Does anyone know which heat detectors to use with an older Simplex 4004-9101 conventional zone FACP?
Probably a 135 fixed temp would work.
I’m thinking the 4098-9733 heat detector will work but not sure.
Any ideas?
Thank you, everyone!
The model you listed is addressable and won’t work.
What you’ll want to use is a 4098-9401.
https://www.tycosimplexgrinnell.com/wps/wcm/connect/f7a78eb1-c475-42ed-9b02-503b6a1fe708/4098-9401%2C+4098-9402%2C+4098-9403%2C+%26+4098-9404.PDF?MOD=AJPERES&CACHEID=ROOTWORKSPACE-f7a78eb1-c475-42ed-9b02-503b6a1fe708-kX1P2QX Datasheet
Not the 4098-9733. That is the electronic heat sensor for use on addressable MAPNet or IDNet circuits.
Use one of these on a 4004 hardwired panel.
4098-9401, 4098-9402, 4098-9403, & 4098-9404
Electronic Heat Detectors, direct connect models
4098-9612, 4098-9613, 4098-9614, & 4098-9615
Electronic Heat Detectors for two-wire and four-wire bases
Thank you, everyone.
That was pretty cool… I joined up yesterday afternoon, needed some info with not much time for a lot of research or time wasted, the next morning is an answer.
Thanks again and hope I can also provide some answers from time to time too.
additional response…
Couldn’t I use a 4098-9612 135 f.t. HD, if I don’t have the others you guys mentioned? Looks like that is compatible with the 4004 series FACP.
Thoughts?
Not the 4098-9733. That is the electronic heat sensor for use on addressable MAPNet or IDNet circuits.
Use one of these on a 4004 hardwired panel.
4098-9401, 4098-9402, 4098-9403, & 4098-9404
Electronic Heat Detectors, direct connect models
4098-9612, 4098-9613, 4098-9614, & 4098-9615
Electronic Heat Detectors for two-wire and four-wire bases
[/quote]
My bad…it looks like you said the 4098-9612 will work.
They both work, they are just wired differently.
With the 4098-940X series, the wiring goes into the detector head.
With the 4098-961X series, the wiring goes into the base.
Awesome. Thank you everyone for your timely and knowledgeable responses. It’s greatly appreciated!