What you’ve bought here is a fire suppression/releasing control panel. This acts very differently to a fire alarm panel.
First the zones…
Zone 1 is a Manual Release zone. When this goes, it overrides the delay timer, unless the output circuits are in Mode 4 (See Below).
Zone 2 is a Fire Detection zone. When this goes, a timer starts counting down. After the time expires, the system releases.
Zone 3 is a Waterflow zone. When this goes, it means that somewhere a suppression agent is being released, whether it is water from sprinklers or a manual system dump triggered by a valve.
Zone 4 is a supervisory zone. Depending on how it is set up it could activate the releasing relays.
Next the output circuits…
These will behave depending on how you set your DIP Switches, but here’s four possibilities:
-
NAC1 and Releasing Circuit 1 activates if Zone 1 OR Zone 2 is activated. NAC2 activates when Zone 3 goes into alarm. Releasing Circuit 2 activates if Zone 4 gets a supervisory condition.
-
NAC1 activates if Zone 1 OR Zone 2 is activated. NAC2 activates if Zone 3 goes into alarm. Releasing Circuit #1 activates if Zone 1 AND Zone 2 go into alarm. Releasing Circuit #2 activates if Zone 4 gets a supervisory condition.
-
NAC1 activates if Zone 1, Zone 2 OR Zone 3 is activated. NAC2 activates if Zone 4 gets a supervisory condition. Both releasing circuits activate if Zone 1 OR Zone 2 go into alarm.
-
NAC1 activates of Zone 1, Zone 2, OR Zone 3 is activated. NAC2 activates if Zone 4 gets a supervisory condition. Releasing Circuit 1 activates if Zone 1 goes into alarm, Releasing Circuit 2 activates if Zone 2 goes into alarm.
Lastly, there is a delay timer that can be set between instant, 10 minutes, and 15 minutes.
If you set it up correctly you can use it as a fire alarm panel, just note that you are limited to two zones and one NAC, depending on how you plan to use it. These things aren’t actually meant to be used as fire alarms due to the fact that they are agent release panels.
If it weren’t so late at night I’d give you details of how to set one of these up to work like a fire alarm, but my tired brain can’t remember how I did it a few years ago for a demonstration “fire alarm” setup.
BTW, here is the manual.
Sources: Manual, and used them before.