Hi All,
We have a alarm “TROUBLE IN SYSTEM NO DEVICES INSTALLED” in our Notifier AFP 200 panel. Kindly assist to solve this.
Thanks in advance.

Your AFP-200 has no devices installed, run autoprogram after installing devices to the SLC loop.

Thank you very much. I have done this and the controller started reading all installed devices. But we got a new problem.

We have 2 different places where the heat detectors and FM 200 cylinders are installed. If I operate MCP at place 1, fire panel activates both of the FM 200 cylinders SOV at place 1 & place 2. It should not be. If I operate MCP at place 1 then it should activate the Place 1 cylinder SOV. Respectively for place 2. Hope you understand.

I have just ran the auto program and give enter, that’s it. I don’t think the auto pogrom changes something.

The AFP-200 has releasing zones. For each place, set the initiating and notification devices in its own releasing zone.

Thank you very much. I should use Notifier programming software to do Creating/splitting zones, mapping and linking of monitor module and control module, linking releasing circuits with zones (control modules)

Or

Can I do manually?

Please assist. Thanks in advance.

You can use the software, although it’s quite old and probably only works on older PCs. It may be easier just to just do it from the front keypad. Refer to the user manual on how to program using the panel keypad.

Well noted sir. Thank you very much for your kind advice. It was really helpful. I appreciated. Have a good day.