Make Up a System (2.0)

New System (2030- foreseeable future):

Here, I want to go over what I think could be some possibilities if the system is replaced. I’ll start with what I think is most likely, and then move onto other possibilities.

If they decide to stay with Simplex:

Panel: A 4100ES upgrade kit is installed for the 4100U, as well as the components that are necessary for IDNac devices.

Notification Appliances: The existing devices are kept, but some that need to be moved, or are not functioning properly are replaced with the equivalent Eaton Eluxa devices. The new areas receive the appropriate Simplex TrueAlertES speaker/strobes and remote strobes, with white covers that have “ALERT” lettering (for potential future use).

Pull Stations: The existing devices are kept, but the new areas (as well as any areas with faulty devices) receive Simplex 4099-9004 addressable pull stations.

Smoke Detectors: All areas (including the new areas) have Simplex 4098-9714 smoke heads on 4098-9792 addressable bases.

Annunciator: Nothing is changed, except the labels are updated to 4100ES labels.

If they decide to go with Autocall:

Panel: All of the components that need to be changed to convert to an Autocall 4100ES are replaced. The existing Simplex 4100U cabinets are reused.

Notification Appliances: The existing devices are kept, but some that need to be moved, or are not functioning properly are replaced with the equivalent Eaton Eluxa devices. The new areas receive Eaton ELSPSTW-AL and ELSPSTWC-AL speaker strobes, and ELSTW-AL and ELSTWC-AL remote strobes. They all have white covers, and “ALERT” lettering (for potential future use).

Pull Stations: All areas receive Autocall A4099-9004 addressable pull stations.

Smoke Detectors: All areas receive Autocall A4098-9714 smoke detector heads, with A4098-9792 addressable bases.

Annunciator: The necessary components are swapped out, and the labels are changed to Autocall 4100ES labels.

If they decide to go with Siemens:

Panel: The existing 4100U is fully replaced with a Siemens Cerberus PRO Modular system with voice evac. It receives XDLC SLC cards, and XNLC addressable notification circuit cards.

Notification Appliances: All areas receive Siemens SA-SS-WW-F and SA-SS-CW-F addressable speaker strobes, and SA-ST-WW-F and SA-ST-CW-F addressable remote strobes. Because their lettering can easily be swapped later, “ALERT” lettering is not needed.

Pull Stations: All areas receive Siemens XMS-S pull stations, with STI Stoppers (without alarms). This helps prevent accidental activation from touching the front of the pull station, which is a common issue with these devices.

Smoke Detectors: All areas receive Siemens OP921 addressable smoke detectors, with DB-11 bases.

Annunciator: The 4100U “Remote Command Center” is replaced with a Siemens CAB3 annunciator cabinet, with an SSD-C-REM annunciator, and an SCM-8 switch control module and an LVM remote microphone for voice evacuation control. All other bays are taken up by blank plates. This size of a cabinet is completely unnecessary, but it was selected because it would most easily fit the spot in the wall of the previous 4100U equipment.

If they decide to go with Potter:

Panel: Potter AFC-1000V

Notification Appliances: The NACs are set to Wheelock sync. The existing devices are kept, but some that need to be moved, or are not functioning properly are replaced with the equivalent Eaton Eluxa devices. The new areas receive Eaton ELSPSTW-AL and ELSPSTWC-AL speaker strobes, and ELSTW-AL and ELSTWC-AL remote strobes. They all have white covers, and “ALERT” lettering (for potential future use).

Pull Stations: All areas receive Potter PAD100-PSSA addressable pull stations

Smoke Detectors: All areas receive Potter PAD300-PD addressable smoke detectors, with PAD300-6DB bases.

Annunciator: Potter GTSA-7 color touchscreen annunciatior with voice evac controls in a cabinet

If they decide to go with Gamewell-FCI:

Panel: Gamewell-FCI GFP series panel with voice evac

Notification Appliances: All areas receive System Sensor SPSWLED and SPSCWLED speaker/strobes, and SWLED and SCWLED remote strobes

Pull Stations: All areas receive Gamewell-FCI MS-7ASF single-action addressable pull stations

Smoke Detectors: All areas receive Gamewell-FCI ASD-PL3 addressable smoke detectors on System Sensor B300-6 detector bases

This system is for a 9 bedroom (although 8 + an office would simplify things), 2 story + walkout basement SFR being remodeled into a transitional-living group home (R-4/small board&care, being treated as Condition 2 although Condition 1 may be justifiable, permitting a 13D system). Gas service is provided for fireplaces in the basement family room and main floor living room as well as mechanical equipment, and the walkout basement leads to a patio sheltered by a deck accessible from the main floor. There is also a 2-car attached garage, and an unfinished, presumably vented attic.

Rooms are as follows:

  • 2 basement bedrooms
  • 2 basement storage rooms and a mechanical room
  • A family room, bathroom, & kitchen in the basement
  • 2 full bedrooms and a closetless bedroom (the latter probably better off being an office) on the main floor
  • Main floor living, dining, multipurpose/family, & kitchen spaces
  • 1.5 bathrooms on the main floor
  • and 4 bedrooms & 2 bathrooms on the 2nd floor

Life Safety

Passive Measures

The door from the basement stair to the basement storerooms is retrofitted with a Tell 12641 PA AL closer, as it is required to be self-closing to meet NFPA 101.

Suppression

It is presumed for the purposes of this post that retrofitting a NFPA 13R system is required as per IBC R-4 Condition 2 sprinkler requirements. (IBC R-4 Condition 1 and NFPA 101 would permit a 13D system for this instead.) Local requirements for backflow prevention also mean that an electrically supervised system is all but required (instead of using inherent supervision).

The garage is large enough that insulating and at least partially conditioning it is the only practical sprinkler retrofit solution short of resorting to an anti-freeze or dry-pipe loop, although the closet abutting it is left unconditioned, with a Reliable DH56 covering that space amply. This obviously isn’t practical for the covered patio, though, but fortunately, a single Reliable DH80 dry-sidewall sprinkler can cover that space, and is permitted to as per IBC 903.3.1.2.1. Both kitchens are also retrofit with Guardian-SSI 1384B mechanical UL300A wet chemical suppression systems in their kitchen hoods, monitored by the alarm panel.

Control

The alarm control panel for this system is a Napco Firewolf GEMC-FW32CNVKIT with the internal relay in line with the audible NAC for reset purposes, one of the programmable outputs also set up for reset to provide resettable power to non-audible detectors, and a GEMC-EZM8 at the panel for expansion. One of the telco lines is connected to the internet/telephone gateway, while the other telco line from the panel is connected to a Honeywell HW-AV-LTE-M-2 cellular dialer, with a relay module used to interface the dialer’s trouble output to a zone. Standby power for the system is supplied by a pair of 12Ah batteries.

Initiation

All living and sleeping spaces have 4WTA-B smoke detectors in them for a total of 4 detectors in the basement and 5 on each main floor, with these detectors all wired to the audible NAC to sound alongside the system horns. The panel location (2nd floor closet or mechanical room) gets a 4WT-B for self-protection, powered from aux resettable power, and there are Macurco CM-E1 CO alarms and GD-2B gas alarms on each floor, in addition to an additional GD-2B in the basement storeroom adjacent to the gas service entrance.

A single Napco FWC-CNV-PULLK pull station is present at the water service entrance or another suitable location, and the vented attic has 7 Thermotech 302-ET-194 stick heats in it in lieu of extending the sprinkler system into the attic.

Notification

The notification system consists of Eluxa ELMTSTs set for continuous tone in the kitchens and basement storage rooms along with Eluxa ELST strobes in the main corridors and all common spaces not otherwise covered, for a total of 16 15cd strobes and 1 30cd strobe (in the basement family room). The waterflow alarm is a Gentex GB6-120.

Security

Video

A Hanwha ARN-810S NVR with a few TB of WD Purple fitted into it provides recording capability for any IP cameras the place may wish. (It’s small enough and has active enough residents that doorphone security isn’t really called for.)

Panic

The GEMC-FK1 on the panel is set up for two-key panic or manual fire operation.

Communication

A Cortelco 121100TP227S analog telephone in a staff space is connected to Line 1 of the ISP-supplied MFVN gateway, which is fitted with a 24h battery. Line 2 is connected to the alarm dialer, and other phone services, such as a cordless phone, are connected via the dialer’s phone connection.

For a change of pace, this system is for a single-story branch location for a local credit union that is presumed to have a sprinkler system in addition to the obligatory security and access control measures. It also has an ITM in a drive-through lane with a canopy overhead.

Life Safety

The alarm system has two zones reserved for sprinkler monitoring, as it is presumed that this building is sprinklered due to being commercial new construction. The building is small enough to not have significant life safety needs otherwise, although there is an Exitronix S900C-SM-R exit sign/emergency light combo to direct folks to the auxiliary exit door and illuminate the corridor leading that way in case of a power outage.

Security

Passive Measures

All glazing in the building is presumed to be of a laminated, forced-entry-resistant type. The exterior doors are also heavy-duty hollow metal units, capable of accommodating multi-point locking mechanisms and forced-entry-resistant glazing. There are also fixed mullions in the main vestibule door frames to provide secure strike points for the door latches and locks, as well as direct traffic flow.

The (small bedroom closet sized) vault is presumed to be of a modular type, as is typical in modern financial institution branch locations. The data room and workroom receive a lesser degree of fortification using expanded metal mesh in the walls to provide secure mounting and protect them from cutting attacks.

In addition, both of the building’s main data connections are laid on separate paths using galvanized rigid steel conduit to carry the fibers, with the conduit laid in wet concrete and then backfilled with another 6” of concrete cover. This prevents someone from trivially severing the data connection to the building then jamming the cellular signal to the panel’s communicators to prevent the communications failure or the jamming condition from being reported to the monitoring station.

Alarms

The primary alarm panel is a Bosch B9512G with two B444 cell modules (one for each carrier). B915 keypads in the vestibule and workroom, and a D8108A attack resistant enclosure with an ICP-EZTS tamper to house the main panel and its batteries, with the panel located in the main workroom, near the data room, due to the small size of the vault. The onboard Ethernet port is used for video verification with Bosch cameras and as the primary alarm communicator.

At this main location, in addition to the panel, there is a B208 input expander and a B520 auxiliary supply mounted on D137 brackets. The panel is connected to 2 19Ah batteries to supply 72h of standby and 30min in alarm, and the B520 is connected to a third 19Ah battery in an Altronix BC100.

The remaining three B208 cards and another B520 supply card are located in the access control enclosure. Alarm notification is supplied by a Resideo AB12M at the base of the clerestory. All the alarm power transformers use D8004 enclosure kits to protect them from inadvertent disconnection.

Initiation

Initiation for the system consists of pairs of Magnasphere HSS-L2C-101 door contacts on all doors save for the inner vestibule doors, which have both a HSS-L2C-111 and a HSS-L2C-101 on each leaf. The vault and ITM doors have HSS-L2S-817s on them, and use Bosch ISN-SM-50 seismic sensors, with another identical sensor in the D8108A.

The glazing is further protected by Resideo/Honeywell FG1625RT glassbreak sensors, save for the glazing in the breakroom window, which receives 24-hour protection from a FG1025Z directional glassbreak. Motion detection is supplied by Bosch ISC-PDL1-WA18G dual tech motion detectors with their mask trouble contacts wired as tampers, and the IP camera system is used to video verify alarms. Honeywell 268 squeeze-action holdup switches are used at all teller stations and at the cash-handling table to provide holdup alarm functionality, and Honeywell 264 bill trap clips are also present in the teller drawers.

These detectors, as well as the locks on the vault and ITM, boil down to the following zone mapping, with the first 8 zones being the panel zones, the second 8 zones being on the B208 in the panel enclosure, and the remaining zones on the B208s in the access control enclosure:

  1. the panel’s seismic sensor
  2. the vault’s seismic & heat sensors (the latter being a FDD 7050C)
  3. the vault’s contact
  4. the ITM’s seismic sensor
  5. the ITM’s contacts
  6. the ITM lock’s shunt circuit
  7. sprinkler waterflow
  8. sprinkler supervisory
  9. JamAlert
  10. bell tamper
  11. duress/holdup, combining the holdup switches at the teller stations and the cash handling desk with the duress contacts on the ITM and vault locks and a set of bill traps in the teller cash drawers
  12. workroom exterior door (back door)
  13. workroom interior door (to teller area)
  14. breakroom directional glassbreak (alarm/tamper)
  15. breakroom directional glassbreak trouble
  16. workroom/breakroom motion sensors
  17. lobby/teller area motion sensors
  18. office 1 motion sensors
  19. office 2 motion sensors
  20. office 3 motion sensors
  21. main outer door contacts
  22. main inner door contacts
  23. main outer door deadbolt monitoring strike
  24. lobby/teller area glassbreaks
  25. office 1 glassbreaks
  26. office 2 glassbreaks
  27. office 3 glassbreaks
  28. hoteling room glassbreak
  29. hoteling room motion sensors
  30. server room contacts
  31. server room motion sensors
  32. entry vestibule glassbreak
  33. side door contacts
  34. side corridor motion sensor
  35. intercom camera analytics alarms
  36. office 1 door
  37. office 2 door
  38. office 3 door
  39. hoteling room door
  40. and keyswitch (arm/disarm) control from the access control system

The outputs to the ACS consist of a relay contact on the bell output signal, an arm/disarm output relay, and a trouble relay. (None of the detectors are configured to use latching outputs or alarm memory functions.)

Video Recording and Verification

A set of 15 Bosch NUV-3703-F04 dome IP cameras are present to provide the main video recording and verification functionality, set up as follows:

  • 2 cameras cover the lobby from each end of the clerestory
  • 2 cameras cover the teller area from the back wall
  • 1 camera is present in each office
  • 3 cameras cover the workroom
  • 1 covers the ITM and side door from under the canopy
  • 1 covers the area outside the front door
  • 2 cameras, 1 on the corner of the clerestory and the other on the corner of the building, cover the trash enclosure, back door, and associated breakroom glazing
  • 1 camera covers the server/data room
  • 1 camera covers the hoteling room
  • and 1 camera covers the hallway to the side door

This is supplemented by:

  • The camera in an Axis I8116-E intercom at the main inner door
  • and a Hanwha PNM-9000QB covert camera unit with SLA-T2480VA heads in the ITM and in signs at each teller station.

Recording and power functionality is provided using a Mobotix Mx-S-NVR1B-16-POE NVR with a pair of 10TB WD Purples in it for a full month of archiving and a Grandstream GWN7701P on the Mobotix NVR’s LAN port for extra camera ports. The NVR, in turn, is powered from an industrial 48V setup consisting of two Phoenix Contact PS-EE-2G/1AC/48DC/480W/SCs (1585287s) set for 54V and combined by a Traco TIB-REM480 FET redundancy module, backed up using a Nextys (TDK-Lambda) DCW20 DC-UPS with two cross connected strings of C&D UPS12-675PLMFs for 72.5h of battery life. The bank is protected from overcurrent by a 20A RK5 fuse in a fuseblock located on the wall next to the bank positive terminal. The NVR also monitors the Nextys’ dry contacts for power failure and low battery indications.

The two indoor supplemental cameras connect to PoE ports on the auxiliary switch, while the non-PoE ports connect to the intrusion panel as well as the two outdoor supplemental cameras and the NVR. Those outdoor supplemental cameras consist of:

  • an Axis P1518-LE on the side of the building, facing the driveway entrance, to provide an alarm-triggered LPR capability
  • and a Pelco SRXF3-8180-ERS to provide a wide-angle overview of the area outside the front door.

These cameras receive 12V power from a FPO75-E1 with a pair of 18Ah batteries in it, providing them with 6h of power.

Access Control

The ACS cabinet is an Altronix Trove1BL1R in the data rack. In addition to the Bosch expanders mentioned above, this cabinet contains a Mercury MP4502 control board that talks to the bank’s access control headend over a VPN tunnel, as well as a MR50-S3 that provides I/O expansion to interface to the alarm panel. An AL400ULB with a PD8ULCB and 2 12Ah batteries for 12h of runtime is used to power this all while providing room to add an additional door.

The readers for the ACS are HID Signo 20s, save for the back door, which receives a Signo 20K to permit 2FA. The intercom system is also tied into the ACS using an Axis A9210 network relay module to receive supervised door inputs and provide a remote secure relay output to unlock the door independently of the rest of the ACS “brains” – this module is powered from a PoE port on the video system’s supplemental switch.

The ACS controlled doors use Securitron CEPT power transfers with Accurate mortise locksets, consisting of:

  • a M9159ESEC-MP with AE (REX) on the back outer (workroom) door (the most vulnerable door to forced entry in the place)
  • M9159ESECs on the access controlled interior doors (to the workroom & data closet)
  • and additional M9159ESECs on the inner vestibule doors

The side door has a 9159SEC-MP on it, as it is presumed to not need access control, and the outer vestibule doors have 9122SEC-MPs with interior indicator trim on them to provide after-hours locking. Should the side door need access control, the lockset can be replaced with a M9159ESEC-MP, and there’s enough expansion capacity in the system to accommodate another MR50-S3 and an Altronix VR2T module to power a Signo 20 at that door without enlarging the power supply or batteries.

Communications

A FortiGate FG-80F, Juniper SRX300, or equivalent UL listed dual-SFP firewall appliance provides the main firewall and WAN connections for the branch, with 2 fiber links (xPON or P2P) to 2 different providers. The uplink from the NVR is connected directly to the firewall appliance’s internal LAN switch, which also accepts a copper uplink from the main switch for the branch.

Power to this appliance is supplied by a Samlex SEC-1215UL charger and a C&D UPS12-705PLMF battery to provide 72.5h of standby as it carries traffic from the NVR and alarm system. The shipped power supply is used to provide a redundant backup.

Samuelsville Central YM/WCA; Samuelsville, Ind.

A sprawling architectural record of the city’s social and athletic evolution. Standing on the edge of downtown, it transitions from a 12-story 1920s high-rise into a series of mid-century modern mid-rise expansions. This facility has served as the city’s premier fitness and community hub through the Depression, the post-war boom, and the industrial shifts of the late twentieth century.

I. Architectural Heritage: From High-Rise to Mid-Rise

The building reflects a prestige collaboration between regional and national masters.

1920 & 1937 High-Rise: Designed by Samuel Hannaford & Sons of Cincinnati, these sections feature the firm’s signature neoclassical robustness. The exterior is anchored by General Bronze entrance doors and window frames.

Post-War Expansions (1948, 1956, 1965): Designed by Perkins & Will, these mid-rise additions shifted toward the “International Style.” They extensively utilized Pittsburgh-Corning glass blocks paired with Alcoa double-hung ventilating sections featuring Thermo-Pane insulating glass for superior thermal performance.

II. Athletic & Recreational Systems

The YM/WCA became a regional powerhouse for indoor sports, housing some of the most specialized equipment of the era.

The Bowling Alley (1948 Section): A six-lane facility featuring rare Backus semi-automatic pinsetters. In the early 1950s, these were modified with AMF controls to keep pace with modern league requirements. This joined the 1937 wing’s hybrid manual/Backus setup.

Gymnasia & Equipment: The athletic spaces are outfitted with a mix of Porter and Recreation Equipment Corp (RECO) gear.

The Pool: A moisture-heavy environment managed by specialized Herman Nelson dehumidifying units.

III. Electrical, Vertical Transport & Communication

Electrical: Standardized on General Electric (GE) gear throughout. Lighting features Sunbeam and Perfectlite fixtures (including electric exit signs), while the gymnasium and pool areas utilize high-output Holophane mercury vapor fixtures. Wiring is entirely Hubbell, including outdoor-grade moisture-proof units in the natatorium.

Elevators: The 1920s high-rise originally operated with manual Otis elevators, which were retrofitted with Autotronic automated controls in the late 1940s. The mid-rise expansions utilize basement-traction “black button” units.

Sound: A building-wide Stromberg-Carlson system handles general paging, but the gymnasiums feature high-fidelity, independent ALTEC-Lansing systems equipped with their iconic multicellular horns for maximum acoustic coverage in cavernous spaces.

IV. Mechanical & Climate Control

The building’s mechanical plant is a heavy-duty “York” ecosystem.

Thermal Plant: Heating is provided by York-Shipley (Y-S) boilers, while cooling and air conditioning are strictly York units.

Air Movement: Large-scale Buffalo Forge fans drive the internal circulation. The roofline is a forest of ventilation, including Swartwout “Airlifts,” ILG PRVs, and Jenn-Air units.

Cooling: A massive Binks cooling tower manages the facility’s heat rejection.

Controls: The entire pneumatic and electrical control logic was provided by General Controls.

V. Life Safety & Special Systems

The YM/WCA features a particularly unique fire protection and chronometry layout.

Fire Alarm System: A rare ACME (NYC) system serves the building. It features 10-inch single-stroke bells and semi-flush coded pull boxes. The 1956 and 1965 wings incorporate mid-century modern styling into the pulls.

Detection: The system is a hybrid of Fenwal heat sensors, Photoswitch beam sensors (for the long corridors), and Pyrotronics F3 ionization detectors tied into an FIU panel.

Clocks: Time synchronization throughout the twelve floors is managed by a Stromberg master clock system.

Maintenance & Sanitation: A high-capacity Spencer Turbine Co. central vacuum system serves the entire property. The building also features dedicated rooms for trash and linen chutes, equipped with self-closing fire-grade doors and spring-hinged hardware.

Plumbing & Hardware: Standardized on Kohler fixtures and Lockwood door hardware throughout all five phases.

VI. The 2026 Status

In 2026, the YM/WCA remains a vital “third place” for Samuelsville residents. While the 1920s Otis elevators still hum with their post-war Autotronic brains, the facility has become a point of pride for architectural historians, especially the preserved Alcoa window units and the rare ACME fire alarm signals that still protect the high-rise.

This system is for a 4 story + partial basement mixed-income condo building, presumed for the purposes of this exercise to be all-electric, with a small community room, package room, and on-site management office, as well as a single MRL elevator serving all floors and a single row of overhung parking off a rear alley. There is also a small, single-egress commercial bay at the ground floor level, but the commercial tenant is presumed to supply their own intrusion protection for this bay on an as-needed basis.

Life Safety

Control

The main FACP for the building is a PFC-6006 (yes), mounted in the main entrance vestibule, with a pair of 7Ah batteries in it. It uses its DACT lines to communicate down two different paths, with one connected to the ISP’s voice gateway and the other connected to the elevator cellular communicator’s voice port. It also has its Ethernet port tied to the management office network.

Initiation

System Sensor 4WTR-B detectors are used for elevator recall on all floors, with a 4WT-B fitted for self-protection of the panel. Napco FWC-CONV-PULLK pull stations are fitted in the riser room, management office, and commercial bay to provide manual initiation, and a 4WTR-B on a 12"x12" weathertight hatch into the machine space for the elevator provides machine space (“flashing hat”) smoke detection.

Notification

Alarm notification consists of System Sensor P2WLED-LFs in apartments with SEP-SPSWL-P expanders for the smoke alarm strobes in the H/V units and P2WLEDs in common areas. There is also a courtyard within the building, which is covered using P2GWKLEDs. Each of the main floors has an AL842ULADA NAC extender on it with 7Ah batteries to provide notification power, and the H/V unit smoke alarm strobes are powered from individual MP120KL modules.

There is also a Gentex GWHSR (Commander5) set for whoop tone and 15cd mounted at the FDC to serve as the waterflow alarm. Power for this is provided from the auxiliary power output of the PFC6006.

Emergency Lighting

PLT-50290 combo emergency light/exit sign fixtures provide exit guidance on the upper floors of the building. Egress lighting at the exit discharges is supplied using:

  • an Atlas WSPS12LED3K with a button photocell and a Fulham FHUPS1-UNV-12L-SD remote inverter for the side exit and
  • a pair of RAB WFRL4R99FA120WS fixtures in the rear exit access aisle, each with a Fulham FHUPS1-UNV-12L-SD inverter providing backup power and set for 3000K color temperature.

Lighting in the storm shelter is supplied using Satco 62-1700s in 62-1720-EM battery bases to serve as normal/emergency fixtures. Additional normal-only RAB WFRL4R99FA120WS fixtures illuminate the rest of the parking overhang with one fixture per stall or stall-equivalent.

Residential Life Safety

The unit smoke alarms are Gentex S units, save for the H/V units, which use a combo of PL1AS alarms in the bedrooms and living rooms with a Gentex SR over the door to act as a remote relay for the PL1ASes so that they can trigger the strobes.

Emergency Communications

The elevator communicator is a K-Tech Connect with a generic (USB Video Class) HDMI-to-USB dongle plugged into it, accepting the HDMI output from a Hanwha QND-8011 camera. The traveling cable is a Prysmian Draka Cat5e unit carrying both 100BaseT connections in a single Cat5e cable, as well as PoE to the camera. To do this, there is a Tripp Lite NPOE-EXT-1G30 extender/repeater in/near the machine space to provide "OR"ing and normalization of the POE supplies from the NVR and from an Altronix NetWay1 injector powered from elevator communication backup power.

Power for the communicator itself is supplied at 5V using an Altronix VR6 card at the COP to step down the 24V supply on the traveling cable. An AL300ULXX with a second AL300ULB fitted provides power to both this communicator, with 2 12Ah batteries for 4h of talk time, and the area of refuge system, with 4 12Ah batteries in a separate BC400SG enclosure to provide 24h of standby + 4h of talk time. Both of these supplies are monitored by the spare zone on the PFC-6006.

That AoR system consists of a Snom D120 phone in a VE-ARSW enclosure with the Dual Air’s data port connected to one port on the D120 and the switch connected to the other port on the D120, as well as a Teltonika TSW101 switch that provides PoE to the D120 and to a set of 3 Viking E-1600-32-IP area of refuge phones. The K-Tech Connect also receives its network connection via the TSW101, and is daisy-chained in with a Grandstream HT801 to supply a phone connection to the communicator’s mating phone, run off communicator power via another VR6 card located in the supply enclosure.

Security

Access Control

The access control system consists of a Bas-IP AA-07FBI video entry panel at the main entrance with a SH-42 remote relay and a SH-12 remote Wiegand interface, a Grandstream GXV3450 videophone paired with a HT813 ATA in bridge mode in the management office, Bas-IP AU-04LAF apartment units in the H/V units, and a Honeywell MPA2C3-4 access controller, along with a Teltonika TSW114 switch running off a NVR port and 24V NVR power to tie the access controller, the videophone, and the apartment units together and provide an upstream connection to the NVR. (The HT813, GXV3450, and AA-07FBI are daisy-chained off a single switch port.)

The AU-04LAFs in the H/V apartments are equipped with an illuminated doorbell button at the entry door and System Sensor CHSCWL chime strobes fitted with LENS-G2 lenses inside the units to provide an audiovisual doorbell function to those units, all powered from a local 12VDC supply. There’s also a switch in each H/V unit bedroom that deactivates the chime strobe in that room.

The readers on the remaining doors consist of a Bas-IP MR-03KP for the parcel room door and ICT PRX-TSEC-MINI readers for the remaining exterior exits. The door locks themselves are Command Access ML180EUs with Command Access CDL power transfer loops and GRI MS20RS-T door contacts, as well as a fixed frame mullion at the main entrance to direct traffic and permit the use of mortise locks here. There are also postal locks connected to auxiliary inputs on the MPA2C3-4 to permit mail carriers to access the main entrance and package room.

Power for the main entrance doorphone, the office videophone and ATA, door locks, and the access control panel, as well as the CCTV system, is supplied by a LifeSafetyPower FPO150/150-D8E2 with a B100 card in it for 12V supply. Backup power (>24h of idle + 4h of full usage) for the ACS is supplied by a pair of 48Ah batteries in an EX-S4 “sidecar” enclosure, while the card for the CCTV system is connected to a pair of 18Ah batteries to provide 4h of backup time for that side of the security system.

CCTV

The CCTV system consists of a Speco N16WNRN4TB NVR, an EtherWAN EVB200 to convert 24V from the LSP supply to 48V for the recorder, and the following cameras and sensors, in addition to the entrance panel’s camera and the camera in the elevator:

  • A Hanwha ANV-L6012R IP dome camera at the back door, under the overhang
  • Hanwha ANO-L7012R IP bullet cameras at the front and rear of each side of the building, providing full coverage of both sides
  • a Speco CVC605CMT5 HD-TVI corner camera on a GeoVision GV-GVS2100 encoder to cover the package room
  • an Axis M3085-V with a T6101 Mk II portcast interface monitoring a FG1025Z directional glassbreak for the management office
  • and another Axis M3085-V/T6101 Mk II pair for the front door camera, this time monitoring a FG1625RT non-directional glassbreak located inside the vestibule.

Miscellaneous

The management office has a FortiWifi-60F for network security & LAN/WLAN connectivity. The FortiWifi’s dedicated DMZ port is connected to a Ruckus R350 AP with Unleashed firmware installed to provide WLAN connectivity in the lobby and community room. The ISP supplied voice gateway for the management office’s internet service is ordered with 24h backup, with its primary phone line tied to the HT813 to permit the management office to make phone calls during power outages.

1 Like

This system is for a locally historic, fully sprinklered seven-story + mezzanine + basement high rise (~80’ from grade plane to the top floor) that is being converted from office/ground floor commercial to residential (R-2 apartments)/ground floor commercial.

Life Safety

Fire Alarm & Voice Evacuation

The FA and voice evac required for a building of this size is supplied using an Advanced Axis AX networked system. The hardware consists of:

  • an AX-CC2-16 with 18Ah batteries and an AX-DSP in the FCC, and its internal amps wired to the stair tower and elevator car NACs respectively
  • 2 AV-VBs with 7Ah batteries on the ground floor
  • an AV-VB with 7Ah batteries on all the other floors
  • an AX-LED16RY in an AX-LZA-CAB1 to provide “first look annuncation” at the building’s south entrance (adjacent to the FDC)
  • two Class X SLCs (yes, the Soteria devices have built in isolators) for the whole building, with one dedicated to NAC modules for the apartments and the other handling all other SLC duties
  • and a Bosch B465 monitoring the panel’s discretes to serve as the (IP) communicator feeding one of the ports on a 2N EasyGate IP+ powered from a diode-OR of FACP and AOR power, as one of the downsides of the Axis AX is that its DACT module is rather janky/hard-to-get.

Initiation

Initiation consists of:

  • per-floor waterflow & supervisory switches
  • full corridor smoke detection on each floor above the first (as compensation for the relatively poor egress layout of the building) in addition to smoke detectors for recall service
  • self-protection smoke detection in the FCC and the various electrical closets
  • supervisory circuits for the smoke control system, including an SL-DA4R-P duct detector to provide smoke shutoff for the stair pressurization fan
  • an addressable pull station in the sprinkler riser room
  • and a CO and fuel gas detection system in the existing boiler room and at the gas service entrance in the southeast storage room, consisting of:
    • a pair of standalone QEL Q5-CH4-100L-0-A detectors sharing an IDC, with one for each room
    • a 24VAC gas shutoff circuit, controlled by and powering the Q5s, that also provides a fail-safe prealarm signal to the FACP
    • and a System Sensor CO1224TR on the ceiling of the boiler room, monitored by a FACP monitor module.

Notification

The building uses Eluxa devices throughout, with a mixture of ceiling and wall mount speakerstrobes and ceiling mounted infill speakers along with wall mounted remote strobes and wall mounted speakers in audible-only zones. The existing waterflow alarm device is retained as part of the conversion, though.

The amplifiers in the AV-VBs are set up as primary/backup pairs driven from the Axis AX network with Class A trunk/corridor NACs; this provides a fully redundant setup.

Fire Pump & Standby Power

A containerized diesel genset on the roof supplies standby, fire pump emergency, and a small amount of miscellaneous emergency power to the building. The genset has the obligatory remote annunciator at the FCC, and is also monitored by several fire alarm monitor modules.

Transfer is handled using a 480V Cummins OTEC switch for legally-required and optional standby. A single ETC SC1008 mechanically held BCELTS running at 277V serves as the emergency power switch, though, as all it has to power is the 3kVA 277/120V transformer feeding the outlets and HVAC in the FCC.

The fire pump controller is also a transfer type, using a Master MCRT primary reactor transfer controller driving a relatively modest vertical in-line pump. (The building just barely meets high-rise criteria, so it doesn’t need a fancy variable speed controller or even a full jockey pump.)

Annunciation

Primary annunciation is provided by the AX-DSP in the AX-CC2-16, located in the FCC on the ground floor. This room also has the other required annunciators for the elevator control system and standby generator in it.

The AX-LED16RY at the south entrance provides “first look” LED annunciation consisting of the following:

  • Solid yellow LEDs for system or floor troubles, rescue comms trouble, CO/gas trouble, stair pressurization trouble, or fire pump trouble
  • Flashing yellow LEDs for system or floor sprinkler supervisory, generator trouble, or elevator recall
  • Solid red LEDs for system or floor alarm (smoke detected), rescue comms alarm, stair pressurized, CO or gas alarm, or fire pump running
  • And flashing red LEDs for system or floor waterflow, fire pump running on generator power, stair pressurization smoke shutdown, gas shutdown, or machine room smoke

with the annunciation zones organized with Floors 7 to 1 and the basement from top to bottom on the left, and the following annunciators on the right:

  • System Status
  • Rescue/Elevator
  • Boiler Unsafe
  • Fire Pump/Genset
  • Stair Pressurization

Residential Life Safety

The in-unit smoke alarms are generic 120V units. CO and fuel gas alarms may or may not be needed, depending on whether heat and hot water for the apartments is being supplied by in-unit combustion appliances or by the building’s central boiler plant.

The speaker and strobe NACs for the apartments are supplied off individual NAC modules; this prevents a fault in an apartment from taking down notification in other units.

Stair Pressurization

The stairwell pressurization fan is a Canarm AX variable speed unit located on the third floor to provide direct single-point injection into the stairwell, with a combination baro-relief and powered anti-chatter damper in the stairwell penthouse. (It is presumed that an enclosure is added to the stairwell at the basement level, as that stairwell was previously open to the basement.)

The aforementioned addressable duct detector is used to provide smoke shutdown for the fan, while fan proving is accomplished using an AC case fan mounted in the duct to generate a low AC voltage from the airflow across it, along with an industrial optocoupler module to provide a dry output from that “wet” AC input. The fan speed is preset using a Bourns 3059L-1-503LF wire leaded multiturn trimmer mounted in a junction box adjacent to the fan.

Egress Lighting

The building’s existing light fixtures are modernized with LED emitters and per-fixture emergency drivers/inverters to provide normal/emergency lighting in corridors, common areas, and commercial tenants. The FCC, storm shelter, and some electrical spaces, however, use emergency mini-inverters driving surface-mounted utility fixtures, but with enough battery in the inverter for 2h of runtime, and the sensor for the space cutting off power to the fixture even when it is in emergency (no sense burning battery to throw light around that nobody sees). The exit signs are also the existing units, modernized with LED bulbs, and the exterior lighting is retained intact as well.

Other FCC devices

HVAC service to the FCC is provided using a Daikin Oterra RXQ09SABU9-FTXQ09ASBU9 9kBTU mini-split heat pump and a Fantech HERO 150H-EC HRV. An auxiliary contact on the FCC’s lighting control sensor disables the heatpump outright and turns the ERV down to a low setting when the space is unoccupied.

The obligatory FCC telephone is a Snom D120 connected to the spare LAN port on the EasyGate via an Altronix NetWay1 injector powered from the Area of Rescue supply. It also provides firefighters with a wired-of-sorts Internet connection via the passthrough port on the D120.

Elevator and Rescue Assistance Communications

All actual elevator and rescue assistance communications duties in the building are performed using a Rath/Janus/Avire 10-station SmartRescue analog AOR system. An additional station for this system is present on the ground floor, inside the stairwell, on the public side of the in-stair partition door. The two phones in the elevators are connected to a Viking LV-1K to annunciate elevator failure at the elevator landing and to a PAM-2 relay that sends that failure signal onward to the monitor module for the area of refuge system.

(Note that video communicators are not required during a change of use or elevator refit in an existing building in the jurisdiction I’m in since we’re on A17.1-2013 and IEBC Chapter 10 does not require compliance with IBC Chapter 30.)

The SmartRescue receives its 24VDC power via an Altronix PD16WCB located within the SmartRescue’s base station, which is in turned powered by one half of a LSP FPO75/75-E2 supply, with the SmartRescue supplying its own battery backup. The other half of this system supplies 24V to the EasyGate and 12V to a Hitron CODA cable modem via a B100 card, with 4 14Ah batteries for this half of the system to back it up for the 24h standby/4h operating requirements of NFPA 72.

The CODA provides a wired LAN drop to the EasyGate and a second wired LAN drop to the access control system, while the SmartRescue’s analog phone line is connected to the FXS port on the EasyGate. (Ideally, we’d use a voice gateway instead of the cable modem, letting us have analog lines down to the alarm communicator, area of refuge system, and the FCC telephone, but the Hitron gateways aren’t supported by the local ISP where this building is, and the Technicolor gateways they do support aren’t documented enough to permit them to be used for this application.)

Security & Access Control

Residential Access Control

The access control system for this building has to overcome one major problem: several of the commercial tenants on the ground floor can only be accessed via the building’s lobby, instead of having their own doors, and the accessible route to the basement tenant bay requires passage through the lobby as well. This requires three things to overcome:

  • the ability to access control the elevators (not terribly hard)
  • the ability to access control the interior stair above the first floor (which is possible, but requires the use of either stair reentry locking or an in-stair partition door)
  • and the ability to grant visitors to the building one-time access to the stair and elevators.

With this in mind, we wind up with a system that uses the automation functionality of a pair of 2N IP Verso 2.0 doorphones, one at each main entrance, to request visitor PIN codes from an Inner Range Inception access control system via the Inception REST API. This manual integration, while relatively complex-sounding, permits tenants to let visitors in off-hours while requiring a minimum of fire alarm interfacing, and also permits the lobby to function normally during business hours.

The south entrance doorphone is configured as a 1x3 with a camera module, mechanical keypad, directory display, and OSDP module, while the east entrance doorphone is configured as a 2x2 with a teleloop in addition to the aforementioned modules. Both of these doorphones are on the same LAN switch as the Inception and receive 12V from the access control supply directly. Each of these entrances also has an Inner Range SIFER reader (994723) at it, and the doorphone unlocks the door via a 2N security relay module to prevent “paperclip” and other forms of tampering based attacks.

The in-stair door on the ground floor and the elevators use SIFER keypad readers (994726) in order to accept PIN codes for guest access. There is also a CommFront RPT-485_422-2 RS-485 repeater powered from reader power using a Recom R-78W5.0-0.5 step-down module to serve as a bus splitter for the OSDP bus between the two elevator cars. The door contacts on the exterior doors, in-stair door, and interior doors are GRI MS20RS-T Magnaspheres.

All of this controls:

  • Von Duprin 5547 concealed vertical rod crashbar panics with E371L-BE electrically unlocked trims and Securitron CEPT power transfers on the historic south entrance doors
  • a Falcon 1790 pushpad storefront rim panic with a Command Access MLRK1-FAL17 electric latch retraction retrofit kit and a Securitron CEPT power transfer on the accessible (low energy operator equipped) east door
  • and a SDC S6303FH Spectra HiTower electrically locked frame actuator controlled mortise panic with a SDC LRSDC1R retrofit REX switch and a Command Access CDL transfer for that REX signal on the in-stair partition door on the ground floor

Additionally, the ACS receives arm/disarm signals from the security systems for the various tenant bays, with the exception of the northeast tenant bay on the ground floor, to determine whether the lobby should be considered open, with the east door electrically dogged and the south doors unlocked, or closed, requiring a credential or doorphone trigger for entry.

Common Areas

The common areas in the basement, consisting of two storage areas and an exercise room/storm shelter, are managed by the Inception, with SIFER readers at each of those four doors. The storage room doors themselves use a combination of a Falcon MA881 electrically unlocked mortise lockset and a Command Access CDL power transfer. However, the exercise room/storm shelter must function as an assembly space during storms, with sufficient occupant loads to require panic hardware. Furthermore, it must meet FEMA 361 & ICC 500 community shelter requirements, which means that the door hardware must be fully tornado rated and tested.

This is accomplished using Ceco/Curries StormPro door slabs fitted with Corbin-Russwin FE5400SA multipoint fire exit devices, Corbin-Russwin N9905 electrically unlocked trims, Securitron CEPT power transfers, McKinney SP3786NRP hinges, and Norton Rixson 7500 closers. The trims were chosen over electric latch retraction so that the door cannot be unlatched by debris impacts. These doors also have Securitron DPS-M contacts on them instead of the GRI Magnaspheres in order to maintain the UL windstorm listing of the door.

Individual Apartments

The individual apartment doors are solid wood slab doors with Marks 5 series mortise locks on them; this provides options for fine finishes and decorative lever trim, while being much sturdier than typical decorative-style residential mortise hardware at not much more cost.

Access Control Power, Networking, Modules, & Mounting

Power to the ACS and doorphones is provided by an Altronix AL1024ULXB2 power supply card and a VR10 regulator with a PDS16CB stacked on the VR10 and an ACM4CB module mounted on a BR1 bracket that isolates the door relays for the outside entrances from the access controller in addition to unlocking the stair partition door based on a FAI command from the FACP. This supply also provides 12V to a NetGate 2100 to provide WAN/LAN isolation & switching for the system.

These power modules and network devices, along with the Inception system consisting of its 996300NA controller, controlling the ground floor doors via the ACM4CB and directly handling the elevator readers as well, and the following Inception modules:

  • an Inner Range ILAM (996018PCB&K) for the basement doors, providing UniBus to:
    • a lift interface (996540PCB&K)
    • and a 2 door expander (996535PCB&K)
  • and an Inner Range LAN zone expander (996005PCB&K), providing a UniBus connection to:
    • another lift interface (996540PCB&K)
    • and any UniBus zone expanders required (which can go up to a triple-stack in the far lower right position)

This is all wrapped into a Trove2IR2 with the aid of double-stacked modules, along with a pair of 20Ah batteries for over four hours of backup power service. The WAN for this comes from the other port on the Hitron CODA; it doesn’t have cellular backup, but that’s OK in this case as it’s not providing intrusion reporting to a central station.

Strobes in all apartments? Will they be set to 15/110/177 cd depending on the apartment type?

Interesting, I haven’t heard of this brand before.

Since this is a conversion, will these “generic” units be PL1AS’s?

In the mixed-income building:

One could VE to horns in the non H/V units but the strobes do enhance visitability somewhat, as quite a few of the units in the building are designed to be handicapped visitable.

Aye, the building design for that building was done using 110cd for all apartments and 15cd for common and hall strobes save for a couple of 30cd strobes in larger common spaces.

Regarding the high-rise:

They’re owned by Halma (the parent company of Apollo), and could be considered the “native” panel brand for the Apollo protocols

In this case no. I’d have called out the PLACE units specifically if I wanted them.

Is this in a jurisdiction that has not adopted the 2021 codes then?

Correct indeed. (It’s also why some of the AoR systems aren’t UL2525)

Interestingly, Ontario’s building code started requiring strobes in residential units a few years ago:

(1) Except as permitted by Sentence (4), where a fire alarm system is installed, visible signal devices shall be installed in addition to alarm signal devices

. . .

(i) in living spaces in a suite of residential occupancy in a Group C major occupancy apartment building.

I regularly see listings for newer condo units in my area with a variety of horn/strobes or speaker/strobes: L-series devices (and, occasionally, Advances), Genesis devices, TrueAlerts, and Mircom 400-series devices seem to be the most common. I’m not familiar with other jurisdictions, but this may very well also be a requirement in other provinces.

This system is for a ~180 child daycare, treated as an E/I-4 combination, going into a ~12,500 ft2 commercial bay in a sprinklered single story warehouse building, previously inhabited by a business occupancy, with gas service to rooftop HVAC units and the kitchen. The other tenant has a heavy-vehicle service garage, warehouse, and office space within the building, none of which requires anything beyond sprinkler monitoring and perhaps CO detection.

Life Safety

Alarm Control

The fire alarm control unit for this building is a Fire-Lite ES-200X; while it’d be possible to cram this system into an ES-50X with some work, it’d leave no room for expansion whatsoever, and a Potter panel wouldn’t save any money due to the need for DACT and Class A cards. It has one of its DACT lines connected to an HW-AV-LTE-M-2 and the other DACT line connected to a MFVN voice port from the ISP (LIne 2 on typical business gateways) with a phone line downstream of it if need be.

The panel has 18Ah batteries in it, and provides a Class A SLC with Class A auxiliary power run alongside the SLC for non-smoke life safety devices. An ANN-RLY board connects it to a nearby SAFEPATH SP40S for voice evacuation and mass notification, with a set of 12Ah batteries in that panel for standby power and a Snom PA1+ SIP paging interface permitting it to be used for regular one-way paging duties from the telephone system.

The panel is programmed with custom zone types to handle CO, fuel gas, and security monitoring – this permits CO and gas notification via the EVACS, as well as correct reporting of all conditions to the central station.

Initiation

Smoke detection in the corridors and in the staff breakroom is required by NFPA 101 and is provided by SD365T smoke detectors on the SLC; this set of 10 smoke detectors also protects the panel itself (which is located in a corridor). CO detection for the classrooms and kitchen, though, is supplied using Macurco CM-E1 conventional CO detectors on monitor modules, including a dual monitor module for the kitchen. There is also a Macurco GD-2B fuel gas detector at the kitchen, connected to the other zone of the dual monitor module there, with the detectors powered from the Class A loop.

Other dual monitor modules receive the following input pairs:

  • the supervisory and waterflow switches from the sprinkler system
  • the walk-in panic and failure alarms
  • trouble/security alarm conditions from the access control system, as well as the office holdup switches.

There are also monitors for the kitchen hood suppression system and the voice communication system. Each of the three exits (main door, side door, and nursery) as well as the front reception desk has a BG-12LX pull station at it, and duct detection is supplied using SD365 addressable duct detectors in DNR housings at the supply and return of each AHU along with a single relay module at the AHU for shutdown. Finally, there’s a relay module at the nursery exit door to provide FA control of the delayed egress lock on that door.

The EVACS also can be directly initiated by the strobe output of a Midland WR120 weather radio in the lunchroom/storm shelter space, powered from the EVACS auxiliary power output using a Recom R78W9.0-0.5 DC/DC converter.

Notification

The notification appliances consist of:

  • ELSPSTW-N speakerstrobes in all classrooms, miscellaneous rooms and corridors, set for:
    • 1/4W and 15cd for regular rooms and corridors, and
    • 1/2W and 30cd for the lunchroom
  • ELSPKWC-N ceiling mounted speakers, set to 1/8W, to serve as infill speakers in the corridors
  • ELSTW-N remote strobes in the restrooms and kitchen, with the main restrooms getting 30cd strobes and the remaining restrooms and the kitchen getting 15cd strobes
  • EL4XSPSTW-N NEMA 4X speakerstrobes set for 1/4W and 15cd in the walkin cooler and walkin freezer spaces
  • a pair of AtlasIED VT-157UF speakers set to 8W to provide the 99dBA needed in the kitchen
  • and another pair of AtlasIED VT-157UF speakers set to 4W to provide the 85dBA minimum needed in the outdoor play area.

Exit Signage & Emergency Lighting

The exit signs in the building are CLPU2-RWRC lightbar style combination exit signs with RHLED1-PWP-MV remote heads. The exterior lighting, though, is left unchanged.

Miscellaneous Life Safety and Supervisory

The walk-ins are monitored by GRI T8800R temperature monitors powered from an AL125UL with a 7Ah battery in it. This supply also powers the LEDs on refurbished 3050CT panic switches at the walk-in entrance doors, with an EOL relay supervising that power supply, and a Seco-Larm SD-72051-V0 normally closed keyswitch for resetting the panic switches. The walk-in cooler also has a GRI 290-1 local door prop alarm on it. (There’s no need for a prop alarm on the freezer as it’s accessed from the walk-in cooler.)

There is also a Viking E-1600-20A-EWP analog emergency phone installed at the outside of the play area door and connected to FXS1 on the PBX. This permits the use of a double-cylinder deadbolt on the play area door; otherwise, it’d need a panic swinging into the building, which is an obvious security problem.

Security

The overall security system for this building is designed to meet PASS Tier I requirements, with intercom communications, monitored perimeter security & access control, doorphone visitor entry control, and perimeter video surveillance. There is also delayed-egress and glassbreak-triggered recording to protect the nursery exit door, and security film on all the glazing to provide passive resistance to breakage. Furthermore, both offices and the front desk have HUB-T holdup switches underneath the desk, connected directly to a security zone on the FACP.

Access Control

The access controlled doors have the following hardware on them:

  • The main doors use Falcon MEL1692NL-OP CVR storefront exit devices with ELR
  • The nursery exit uses a Falcon F-19-R-EO storefront rim exit device but with an Alarm Controls DE1200 delayed egress maglock on it
  • And the side exit door has a Falcon MEL-24-R–NL rim exit device with ELR

The access controller is also tied into the existing operator for the functioning dock door.

The front and side doors also have Bas-IP AV-06M doorphones on them with SH-12 remote Wiegand converters and SH-42 remote relays tied into the main access controller. The door contacts are GRI MS20RS-Ts on all perimeter doors except for the dock door, which has Magnasphere MSS-106S-Gs on it. There are also FG-1625RT glassbreaks for the glazing in the breakroom, stub hallway, playground door, and front vestibule, while the nursery glazing is protected by FG1025Z directional glassbreaks to permit it to have 24h glassbreak protection.

The access controller itself is a CDVI ATRIUM A22K with a 20Ah battery in it for 12+ hours of standby operation (including the delayed egress maglock). This controller uses zone-doubled inputs to monitor door contacts on the perimeter doors, the doorphone remote relays for the front and side doors, the glassbreaks, and the delayed egress lock on the nursery door. The two doors are controlled by the ATRIUM’s relay outputs, and the low current outputs are used to provide door unlock inputs to the remote Wiegand interfaces as well as controlling relays that unlock the dock door, trigger the nursery camera, and provide alarm and trouble outputs to the FACP monitor module that supervises this system.

Miscellaneous Locking

The classroom doors, while not electrified, are fitted with Cal-Royal SC8071 classroom security mortise locksets. The lunchroom/storm shelter needs ICC 500 compliant hardware, though, so it uses Steelcraft Paladin PW14 doors with Ives WS45 manual holders (this works because fire doors required only for ICC 500 compliance aren’t required to self-close), Ives 5BB1HW-NRP hinges, and Von Duprin WS-T-9957-2SI panic hardware with 996L-BE trim for the three main entrance/exit doors. The kitchen door, though, isn’t an egress door for the lunchroom, so it is a Ceco/Curries StormPro door fitted with a Sargent FM7390 classroom security holdback mortise lockset and a Norton Rixson 7500 closer to permit push-pull operation under normal circumstances, along with McKinney SP3786NRP hinges.

The play area door is a new hollow metal slab with a viewing window that uses a Schlage B662 OS-LOCxIS-LOC deadbolt under 2021/2024 Code provisions that permit double-cylinder hardware to be used on doors to exterior areas that do not have egress independent of the building. The door also has an Ives 8103EZHD pull handle and a LCN 4050A-CUSH closer on it for push-pull operation when unlocked.

Video

The video system consists of a Hanwha ARN-810S PoE NVR powered from the combination of a PSA-48-120 48V DIN rail supply in a junction box and a PSH-BCM360S DC-UPS/battery charger sharing an Altronix BC1240 enclosure with a 40Ah 12V battery. The cameras consist of LND-6022R dome cameras inside the entrance doors (front, side, playground, and dock), a LNO-6012R bullet camera monitoring the outside of the side door and dock door, and an Axis M3085-V minidome with a T6101 Mk II portcast interface monitoring the nursery exit door with the portcast interface using a supervised input to receive a recording trigger from the access control system.

Intercom

See this Make Up an Intercom/PA/Bell System Post for the intercom system for this building.

If they go with potter, cant they also use system sensor A/V’s?

They could, but I’ve never seen my local Potter dealer use System Sensor devices. It’s really all just speculation anyways. Overall, I’d be quite surprised if that building got anything other than a Simplex 4100ES, Autocall 4100ES, or Siemens Cerberus PRO Modular.

This system is for a total overhaul of a vacant single-story nursing home, presumably of frame construction, that converts it into a three-story independent senior living apartment building with two large courtyards, elevator access to all three floors, and a storm shelter/community room space. This totals up to 160 units, including 6 hearing/visual units, in what is presumed to be an all-electric building, as there is no sign of gas service to the existing building.

Life Safety

Control & Communication

The fire alarm panel for this building is a Potter AFC-50 with a CA-6075 card and a pair of 12Ah batteries fitted. A HW-AV-LTE-M-2 provides cellular communication from the relays on the AFC-50. Note that the FACP and NAC extenders live in the north elevator lobbies.

Initiation

The smoke detectors are PAD-300PHDs, located at all elevator lobbies and in relay bases on access hatches for the elevator machine spaces as it’s presumed this building will use MRL elevators. (The east elevator has an adjacent stair which can be used for access to this, while the other detectors need to be accessed from the roof instead.)

There is a PAD100-PSSA in the sprinkler room, and another behind the front desk.

Each elevator shaft also has a PAD100-TRTI for recall outputs, with the east shaft module connected to the initiating circuits from the Area of Refuge system and the north shaft module doing double duty as a sprinkler monitor.

Notification

A PAD100-NAC module provides a Class A control circuit for a set of NAC extenders, with 2 AL842ULADAs supplying the ground floor and individual AL1042ULADAs for the second and third floors. The actual notification appliances are Gentex Commander5 units, with GHS hornstrobes set to 15cd in the corridors, smaller amenity spaces & mailroom and to 30cd in the shelter space & larger amenity spaces, GS remote strobes set to 15cd in the storm shelter space restrooms, a GHSC set to 15cd to fill in a gap in the notification in a commons area, GHLF low frequency horns in regular dwelling units, GHSLF low frequency hornstrobes set to 110cd in the H/V units, and GWHS weatherproof hornstrobes set to 75cd to serve the courtyards.

The interior stair and cross-corridor doors are on Seco-Larm DH-171SQ holdopen magnets powered from the AUX1 outputs of the NAC extenders, which all have 7Ah batteries in them. The sprinkler hornstrobe is a MT4-115-WH-VFR set to whoop tone.

Residential Life Safety

The smoke alarms in the units are Gentex PL1ASes, chosen for their 520Hz support. The H/V units also have a Gentex SR in them to supply 120VAC to Edwards 203-8A-T strobes.

Emergency Communications

Emergency communications in the building consists of a combination rescue assistance/elevator emergency system using an EmerCom EMCS-MR consolidator as the core of the system. The phones consist of EMC-60-MSGs in each elevator, EMC-60s with their 9V NiMH backup batteries swapped for EMCS spare packs at the rescue assistance comms locations, and the handset in a EMC-FRM-ALRM at the north elevator lobby to serve as the master station. The other two communications alarms are EMC-ALRM units, located at the east and west elevator lobbies.

The video side of things is handled using Speco CVC605CMT5 cameras feeding an Axis P7304 encoder. Power to this is supplied using a LSP FPO75/75-2D8PE2 with:

  • one of the cards supplying AC-only power to the AoR and elevator phones
  • the other card feeding battery-backed power to the consolidator using a quad of 18Ah batteries in a SSU00506 trough
  • and an Altronix VR5BT with a 12Ah battery located in the E2 enclosure to provide 12V power to the DSL or cable modem, cameras, and encoder

Emergency Lighting

The emergency lights consist of:

  • RAB ECOMBO-RS combination self-test fixtures in the corridors
  • RAB EM-RS emergency light units in the stairs, also with self-test support
  • RAB WFRL4R99FA120WS wafers on individual Fulham FireHorse FHUPS1-UNV-12L-SD inverters under the overhangs and in the storm shelter areas
  • and RAB SLIMXXSY wallpacks on individual Fulham FireHorse FHUPS1-UNV-12L-SD inverters for the rear and side exit stair discharge doors

Storm Shelter Hardware

The storm shelter requires proper tornado-resistant openings to go with its tornado-resistant walls and framing, as well as being an assembly space with several panic exits, and to this end, it uses Winco ICC 500 rated fixed windows along with:

  • a Steelcraft Paladin PW14 door fitted with a Securitech 84T11-IHD-HVL 4-point CVR exit device, mortised-in Securitron MSS-1 contacts, Ives 5BB1HWNRP hinges, and an interior-mounted LCN 4040XP closer for the direct exit from the storm shelter space.
  • a pair of Ambico tornado rated doors in an Ambico fixed-mullion frame, fitted with Securitech 83T46-G1-IHD-HVL 3-point CVR exit devices with electrified classroom trim, Gallery GSH918 hinges mounted with jamb pin screws, Von Duprin EPT-2 concealed power transfers, LCN 4040XP closers, and GRI MS180-T contacts to serve as the main entrance to the community room/storm shelter
  • A single Ambico tornado rated door with a similar setup to the pair for the auxiliary entrance to the community room/storm shelter
  • And a single Ambico tornado rated door in an inswing configuration with Gallery GSH918 hinges, a Von Duprin EPT-2 transfer, a LCN 4040XP closer, GRI MS180-T contacts, and a Securitech 83L46-G1-IHD-HVL 3-point CVR mortise lock with electrified classroom trim

There is also a communicating door between two parts of the storm shelter; this door does not need to be tornado-rated, so it gets a Cal-Royal AF2200x2200PULNL.

Security

Access Control

The access control system for the building is an ICT Protege WX system consisting of a PRT-WX-DIN-IP controller and 5 PRT-HRDM-DIN expanders, stuffed into a Trove1DR1 enclosure along with an AL1024ULXB2 for power and a VR6/PDS16CB pair on a BR1 bracket for 12V and 24V distribution. The backup power for this consists of another quad of 18Ah batteries mounted in a SSU00506 trough below the Trove to give us 10h of runtime.

The contacts on the non-tornado doors are all GRI MS20-Ts, with Securitron CEPT transfers on the non-tornado-rated access controlled doors, and fastened mullions on all other double doors. The locking hardware consists of the following:

  • Cal-Royal A7700xESC7705xFLR7700 ELR storeroom function rim exit hardware on the outer and inner main vestibule doors
  • Cal-Royal AF7700xESC77/98EU electric-trim storeroom function rim exit hardware on the other resident entrance doors (this doesn’t need to be fire exit hardware, its just ordered that way as it’s the easiest way to get an A7700 less dogging)
  • Cal-Royal AF7700xNESC2230 rim passage fire exit hardware on the interior stair & cross-corridor doors
  • Cal-Royal AF7700EO36s on the stair discharge doors
  • and Detex V40xWs with 14BN trim and matching mullions on the doors from the courtyard into the building. (Even at 15sf/occupant, these courtyards are so large, at nearly 12000sf each, that they exceed the 300 occupant limit for double-cylinder doors on courtyards).

Visitor Management

Visitor sign-in is handled using a Surface Pro tablet running both the EVTrack backend software and the EVTrack Front Desk package (the latter using WSABuilds). Power to it is supplied using a standard Surface adapter via the power port on a StarTech USB-C to Ethernet adapter, and it opens the inner vestibule door using an Axis A9210 network relay in the access control cabinet. A StarTech IES5102 Ethernet switch connects everything together.

Dwelling Unit Security

Each apartment has a Cal-Royal SC8456 mortise lock with integral deadbolt on its front door.

Miscellaneous A/V

Each apartment has a Cat5e/RG-6 Siamese cable run to it, with 4-5 on the Cat5e carrying a phone line, 1-2/3-6 on the Cat5e reserved for IP services to apartments, and 7-8 on the Cat5e reserved for video or 2-wire bus services.

This cable terminates in a structured wiring panel with a video splitter, a phone splitter block, and a Cat5e rated patch panel in it; tenants have the options of DSL or cable for tenant Internet, and can either get phone service from the ILEC or as a tripleplay service from the cableco.

The offices are connected to two phone lines, with Line 1 being office-only and Line 2 being shared with the elevator phone system using a Viking LSR-1 powered from the 24V concentrator supply. The office phones are refurbished Nortel/Aastra 9417CWs, with the page line connected between them to permit intercom usage.

Accessibility

The H/V units are equipped with a visual doorbell system that consists of Alarm Controls TS-12T302NS pneumatic timer buttons for the doorbell buttons, Newhouse CHM24V chimes fed switched power via Securitron TM-2 timers in cyclic mode (and with the TM-2’s supplied MOV wired across them), Edwards G4EWN-G strobes in each room for visual notification with RCI 10R1-6 bridge rectifiers to provide them with 24VFWR, and 20VA/24VAC doorbell transformers to power it all. Each H/V unit bedroom also has an extra one-gang switch in it that can be used to cut off the visual notification strobes.

1 Like

System for large high school

Panel: Simplex 2001

Pulls: Simplex 4251-30s

Smokes: Simplex “whiffle ball” smokes

NAs: Simplex 2901-9806s mounted on 2903 light plates

Over the years, defective light plates were replaced by Space Age AV-32s and defective horns were replaced by Wheelock EH-EL1s.

The school was renovated and expanded in the early 2000s, the panel was replaced with a 4100u, and the new portions had Simplex multi-candela SmartSync TrueAlerts. All portions of the building got their pulls and smokes replaced with IDNet devices.

Then, in 2021, the panel got upgraded to a 4100es, voice evac was added, and all NAs were replaced with simplex conventional TrueAlert speaker strobes with ALERT markings.

1 Like

alright i guess i will take a crack at this.

Channel industries factory consructed 1921

in 1921 channel industries automotive part manufacturer constructed their first factory. It was a modern for the time single story 81785 square foot brick building, fully sprinklered, with a modern Tele-Call fire alarm system consisting of 10 inch single stroke bells and Tele-Call non-coded pull stations.

First upgrade 1938

In the spring of 1938 construction started on a new section of the factory that would add onto the existing factory adding a whole new production line and boiler house which would add an extra 5000 square feet to the building. Thus the sprinkler system and existing fire alarm system was upgraded to fit the existing needs, Benjamin electric company model 8846H electric horns were installed in the new section and boiler room.

Second upgrade 1943

As ww2 ramped up production also ramped up and thus 4 new production lines were added adding another 10,000 square feet primary constructed out of wood due to the on going steel shortage . This time the fire alarm system received an upgrade, in the form of a Autocall Model SA with Autocall non coded pull stations and a replacement of all original signals with Autocall single projector horns.

3rd upgrade 1949

Not much changed in the 1949 upgrades other than upgraded water chiller systems and a addition of a parking lot on the north side of the plant.

1st rebuild 1954

in 1954 a part of the 1920s era brick collapsed into the offices at the very front of the plant causing substantial damages to the building and its systems. the 1920s era offices were completely redone along with the sprinkler system in that part of the building.

4th upgrade 1962

in 1962 after a onslaught of problems in the facility regarding the aging fire alarm system. a new fire alarm system/monitoring system was installed. this was the autocall/howe plant protection system. this system managed both fire alarm activity along with waterflow and other life safety equipment. The system was controlled from a central PSD-1controller inside the main office with a PRS-5s printer. the devices consisted of CFW5-B combination stations along with F4B-S flow switches and 450 horns with single projectors for devices. along this time the plant received a massive expansion with 5 new production lines, a product test center, research and development, and a first aid room.

5th upgrade 1978

after a fire this time in the plants main chiller room, the chillers were replaced. and new horns were added

6th upgrade and rebuild 1986

in 1986 a portion of the world war two construction collapsed in one of the main hauls and the plant administration offices which were rebuilt. as a result of these collapses it completely totaled the fire alarm system and a full system overhaul was needed. the existing panel was replaced with an autocall cd-na fire alarm voice evacuation panel, all pulls were replaced with 4050-001 pull stations, and signals were replaced with autocall rebranded av34’s and av32s with federal signal directone 950b speakers behind them. along with these a few selectone 300’s were installed in the main plant production areas and areas with ambient noise above 60db. the flow switches were kept but the sprinkler system saw the addition of a fire pump.

7th upgrade 1999

In 1999 the fire alarm system recieved slight upgrades, a few of the 80s were replaced with wheelock mt-24lsm horn strobes and wheelock et1080 lsm speaker strobes. along with a few mt4 horns installed outside.

large electrical fire and eventual shutdown 2012

on march 21st 2012 at approximately 8:05pm a electrical fire started in a 480 volt main distribution panel which quickly spread to a large unit substation in the plants main electrical room. this fire completely totaled the room and a few surrounding rooms. the costs were too high to replace the substation and damaged mdp panels and other panels and the plant shutdown. luckily enough someone caught video footage of this event https://www.youtube.com/watch?v=42Kn9JlXE5w (note this is for lore purposes also headphone warning)

1 Like

T.K Stone Middle School (Elizabethtown, KY)

This School Was Built In 1954 (Formerly Elizabethtown High School), Renamed In 1972, And It Was Renovated In 1993, Added A New Hallway In 2001, Cafeteria Renovated In 2003, A Pool In 2013, And A New Entrance In 2025

The Main Panel Is A Early Version Of Simplex 4100ES, And 2 Simplex 4009s Hooked Up On The Panel It’s Located In The Office Hallways,

The Annunciator Is A 4602 Located In The Main Lobby

The Pulls Are 2099-9756, They Are Located In The Hallway Across The Gymnasium, 7th Grade Hallway, Main Lobby, Library, 8th Grade Hallway, And The Auditorium.

There Are 4099-9001 Pulls In The 2001 Addition, 2003 Cafeteria Renovation, And 7th Grade Rear Exit

The New Entrance Has 4099-9004

The Gym Has Older Autocall 4050 Pulls

The Pool Area Has 2099-9138 Pulls

The Alarms Are 2901-9838 Horns On 4903-9105 Strobe Plates, They’re Located In The 7th Grade Hallway, And Hallway Across The Gym

4904-9105 Strobes In The 7th Grade Restrooms

4903-9219 Horn Strobes In The Lobby, Library, And Auditorium

4906-9127 (TrueAlert Horn Strobes) Located In The 8th Grade Hallway, Gymnasium, Cafeteria, Band Room, 7th And 8th Grade Classrooms, And 6th Grade Hallway

There Are Red Wall Mount Simplex TruealertES Horn Strobes At The New Entrance

4906-9101 (TrueAlert Strobes) Located In The 6th And 8th Grade Restrooms

There Is A Early Wall Mount TrueAlert Horn Strobe Located In The Ceiling Located In The Nurse Room

The Pool Area Has 4906-9131 Weatherproof TrueAlert Horn Strobes

Note: The 8th Grade Hallway, Band Room, And Gymnasium Used To Have 2901-9838 On 4903-9105, The 8th Grade Restrooms Used To Have 4904-9105, They Added 4906-9127 Horn Strobes To 7th And 8th Grade Classrooms In 2003

Outside, There Is A Weatherproof Old Autocall Bell.

A Fictional High School: Nickelodeon High School Was Built in 1955 And It Had A Couch Fire Alarm System With Couch Fire Bells, And Couch Chevron Pulls

1965: 2 Bells Broke And Were Replaced With Simplex Bells

1975: A Fire Broke Out In The 9th Grade Hallway And The 9th Grade Hallway Alarms Got Replaced With 4040 Horns + 4050-80 Light Plates And The 9th Grade Hallway Pulls Were Replaced With Simplex 4251-30

1986: Another Hallway Was Added, A 2001 Was Tied To The Main Panel, The Alarms Are 2903-9101 + 2901-9833 And The Pulls Were 4251-20

1993: The School Was Renovated (Including The 9th Grade Hallway, And The 1986 Hallway), The New Panel Is A Simplex 4100 Classic With Simplex 4003, The Pulls Were 2099-9795 Everywhere Except For The Auditorium It Had 2099-9756 (Not To Mention The 2099-9795 In The Cafeteria And Gymnasium Having II Stoppers Under It), The Main Alarms Are 2901-9838 + 4903-9105 In The Library, Big Classrooms, Hallways, Lobby, Office, Band Room, Art Classroom, And Science Lab, There Are 4904-9105 Strobes In The Classrooms, Chorus Lab, Computer Lab, And Restrooms, The Gymnasium And Cafeteria Have 2901-9332 Bells + 4903-9105 Strobe Plates, And The Auditorium Having 4903-9105 + 2902 LifeAlarm Speakers, Outside There Is A 2901-9846, The Signals Do Slow March Time, The 9332s Do Continous, And The 2902s Do A Code 3 (But 2901-9838 Horn) And Message. Also A Luna’s Mexican Grill Was Located Next To The Cafeteria The Alarms Were Wheelock AES Horn/Strobes And The Pulls Were Notifier LNG-1R’s They Also Do Continous Like The 9332 Bells

That looks like it’s referring to the non-sleeping parts of apartment suites where each bedroom is rented out separately, since the common area is less of a private dwelling in that situation.