Whenever I tested the drill function on my MS-9050UD, only NAC 1 sounded. I knew NAC 2 worked, because I had just had the system in alarm. So, I looked at the control panel manual, and noticed that any NAC’s set to non-silencable will not activate during a manual evacuation.
Does the panel have a selective silence feature? I was thinking if it does and you could wire it up, the drill function may sound both your audibles and strobes.
NAC 1 is audibles
NAC 2 is strobes
Since I have separate strobes and audibles, I do not have selective silence enabled.
Yes, it has selective silence, but I am not going to wire it up right now.
If anyone thinks they might know why Fire-Lite had this programmed that way, please post it.