Hey all, it’s certainly been a while, doing well, I’ve just had a lot going on where making new videos has taken a back seat.
I recently rescued a Notifier System 5000 from scrap. The panel has the original version of the MPS-24 power supply (not the MPS-24A like most documentation I’ve found shows). I am having some trouble figuring out which terminal to wire to. I’ve been doing my research - almost no documentation exists for the original MPS-24 power supply, I am only finding documentation for the System 5000 and Sensiscan 2000 that features the MPS-24A.
Here’s what I have been able to figure out so far based on continuity testing I’ve been doing.
- Terminals 2 and 3 seem to be ground/earth, continuity testing reveals that these are tied together
- Terminals 4 and 6 appear to be Neutral (-) In/Out, continuity testing reveals these are tied together. The MPS-24A has the Neutral terminals to the right of the Ground.
- Terminals 5 and 7 appear to be the Hot (+) in/out, continuity testing reveals these are tied together.
- Terminals 8 and 9 to the far right appear to be wired to something else on the panel, I did not remove as of yet)
Below is a photo I took, the ground is marked with green arrows, neutral marked with white arrows, and hot marked with black arrows.
This seems to contradict what the MPS-24A wiring manual suggests. While terminals 2+3 are still the same (Ground). On the MPS 24A, terminals 4+5 are Neutral In/Out and 6+7 are Hot In/Out. (see page 2 of this data sheet: MPS-24A Main Power Supply Data Sheet)
Has anyone worked on these panels with this power supply prior? I wanted to double check prior to wiring anything high voltage up. Everything else seems to be good shape.