Hello, I’ve adopted this MS-4 fire lite alarm when I purchased my 4-plex. The unit is alarming with “system trouble” “power trouble” and BATT LED.
Both batteries are definitely in need of replacing and I’ve ordered them, the line connecting them was also corroded so I pulled it and scraped it clean. The AC power is GREEN, and the batteries won’t be in for about a week. Will it keep alarming or will it stop now that I’ve pulled the batteries? All error lights are still on… thanks
The trouble will stay on until you get the new batteries. Unless your panel has a reminder enabled, it shouldn’t beep. Your system should be ok until you get the batteries (as long as the power doesn’t go out).
There’s some dip switches located behind the plastic cover.
Locate SW1, switch 5. If it’s ON, then trouble reminder is enabled. It’s not enabled by default, you’d hear the buzzer sound every 2 minutes if it was on.
Yes, with trouble reminder, the buzzer will sound every 2 minutes for troubles and will need to be silenced again every 24 hours the trouble remains. If this is off, there should be no beeping.
Also, if you are replacing the batteries, I would be very careful. If you hook up the batteries the wrong way, you will blow up your panel. I did it once when I was a younger and newer technician, wasn’t paying full attention to my connections and blew a booster panel.
As well, many areas have codes regarding batteries. For my area, they need to be a certain type, have a visible date code and be less than 5 years old. Anything more than 5 years and the battery needs to be replaced. Our code is changing it to 4 years very shortly too. So make sure they fall into the right category and work as intended.
I have seen building managers fined and put in jail because they decided to change the batteries, didn’t test them or got outdated ones, fire happened, fire alarm didn’t work because batteries were dead, and someone died.
I’m currently in a place where this panel keeps on buzzing and it’s extremely annoying, I know it’s probably the batteries (no batteries currently), and my manager told me it’s gonna be done next “few weeks”.
Is there any way to silence the beepy sound?
[I thought it’s Sw1 #5 but that is off already]
You need to press the “ACK” button. That should solve your problem. The panel may be programmed to start beeping again after a period of time so you may need to press it again. Don’t mess with the dip switches. Put the black cover back on. Make sure that is does get batteries soon though because, as of right now, the fire alarm system will not function during a power outage.