Make Up a System (2.0)

This takes way too long, anyways

Built in 1975 a 9 floor (It’s on a hill with the first floor being partially underground) collages library. Based on a combination of 2 buildings from different colleges campuses

4207 with coded inputs:

Alarms: 4050-80 Light plate with 4080 10" Bells, 4040 Horn with Projector (Originally outside, now inside due to the 2007 renovation)

Detectors: Statitrol 102-040s Flush smoke, Simplex 4265 Heat

Manual pulls: 4274-2 Coded

In 1994 the building received small renovations over 6 years and a new fire alarm system

4120 connected to the zones from the 4207

MISC: 4100-8210 Miniplex transponder, 4100-1292 Remote command center, 4100-0136 Coded pull module, 2098-9805 test station (for duct detectors)

Alarms: 4903-9329 Speaker strobe wall red, 4903-9161 Speaker strobe ceiling white, 4904-9136 Strobe wall red

Detectors: 4098-9701 Photo or 4098-9716 Ion or 4098-9732 Heat with 4098-9784 Base or 4098-9781 Base, CO1224T CO with 4090-9101 ZAM, 2098-9645 Duct, 4098-9709 Pendant duct

Manual pulls: 2099-9795 Pull with STI-1230 Stopper

In 2007 they add a large study space, self study rooms, more book stacks, secure storage for rare artifacts and additional offices. This makes an exterior wall enclosed and connects to part of the tower. In 2011 CO detection was added to both systems

4100U with info alarm display and fire suppression plaque:

MISC: 4090-9006 Suppression release peripheral, 2081-9046 Coil supervisory module, 2080-9060 Suppression disconnect, 2098-9806 test station (for duct detectors)

Alarms: 4906-9253 Addressable speaker strobe wall white, 4906-9254 Addressable speaker strobe ceiling white, 4906-9203 Addressable strobe wall white, 4906-9204 Addressable strobe ceiling white, AMT-24MCW-FR 3 tone horn strobe (Suppression)

Detectors: 4098-9714 Smoke or 4098-9733 Heat with 4098-9792 Base, CO1224T CO with 4090-9101 ZAM, OSI-R Beam with RTS151KEY Test station, 4098-9756 Duct, 4098-XAD-210 Aspirating/Aspirating duct, VLC-600 Aspirating (suppression), 4098-9754 TrueSense (suppression)

Manual pulls: 4099-9001 Pulls with STI-13520FR or STI-13510FR Stopper, 4099-9012 Suppression pull with STI-13320FR Stopper, SS2025AB-EN Abort with 4090-9001 IMA

1 Like

This is a small apartment fire alarm system, and it is 1997. The panel is sheltered but still exposed to outside conditions. The panel is an MS-5024 and it was installed at the apartment after the last parts of the apartment’s construction in mid 1997. This was a small fire alarm installation company that already knew about new kinds of alarms that were being manufactured. They used to install system sensor mass’s, but now they shifted to the new system sensor spectralert devices (now the classics). They also heard about the sync functions so they got the mdl too. At that time, there were no firelite panels with sync protocols, and synchronization existed, but was not required. This is why the company installed the ms-5024u and the mdl. The panel is located right beside the electrical room and the fire alarm system is completely local. The building is 3 stories tall and has 4 homes on each corner of the floors.

  • Above the panel there is an mdl, and then above mdl there is an indoor spectralert classic hornstrobe (Red First gen). The installation company used indoor devices outside thinking it would do nothing since they are is still sheltered. But little do they know…(Set to Code 3 high volume for outdoor and Code 3 low volume for indoor. Hornstobes were fixed 15 candela)
  • There were pullstations at every floor near the stairways, and more system sensor classics. The pullstations were BG-10s.
  • Sprinkler system was tied to the fire alarm system, but the flow-switch was unknown, because a separate department handled everything on the sprinkler system and the fire alarm installers had no access. But the switch was still tied to the fire alarm system.
  • Now for parts of the system in the house. The company was new, so they decided to put NOT ONE but TWO spectralert classic first gen remote horns. One for the entrance and one for the living room close to the backyard side.
  • They also installed System sensor 2100 smoke detectors in place of residential smoke alarms in every room but the kitchen. Thank god they knew what to do about the kitchen. But problems will arise and they do not know that yet. Sprinkler heads were also in the houses of the apartment.

It is late 2001 and the same fire alarm maintenance company reviews their mistakes the consequences of the mistakes after gaining experience from other places where their field was used. First of all, whenever the alarms were tested, many people had a problem, because the alarms in the house were disturbing them. Second was that there were many FALSE alarms caused by burned food in the kitchen, despite the fact that the company tried keeping smoke detectors as far as possible from the kitchens. False alarms were also caused by random people pulling the fire alarm. They didn’t even live there! False alarms were also caused because the bg-10s were easy to activate even without the pull of a human hand. Random birds who bumped into them accidentally set the system off!

In an effort to reduce the problems the company did these things.

  • The company replaced all the 2100s smoke detectors with i3’s, despite how the 2100 series were not even 10 years old.
  • They set the smoke detector zones (Zones 4 and 5) to supervisory on the ms-5024 in an effort to reduce false alarms. This leads to few other problems that happen after a LONG time. Reason being the the supervisory zone on the ms-5024 cannot trigger any other nac. All nacs were for the fire purpose only. The only catch was sprinkler heads in the houses.
  • They did not know what to do with the alarms in the houses, so they reduced the amount of fire alarm tests and all tests were announced no matter what. This also meant that the full alarm tests would be shorter.
  • All Firelite BG-10s were replaced by BG-12Ls, and they also had STI ll Series on them.

This was one of the biggest efforts the company made in order to correct their mistakes, but they did nothing about the indoor devices still being outside.

It is 2010, and there were very minimal complaints, but when the alarms were tested, not all of them would work. Mostly the ones that were in the outdoor hallways. They knew what they had to do. The classics were discontinued, and the spectralert advanced was dominant in the fire alarm market. The company also realized that the previous installers who first installed the system installed indoor devices outdoor as well as the MDL.

  • All outdoor devices were replaced by the P2RKs. (15 Candelas code 3 high volume)
  • Inside classics were left alone(low volume code 3)
  • The Panel was relocated to the inside
  • In place of the MDL, a power supply came in to accommodate for the power draw. The Fire-Lite FCPS-24FS6.

The system ran successfully until the annoying classics in people’s houses were long marked obselete and actually failed to operate because of people actually beating them up! How funny–NOT. It is 2026 and fire alarm maintenance is at it’s peak in the area. The LED L series were released, and the outdoor spectralerts are already old. 16 years since they were installed. More things had to be corrected. Their mistakes were considered code violations. The new employees are new gens and that small company in the 1990s became the most prominent of all of the other ones now. They came back to correct mistakes that were in fact beyond their control but are now under their FULLEST. The employees are trained properly.

The state’s fire alarm codes said that alarms should also be installed in the most obscure outside parts of a building, meaning the system’s nacs would have to be extended. The MS-5024 was also long considered obsolete.

  • All Spectralert Advanced P2RKs were replaced by P2GRKLED Hornstrobes All set to Code 3 High Volume and 15 candelas.
  • The MS-5020 was replaced by an MS-5.
  • The Power Supply had it’s wiring modified for NAC extentions.
  • All smoke detectors inside the houses were replaced by residential smoke alarms. First Alert 9120B’s and SC9120B’s. The houses had their own interconnections.
  • All the classic remote horns that were left in the houses were all replaced by Single HWLs set to code 3 low volume 3.3k tone(Not HWL2s since they were hard to find in the market) and ceiling mount remote strobes. They were a few PCWLEDs and one SWLED for the front door areas. White devices made the houses and buildings look like less of a mess. The company offered to add low frequency sounders for houses that had blind people. No one who lived there was vision impaired, but the offer still remains for future homeowners.
  • The brightness of indoor strobes were adjusted based on what room it was. Living rooms had 30 candela strobes. Kitchens had 15 candela strobes. Bedrooms also had 30 candela strobes to wake people up, and bathrooms had 15 candela strobes. Who would sleep in a bathroom like seriously?
  • The extra outdoor devices were also installed on every 4 sides of the apartment. They were all set to Code 3 electro-mechanical High Volume, and their strobes were set to 75 candela to catch attention on very bright days.

And the system runs like that to this day.

I used real life systems that have the MS-5024 and/or similar components mentioned as a reference for making up this system and I’ve done a lot of research. It took me a few hours to type this out, but it was worth it. This is the most logical storyline I ever made about a fire alarm system.

2 Likes

This system is for a four-building apartment complex, consisting of:

  • A 150 unit, six story 5 over 1 with 1.5 stories of structured parking inside, accessed from two different levels
  • Two three story wood frame (Type V) walkup buildings, one with 41 units and the other with 33. The larger building also has a party room and 12 private garages.
  • An outdoor swimming pool.
  • And a 9 unit townhouse building (which for the purposes of this post, is sprinklered using individual passive purge NFPA 13D systems fed off individual water service lines)

Life Safety

Fire Alarming

The fire alarm system for this complex consists of a trio of Honeywell IFP-75 panels networked together, as the walkups are large enough to need fire alarm systems of their own. This network is accomplished using SK-NIC cards, with the main building having two SK-FSL singlemode modules, and the two walkups each having a SK-FSL paired with a SK-FML. There’s also a SK-F485C converter card in the main building to provide fiber-based monitoring for the townhomes.

A HW-AV-LTE-M-2 communicator provides one of the connections from the network’s main panel to the outside world. The main panel is powered from a pair of 22Ah batteries in a SSU00505 trough, while the two auxiliary panels have SSU-00505s with 14Ah batteries in them.

Initiation

The elevator building has a Class A SLC with:

  • an IDP-MONITOR-2 on each apartment floor for the waterflow switches
  • an IDP-PHOTO-T-W in each elevator lobby for recall
  • an IDP-PULL-SA and an IDP-PHOTO-T-W in the mechanical room
  • an IDP-PHOTO-T in a B224RB and an IDP-RELAYMON-2 in the elevator machineroom for recall
  • an IDP-MONITOR-2 for monitoring the parking garage CO sensors
  • an IDP-MONITOR-2 for monitoring the Area of Refuge system
  • and IDP-RELAYMON-2s in both the NAC extenders

The walkups also have Class A SLCs but with a much simpler initiation setup, consisting of:

  • an IDP-PHOTO-T-W for self-protection
  • an IDP-MONITOR-2 for sprinkler monitoring
  • and an IDP-PULL-SA for manual initiation.

The larger of the two walkups also has an IDP-MINIMON monitoring a CO1224TR in the hall behind the private garages.

Finally, the townhouse has a setup consisting of a 5895XL intelligent power supply board powering and talking to a SK-F485C converter and a 5880 annunciator driver (used for its zone inputs in this case), all wrapped in an Altronix WP5 on the outside of the building with a pair of 7Ah batteries for power.

Notification

The notification appliances consist of MIZ-24 minihorns in the units and ELMTS hornstrobes in corridors and common areas, with the occasional ELMTSC tossed in where needed. The garages use EL4XMSTs instead, and these units, set to whoop tone, are also used for the outside fire sprinkler A/Vs.

The indoor notification the walkup buildings is powered by an AL602ULADA with 7Ah batteries in it driving a Class A loop for the apartments and two Class B circuits for the hallway hornstrobes. The main building, though, needs much more notification grunt, so it has a FL-PS10 with a ZNAC-PS card and 7Ah batteries in it to power the apartment and common area devices, while the garage devices, and the power for the garage ventilation detectors, is handled by an AL602ULADA with 31Ah batteries in a SK-RBB box beneath it. Both NAC extenders have IDP-RELAYMON-2 modules for triggering in them that also handle supervision for the garage sprinkler systems.

Emergency Lighting and Exit Signage (and Outside Egress Lighting)

The emergency lighting consists of Exitronix GCRS-U-WH combo units in the walls and stairs, supplemented by Exitronix LED90 “bugeye” emergency lights as-needed. Each apartment building also has an IOTA IIS-25-I in it powering RAB SLIMXXSYs over the exit discharge doors.

The parking lot itself is lit using LSI Lighting OPS-SA-6L-5C-UNV-30K8s

Garage Ventilation

The main garage ventilation detectors are Belimo 22G0214-5Cs, with a Belimo C-22G-50 relay module to turn the ventilation on and off. The fans themselves are Canarm AX variable speed units used in a two-speed operating mode.

Residential Life Safety

All the units have generic smoke/CO alarms in them. The townhome 13D systems are passive purge systems using inherent supervision – there’s no way to shut one of them off without shutting off the domestic water supply to that townhouse unit.

Backup Power

There’s a Cummins C40N6 running off a buried propane tank at one end of the complex to provide standby power to the elevator and all life safety and security equipment, as well as to telecommunications equipment and some lighting.

Emergency Communications

The main area of refuge system consists of a Talkaphone AOR-5-DKL with AOR-CSE-FM boxes at the elevators on all residential floors save for the main exit floor and an AOR-CSE-SM box on the ground garage floor. The elevator communicator, on the other hand, is a Commend TD5 ID CM with a Draka Cat5e traveller providing IP and PoE connectivity to it, along with a Viking LV-1K indicator on the main floor to annunciate a failure of the Commend via its builtin relay.

There is also a Viking E-1600-30A-EWP in a VE-5x5 box on a VE-GNP pedestal to serve as the swimming pool’s emergency phone. This is run from the main building with an ITW-Linx CAT6-235-RJ45 primary protector in-line to keep surges on the copper from causing damage to anything but the pool phone.

Power to all this is supplied by an AL600ULX that supplies the AOR system directly with 24VDC, and also has a VR5BT with a 14Ah battery in it to power the elevator phone via NetWay112 injector and the Vola for 4 hours, atop the Vola’s built-in 24h battery.

Telecoms

The main telecom plant consists of duplex OS2 + a coax/Cat5e Siamese to each apartment. This is terminated into the MDF for the building, where each unit can be fed from a given fiber ISP’s splitter rack or from coaxial cable.

The emergency telecoms are handled by a combination of a Vola PR12 running on battery-backed 12VDC and a pair of LVR-1s that can switch the AOR and pool phone lines between landline MFVN service and the Vola’s phone lines. The PR12 also has its LAN port connnected to the Commend and its WAN port connected directly to the cable gateway that provides Internet & phone service for the landlord and building services needs.

The rest of the building-service network, though, is run through an opnSense DEC697 appliance. One of the ports on this is the WAN link, another is a DMZ for guest wifi in assembly spaces, one port feeds the main security switch, and the final port is available for office networking needs.

The inter-building links consist of 6-fiber OSP OS2 cables between the main building and the two walkups, with three fibers for aggregated ISP service, two for fire alarm use, and one for the security system, and duplex OSP OM3 cables between the two walkups and between the main building and the townhomes. There’s also a duplex OSP OM3 cable that provides guest networking to the larger walkup building, run alongside the singlemode cable, and RG6s with TII 212 protectors on them run from the main building to both walkups so they can have the cableco as a service option.

That guest wifi is handled using HPE Aruba AP22Ds, with one in the main building’s lounge and one in the larger building’s party room. The interconnection between them is supplied using FS MMC-1F1Ts with SFP1G-SX-31 transceivers in them.

Security

Access Control

The access control system for this building is an Inner Range Inception system with ABB-Welcome IP intercoms, consisting of the following base hardware:

  • A Trove2IR2 in the main building with:
    • An AL400ULX power supply card
    • A PDS16CB power distribution card stacked on a VR6 converter
    • The 996300NA main Inception control unit
    • A 996005PCB&K LAN expander and a 996515PCB&K relay expander to serve the garage doors (via HTTP POST API requests from the LPR cameras)
    • A FS IES3220-8T4F with a SFP-GEB-T & 2 SFP-1G43-BX10 transceivers in it to serve as the main security network switch
    • The H8304 actuator and the D04012 SmartAP for the intercom system
    • and 2 14Ah batteries for 4 hours of standby power
  • A Trove2IR2 in the larger walkup building, but with:
    • An AL400ULX power supply card
    • A PDS8CB power distribution card stacked on a VR6 converter
    • A 996088 network bridge
    • A 996012PCB&K Standard LAN Access Module (SLAM)
    • A 996005PCB&K LAN expander with two 996515PCB&K relay expanders on it to serve the garages
    • A FS IES3220-4T2F with a SFP-1G34-BX10 in it to serve as the security system network switch
    • and 2 9Ah batteries for 4 hours of standby power
  • And a Trove1BL1 in the smaller walkup building with:
    • An AL300ULX power supply card
    • A VR1T regulator module paired with a PDS8CB power distribution card
    • A 996088 network bridge
    • A 996012PCB&K SLAM
    • A FS IES3220-4T2F with a SFP-1G34-BX10 in it to serve as the security system network switch
    • And 2 7Ah batteries for 4 hours of standby power

The intercoms are ABB-Welcome IP H81383K-S units in 41384F boxes with their card readers replaced with Elatec T4W2-F01C7 modules. Standalone reader locations get Elatec T4WK-F01EU7s in MECH-DFW23 front frames to match the stainless steel of the intercoms.

The main garage access control is done using Mobotix Mx-VB1A-2-IR-ALPR cameras with either a single 80VA transformer or individual 30-40VA transformers for camera power. The individual garages are handled using a single Liftmaster PPWR rolling code Wiegand receiver backed up by a Security Brands 12-000 keypad, letting the Inception simply treat them as storage units. Power to the receiver & keypad is supplied by a Traco TIW12-112 power supply.

Door Hardware

The buildings have a TownSteel mortise door hardware package:

  • Unit doors, and the office door, get MCE-13s. (These are also used on the front and back doors to the townhomes.)
  • The common area passage doors get MCE-02s.
  • The conference room door has a MCE-09 classroom intruder lock on it.
  • And the electronic access controlled doors have MCE-122-RQEs on them with Securitron CEPT transfers and Magnasphere MSS-10CT contacts.

The rollup doors use Zap 825-3 or 8825-3 operators. The main garage doors pair these with a pair of Fraba FOS-1 photoeyes (one inside, one outside) on a Fraba YC1001 merge module for safety and EMX ULTRA-DIN loops for entry and exit triggering, while the individual garage doors have a single FOS-1 for the safety photoeye. The individual garage doors also have Zap 8070 autolocks fitted for additional security.

This is for a single story high bay building that’s split into two ~18,500 ft2 bays: one half is a F-1/B woodshop use, the other is for an A-4/accessory B ice sports space.

The Woodshop

Fire Alarm & Suppression

Control Panel & Communicator

The woodshop and associated offices have a full fire sprinkler system, and a FX-5R as its fire alarm panel, with a HW-AV-LTE-M-2 communicator triggered off the FX-5R’s relays, and 9Ah batteries in the panel.

Initiation

Initiation consists of:

  • the waterflow & sprinkler supervisory switches,
  • Napco FWC-CNV-PULLK pull stations at all exits,
  • a System Sensor 4WT-B for self-protection,
  • RT-3000-P duct detectors on the office HVAC RTUs (supply and return, bussed together, with MSR-50RK remote test stations),
  • and a GRI MS-4400A on the dust collector deflagration vent door to trigger a supervisory event should the dust collector go kaboom.

Notification

Notification consists of:

  • a set of EL4XST-FRs set for 75cd in the main shop floor area for V/O notification due to the high sound levels from the woodworking tools
  • ELHSWs in offices and corridors
  • ELSTW remote strobes in the restrooms
  • and an EL4XHS-FR set to continuous tone for the waterflow alarm

A Wheelock DSM is present at the panel to provide sync pulses for the Eluxas.

Emergency Lighting & Life Safety

The emergency/exit lights & signs consist of:

  • Big Beam ELS24XL1RW signs in the shop space (NEMA 4X/dusttight)
  • Lithonia FEM L48 12000LM IMAFL MD MVOLT GZ10 40K 90CRI E7W2H for the shop space normal/emergency fixtures (again NEMA 4X, with integral batteries)
  • Atlas EECPRWGs for the office spaces to supply both emergency lighting & exit signage
  • and a set of Atlas WPS27LED3K wallpacks on an Iota IIS 125 SM DR remote inverter with a dimming control resistor in it to reduce fixture output when on emergency power to serve as the exit discharge emergency lights

The Ice Rinks

The ice rink space, as an A-4 use (albeit with only a small number of spectators) conducted in an unlimited area building with exit doors from the main space directly to the outside, is eligible for the 507.4 exception 2 sprinkler exception; which is good because we’d otherwise have to go to a dry or even a vacuum system for the bulk of the space to prevent freezeups. There is also a full refrigeration machinery room to protect the indirect chillers that both chill the air in the ice hall and provide chilled water for subslab cooling under the ice rinks. (It can also provide heat recovery to provide warm room heating and domestic hot water, saving the need for gas service to the building.)

Fire Alarm

Control & Communications

The FACP is a Potter PFC-4064 with a UD-2000 DACT card, 33Ah batteries in a SSU00500 trough, and a HW-AV-LTE-M-2 communicator wired to a DACT phone line with supervision by the communicator. (The other DACT phone line and the panel’s IP communicator can be connected to other communication paths, if so desired.)

Fire Initiation

Fire alarm signals can be initiated by the following:

  • Waterflow & supervisory switches, covering both the main warm space & the machinery room
  • A 4WT-B on an appropriate pull zone for self-protection
  • A manual pull zone with a single SigCom SG-42SK1-SC pull on it for the machinery room
  • A manual pull zone for the cold spaces, using SG-42SK1-SCs on SG-WP boxes
  • And a manual pull zone for the warm spaces, with a SigCom SG-42SK1-SC pull on it at the main entrance.

The panel is also connected to an auxiliary alarm/trouble zone from the gas alarm system described below.

Fire Notification

Voice evacuation here is handled using a SigCom VECP-25 with a DAPB-100 booster panel. The actual notification appliances, though, consist of the following:

  • A single line of AtlasIED VT-157UCN speakers mounted along the centerline of the ceiling and set for 15W apiece, running off the booster, to give us 86dBA in the far corners of the ice hall
  • Eluxa EL4XST-NW strobes set to 75cd along each wall of the ice hall
  • ELSTW-N remote strobes set to 15cd in the restrooms
  • ELSPSTW-N speaker strobes set to 15 cd and an appropriately low power setting in the warm spaces
  • An ELAMTSTR on a RSSP-24MCW-FR in the refrigeration machinery room, set for High volume, T3Horn/Siren/Chime tones, and 15 cd on both strobes – the expansion strobe serves as the fire alarm strobe in this case.
  • And an EL4XMTST-FR set for slow whoop to serve as the waterflow alarm

Gas Alarming

The gas alarm system is one of two flavors:

  • For natural refrigerants, the system consists of either a Belimo 22G04-5B ammonia monitor or a 22G15-5B6 CO2 monitor paired with a C-22G-50 relay module.
  • Or, for HFC/HFO refrigerants, the system instead consists of a Bacharach MGS-250 NDIR refrigerant monitor paired with a RKI Beacon 110 controller via 4-20mA. (The internal strobe and battery charger options on the Beacon are not needed in this system.)

Either way, there is an alarm initiation relay supplied by the monitor itself, along with trouble, failsafe fan, failsafe shutdown, and local alarm outputs from the controller/relay module. One of the PFC-4064’s NACs is used to supply 24VDC power for all of the gas detection hardware, hitting the monitor first, then the controller or relay module.

The manual ventilation and shutdown controls are KAC W3A-Y000SG-K013-65 callpoints with PS210 “flexi” elements fitted; as much as I’d like to use the STI ReSets instead, none of them are rated for operation below -10°F or so, and the refrigeration room is entered directly from the outside.

Gas Notification

The gas notification system is simple, with the siren tone and strobe on the ELAMTST being used for gas notification in the refrigerant machinery room, and a pair of Federal Signal LP1-024R mini-strobes, one at the entrance to the machinery room and one just below the waterflow alarm, used to provide exterior notification of the hazardous condition inside. All of these appliances share a NAC supplied using a DMP 866 card and a Functional Devices PSMN24DA regulator (to step down 24V power to 12V aux power for the 866).

Emergency & Exit Lighting

The emergency lighting package is a bit different this time, using:

  • Isolite DTH2-1-BK-MB or LPDC2-HY-G-1-BK-BK-MB hybrid photoluminescent exit signs in the ice hall
  • An Exitronix RS2-6-27-WH emergency light in the main foyer space with MLED-GY-2-WP heads in the ice hall (up to 8 of them)
  • An Exitronix RSL-6-60-0-W emergency light to provide power to more MLED-GY-2-WP heads in the ice hall, if necessary
  • and Atlas WPS27LED3K wallpacks on a regular IOTA IIS 125 SM inverter for the discharge light

The main lights in the ice hall are Lithonia CPHB ALO34 UVOLT SWW9 80CRI DWHs.

1 Like

This system is for a fully sprinklered six-building complex that consists of a large collection (158) of self-storage bays, of which some are elaborate enough to have HVAC and pedestrian doors, a roughly 1250sf assembly space that includes a mezzanine, and a manual car wash bay, along with miscellaneous restrooms and support spaces. All six buildings share a single FDC at the front of the complex, and all of the storage entrances are within a perimeter fence accessed via a single vehicle/pedestrian gate pair.

Fire Alarm

Control

The FACP for the complex is a Fire-Lite MS-10UD, located in the clubhouse, with a DMP DualComNF-2 powered from the panel as the communicator. The panel has a bank of 5 Space Age T32-DGs at it to provide lightning protection for IDCs, NACs, and ANN-BUS lines that leave the building. That exterior ANN-BUS feeds an ANN-I/O card in a Space Age SSU02052 annunciator at the complex’s FDC. A pair of 22Ah batteries gives the panel a 72h runtime, which is important since this is a place that may have to go the weekend or more unattended.

Initiation

The clubhouse has a pair of Napco FWC-CNV-PULLK pull stations and a System Sensor 2WT-B self-protection smoke detector in it. All other FA initiation is done through the sprinkler monitoring zones (combo waterflow/supervisory) in the storage buildings.

Notification

The clubhouse has 3 P2RLEDs set to 30cd + 2 SRLEDs set to 15cd in it to provide local notification of a fire (manual or self-protection) or a waterflow condition in its containing building.

The waterflow alarms, though, consist of two Patlite EHS-M1TE horns and a Federal Signal 121ALED-024R rotating beacon mounted on a pole above the FDC, to provide ample notification to passers-by of a waterflow condition within the property.

Other Life Safety

The emergency lighting consists of Sure-Lites APC7RG combination fixtures at the exits from the clubhouse, Sure-Lites APELMINI-R emergency lights covering the stairs down from the mezzanine, and a Best Lighting LEDR-1 at the back of the mezzanine deck. Both exits from the clubhouse have their discharges covered by RAB SLIMXXSY units on an Iota IIS-25 inverter; this inverter also powers a third SLIMXXSY that covers the pedestrian gate out of the fenced area.

General Telecoms

A Sophos XGS88W provides WLAN within the clubhouse and also supplies network connectivity to the security system, with the ISP supplied modem for a WAN. (The DualCom can also connect to this as a supplemental link to the cellular connections, if so desired.)

The various fiber links within the premises LAN use ROBOfiber SFP-7000-85 multimode 1GBase-SX modules. ISP connectivity to individual storage units is beyond the scope of this post.

Security

It is presumed that there will be a video security system on the premises; its design is outside of the scope of this post, though, so it will not be discussed further beyond mentioning that it uses the spare ports allocated for it on the fiber optic media converters and main switch.

Roll-up Doors

The rollup doors to the storage units use Liftmaster DDO8900W jackshaft operators with the supplied Liftmaster photocells for entrapment prevention. The Inception system uses relays to control the interlock inputs on the Liftmasters, thus allowing it to prevent someone from accessing a storage unit unless they are carded into the site.

Pedestrian Door Hardware

The pedestrian doors to the large storage units use Cal-Royal SC8080 SS EU electrified mortise locks, while the clubhouse doors (both front doors and the presumed back door as well) use Detex V40xNS ER EX narrow stile ELR rim panic devices with 03AN storeroom trims. All wiring on doors is brought there using Command Access CDL concealed door loops.

Access Control Backend & Power

The PACS itself is an Inner Range Inception system that shares a fiber optic network backbone with the CCTV system, consisting of the following components and cabinets, along with XPR XP-K-QR-MFBT QR-code/DESFire readers at the gates and all pedestrian doors:

  • The main building has a Trove2IR2 containing the 996300NA Inception controller along with the following modules:
    • A 996005PCB&K LAN zone expander, supporting
      • A 996500PCB&K input expander,
      • and 2 996515PCB&K relay cards
    • A ROBOfiber HGW808S switch to provide network connectivity to the system
    • An ICT IntelliCharge ICT24024-15BC2 on an ICT-DIN clip and some DIN rail to tend the battery bank and power the system
    • An Altronix PDS16CB stacked atop a VR6 for power distribution
    • An Uplink 5530M communicator powered from the panel and connected to an IR 996798 serial cable, with its dialer capture terminals available for other reporting (unfortunately, the Uplink isn’t listed for fire service, and Inception firmware doesn’t have serial support for other NA market communicators)
    • And 4 55Ah batteries in a Trove3SWC for 72.25h of backup power
    • There is also a Space Age T32-DG at this cabinet to protect the intrusion siren output from lightning and surges.
  • The two main large-bay buildings each have a Trove3IR3 containing the following modules:
    • A 996088 Ethernet to Inception-LAN bridge
    • A ROBOfiber LFC-1002-SFP media converter
    • A 996005PCB&K LAN zone expander, supporting
      • 3 996500PCB&K input modules,
      • and 3 996515PCB&K relay modules
    • 3 996018PCB&K Intelligent LAN Access Modules (ILAMs), each hosting 3 996535PCB&K 2 door expander cards
    • A 996012PCB&K Standard LAN Access Module (SLAM)
    • An ICT IntelliCharge ICT24024-BC2 for battery charging and power
    • A Traco TEQ200-4812WIR for 24V to 12V step-down (as these cabinets pull just a hair too much 12V power for a VR10 card to handle)
    • 3 PDS16CBs in each cabinet for power distribution
    • And 4 33Ah batteries in a Trove3BWC for 24h of standby power
  • The rearmost large-bay building has a smaller system, consisting of the following parts contained in a Trove2IR2:
    • A 996088 Inception LAN bridge
    • A ROBOfiber LFC-1002-SFP media converter
    • A 996005PCB&K LAN zone expander supporting
      • 2 996500PCB&K input modules
      • and 2 996515PCB&K relay modules
    • 2 996018PCB&K ILAMs with 3 996535PCB&K door expanders on each one
    • An Altronix AL1024ULXB2 for the main power supply
    • A VR10, along with a PDS8CB and a PDS16CB, for power distribution
    • And 2 22Ah batteries for backup power
  • The rear of the two small-bay buildings contains a couple of large bays as well, so it requires a slightly more extensive system that consists of the following parts, also wrapped in a Trove2IR2:
    • A 996088 Inception LAN bridge
    • A ROBOfiber LFC-1002-SFP media converter
    • A 996005PCB&K LAN zone expander supporting
      • 3 996500PCB&K input expanders
      • and 3 996515PCB&K relay expanders
    • Another 996005PCB&K LAN zone expander, with this one supporting
      • A single 996500PCB&K input expander
      • and 2 996515PCB&K relay expanders
    • A 996012PCB&K SLAM
    • An Altronix AL400ULXB for power
    • A VR6 with a PDS16CB atop it for power distribution
    • And 2 22Ah batteries for backup power
  • And the final building consists entirely of small bays, so it has a simpler system consisting of the following modules, also wrapped in a Trove2IR2:
    • A 996088 Inception LAN bridge
    • A ROBOfiber LFC-1002-SFP media converter
    • A 996005PCB&K LAN zone expander, supporting
      • 2 996500PCB&K input expanders
      • and 3 996515PCB&K relay expanders
    • Another 996005PCB&K LAN zone expander, with this one supporting
      • A 996500PCB&K input expander
      • and 2 996515PCB&K relay expanders
    • An AL300ULXB (set for 12V this time, unlike the other cabinets which all use a 24V main supply) for the main power card
    • And a single 33Ah battery for backup power in the cabinet

Intrusion Detection

Physical intrusions are detected using a RBtec IronClad processor and its associated sensing cables to monitor the fenceline, along with Honeywell FG1025Z glassbreaks in the clubhouse to monitor the glazing there, and GRI Magnasphere door contacts, with MS20RS-Ts covering pedestrian doors and MS4400As protecting the rollup doors.

Fenceline Access Control

The fenceline has a vehicle and an adjacent, associated pedestrian gate in it, with both gates set up for read-in/read-out operation. The Inception LAN is extended out to cover both gates using a LFC-1001-SFP media converter, another 996088 LAN bridge and 996012PCB&K SLAM, all powered from the vehicle gate operator’s 12V auxiliary output.

The pedestrian gate hardware (the pedestrian gate is presumed to be between the vehcile gate and the frontmost building) consists of a Detex WDExV40EEX weatherized delayed egress panic device with 03A storeroom trim on it controlled by a DynaLock 3101B delayed egress controller board. The controller is fitted with a Camden CM1000 for the reset keyswitch along with an IDEC HW1Z-P1F2PQ4R illuminated 22mm 12V buzzer fitted to the bottom of the keyswitch box to serve as the required audible alarm device.

All of this gate hardware is powered from the 24V auxiliary supply in the vehicle gate operator. There is also a PAM-SD on a surge protected NAC from the FACP to trip the fire input on the DynaSwitch controller. The pedestrian gate has a Securitron CEPT power transfer on it, and a Magnasphere HS-L1.5-111 door contact is used to monitor the gate position.

Vehicular gate duty is handled by a 26’ AutoGate/Taimco vertical pivot gate (to reduce entrapment hazards compared to a slide gate) with the supplied VPG-2490 operator, accessorized with an EMX ULT-PLG loop detector for the gate reversing loop, a set of 3 EMX IRB-MON2 photoeyes for entrapment detection, a SDC GL260MRAHDB run from 24V gate operator auxiliary power to provide auxiliary locking for the gate, and a Magnasphere HS-101-WG wide-gap contact to monitor gate closure. Backup power for the gate operator is supplied by a pair of 80Ah Group 24 marine AGM deep cycle batteries.

Security Notification

Security notification is handled by another Patlite EHS-M1TE horn, fed from the surge protected DC siren output controlled by the Inception and mounted to the same pole as the waterflow alarms, albeit facing into the premises instead of along the street.

1 Like

1 Example Of Classic Edwards Being Fully Replaced By A Modern Notifier Solution:
Original Panel: Edwards 6500
New Panel: Notifier NFS2-3030C (With NCA-2 Display)
Original Pulls: Edwards 270-SPO, Mirtone 73303U
New Pulls: All Notifier NBG-12LX
Original Smokes: Edwards 6250 Series
New Smokes: Notifier FSP-951
Old NAs: All Edwards MB-10-24
New NAs: All System Sensor Xenon L-Series
Old Heats: Edwards 280 Series
New Heats: None (Old Heats Removed)
Monitor Modules: Notifier Dual Monitor Module For Sprinkler System