S addressable pull stations
Smoke Detectors: All areas have Siemens OP921 addressable smoke detectors
If it was an EST/Edwards System:
Panel: EST3 (Upgrade to EST4 planned for the summer of 2026)
Notification Appliances: The 2008 areas have EST G4RF-S7VM speaker/strobes and G1RF-VM remote strobes on G1RT trim plates . The 2009 area has the same devices, but with the addition of GCFR-VM ceiling mount remote strobes in the classrooms. The 2018 areas have the same setup as the 2009 areas, but with the addition of WG4RF-HVMC horn/strobes outside. The speakers play this message and the jumpers on the horn/strobes are cut for continuous coding.
Pull Stations: All areas have EST SIGA-278 addressable pull stations
Smoke Detectors: The 2008 and 2009
areas have EST SIGA-PS addressable smoke detectors, while the 2018 areas have Edwards SIGA-PD detectors
If it was a Johnson Controls System:
Panel: Johnson Controls IFC2-3030 with JDVC
Notification Appliances: The 2008 areas have System Sensor SPSR speaker/strobes and SR remote strobes. The 2009 area has the same devices, but with the addition of SCR ceiling mount remote strobes in the classrooms. The 2018 areas have the same setup as the 2009 areas, but with System Sensor SRL and SCRL remote strobes instead of the SRs and SCRs, and the addition of P2RK horn/strobes outside. The speakers play this message and the horns are coded to continuous.
Pull Stations: All areas have Johnson Controls JBG12-LX addressable pull stations
Smoke Detectors: All areas have Johnson Controls 2951J addressable smoke detectors
High School:
This building was opened in the fall of 2024. The system is fully voice evacuation and is compliant with modern codes for signal coverage. The fire alarm system also doubles as the lockdown alarm.
Actual System:
Panel: Siemens Cerberus PRO Modular with voice evac
Notification Appliances: Siemens SLSPSWW-F, SLSPSCW-F, SL2SPSWW, and SC-SS-CW-F speaker/strobes and SLSWW-F and SL2SWW-F remote strobes. The speakers play this message .
Pull Stations: All areas have Siemens XMS-S addressable pull stations with STI Stoppers
Smoke Detectors: All areas have Siemens OP921 addressable smoke detectors
If it was an Autocall System:
This would have been almost as likely as the Siemens system, as my school district’s security system partner is the Autocall distributor in my area, and the Siemens distributor in my area is my school district’s technology and automation partner.
Panel: Autocall 4100ES with voice evac
Notification Appliances: Wheelock/Eaton ELSPSTW and ELSPSTWC speaker/strobes and ELSTW remote strobes. The speakers play this message.
Pull Stations: All areas have Autocall A4099-9004 addressable pull stations with STI Stoppers
Smoke Detectors: All areas have Autocall A4098-9714 addressable smoke detectors
If it was a Potter System:
This would have been less likely, but still possible, as there is a Potter dealer in my area.
Panel: Potter AFC-1000V
Notification Appliances: Potter SPKSTR-24WLPW and SPKSTR-24CLPW speaker/strobes and GES3-24WW remote strobes. The speakers play this message.
Pull Stations: All areas have PAD100-PSSA addressable pull stations with STI Stoppers
Smoke Detectors: All areas have Potter PAD300-PD addressable smoke detectors
If it was an Edwards System:
This would not have been too likely, but it would have been possible, as there is still an Edwards dealer in my area.
Panel: EST4 with voice evac
Notification Appliances: Edwards G4SVWF and GCSVWF speaker/strobes and G1VWF remote strobes. The speakers play this message.
Pull Stations: All areas have Edwards SIGA-278 addressable pulll stations with STI Stoppers
Smoke Detectors: All areas have Edwards SIGA-PD addressable smoke detectors
If it was a Gamewell-FCI System:
This also would have been possible, as the Gamewell-FCI dealer in my state services my school’s fire extinguishers.
Panel: Gamewell-FCI E3 with voice evac
Notification Appliances: System Sensor SPSWL, SPSWLED, and SPSCWL speaker/strobes and SWL and SWLED remote strobes. The speakers play this message .
Pull Stations: Gamewell-FCI MS-7 ASF single action pull stations with STI Stoppers
Detectors: Gamewell-FCI ASD-PL3s