Simplex 4005 with 4602-9102 Annunciator

Hello,

I recently got a 4602-9102 annunciator for my 4005. So far, it appears the annunciator communicates properly with the main panel. I’m not sure how to get the alarm LEDs to light up though.

I can’t find manuals that specifically mention how to wire this up to a 4005, below are my dip switch settings:

SW1: ON ON ON OFF ON ON ON OFF (this is the only configuration that seems to work for me)
SW3: OFF ON OFF ON OFF ON ON ON (this differs from a suggestion I’ve seen on YT, this is the only one that seems to work for me)

My 4005 seems to communicate with the annunciator automatically, I didn’t have to add an RUI card to the panel (it doesn’t detect the annunciator as an RUI card either). I’m guessing I have the wrong dip switch settings?

Specs for reference: 4005 was manufactured in Jul. 2005 and works without any permanent troubles. The 4602-9102 I got should be a newer model (chip number starts with 740-) and I know it works with the 4005 (troubles and buttons all work). Connection is made with 24V and the external RUI terminal from 4005.

Any suggestions are appreciated, thank you.

Random Side Question: Does the 4606-9101 annunciator work with the 4005? I know it works with the 4006, 4008, and 4010; curious since my 4005 is a newer one.

574-015.pdf (398.8 KB)

Thank you for the help!

Looks like my SW3 switch settings were correct, it was SW1 that was wrong. Unless I’m bad at binary math, I fiddled with SW1 until my 4005 picked up the annunciator. All is good now!