So here’s what’s going on. There’s a local demolition sale I found that will be taking place in an old Chase bank building. I emailed the building owner asking for pics of the fire alarm system, since I might be interested. He sent me a link to pics of everything for sale, and the pic below is what I found.
Looks to be one of those old 4208 systems, I think. Although I didn’t see pics of the alarms and pull stations, I’ll bet we’ve got a system of 4050-80/4051s and 4251-20s. Could someone verify this as likely to be true?
Also, can someone provide me some more info about this system? Is this something I should go for if I can get it for the right price? Thanks in advance!
That is a 4208. According to the control module it is a 4208AX, which is the AC panel. It probably has series AC horn circuits. I can’t be sure without seeing a picture of the inside. If the price is right and you like historic old panels it looks clean. How much you want it is up to you. I have a little information, but I will have to dig around to find it.
Obviously I can’t be 100% sure without seeing the inside of the panel. However, I never saw a panel with the “AX” control module (Operating Power Trouble and Supervisory Power Trouble circuits) that did not use AC horns. The panel in the picture has the “AX” control module. Those panels used an “H” signal module (page 25 in the service instructions) which use low voltage AC horns wired in series.
The 4208 DC panel used the “A” control module with one trouble circuit. Those typically used the “N” signal module (page 16 in the service instructions) to operate parallel 24 volt DC horns. The 4208A also had battery backup. Typically there was a set of wet cell NiCad batteries in a separate battery box.