Notifier AFP 100 Zone Programing Set UP Q's

First off thanks for your Post, Yes as to the area having both sets of H/S’s going off but someone talked with the Fire Marshal and said it is possible to have only one set going off which this is a first for me having to not have ours activate. And Yes you are close to what I am talking about but there is no FM200 H/S outside the room? Again not my issue as well as did not see any label as to their H/S off the FM200 System.

My main Q’ is can you have More than One Zone Associated with the Monitor Module On this Panel? On the newer Panels like Firelite which I am more Familiar with, they have the option to have more than 1 Zone but when I added the 3 Monitor Modules Alarm, Supv & Trbl, in the Programming of Each it did not offer more than 1 ZONE! At the end of each Device the Alarm being General Z00 for the entire buildingor another single Zone but not Multiple Zones and the other 2 another Zone 05 which won’t activate the H/S’s. What our Designer was hoping for was to use a Control Relay Module to link it to anything other than the FM-200 System for the 3 or our H/S in the Room but I did not see how there can be more than 1 Zone associated with this Monitor Module but Z 00?

Does the Notifier Panel have the ability to associate more than 1 Zone to a Device like a Monitor Module?

Newaygo1