Pull stations on Vista 15p

Hey folks, I got a vista 15p panel and was wondering if it’s possible so use fire pull stations to activate a fire alarm condition? For both fire zone types it said it would send a trouble for an open condition. Most pull stations are open upon normal condition. Is there any other way to do it? Any help is appreciated! Thanks in advance.

You should wire it as if it were a heat detector, with the EOLR after the last pull station you are going to use

What zone type would I program it as?

Fire With Verification is type 16 while Fire without verification is type 09.