Simplex 4010 to Simplex 4003 Wiring Help

IDNet Channel Failure appears when the SLC does not sense any devices. It is normal for it to appear with nothing wired to the SLC, or after recently disconnecting/reconnecting a device (especially if that device was the first/only device on the SLC).

As for your other questions: Fire Monitor is fine for the point type.

SW3 and SW6 should be all off, so that is correct.