Make up a system
Another college built in 2002
Panel
Simplex 4100
Panel Components
  1. Simplex 4100 Remote Command Center
  2. Simplex 4603-9101 Annunciator
Main Components
  1. System Sensor Classic SpectrAlert Horn/Stobes (mech. code 3)
  2. Simplex 4099-9003 pulls mounted on trim plates.
Remote Strobes
Red wall mount SpectrAlert strobes in the bathrooms, stairwells, and all mobile areas.
An elementary school from 1974 had a Simplex 4208 panel, and the signals were rust-colored Simplex 4051 horns on 4050-80 light plates with “FIRE” on the lens, and there were a few 4051 horn-only units as well. Pull stations were Simplex 4251-11 Chevrons, and a few of them were mounted high up (others were at ADA-compliant levels). The smoke detectors were Edwards heat detectors. Over time, a few of the Chevrons were replaced with 4251-20 T-bar pulls.
In 2004, the system got a total replacement, with a Simplex 4005 panel, a 4603-9101 LCD annunciator installed over the old Simplex annunciator, Wheelock AS horn/strobes replacing the 4051s/4050-80s, and most of the pull stations were replaced with Simplex 2099-9754 T-bars. The Chevrons mounted high-up were replaced with -9754s mounted on Faraday ADA adapters (since Simplex doesn’t make them). The Edwards heat detectors were replaced with Simplex TrueAlarm smokes, model number 4098-9601. Wheelock RSS strobes were installed in the bathrooms.
The William T. Minor High School in Connecticut:
  1. The hallways in the older wing and rooms not listed that have alarms have Simplex 4050-85+4030-1 horns or Wheelock 7002T-24 horns depending on the wing
  2. The new wing (not really new, added in 1985) has Wheelock 7002T-24 horns
  3. The bathrooms in the old wings have Simplex 2903+2901-9838 horns
  4. The bathrooms in the new wings have Edwards 892-2B horns in them
  5. In BOTH the wings, the bigger rooms have Edwards Integrities
  6. The coaches room down in the gym has a Edwards 792-5A-006
  7. The gym has Wheelock WM3T-24s
  8. The pool room has a Wheelock AS horn
  9. The locker rooms has a Wheelock AES horn
  10. The Auditorium have classic SpectrAlerts
  11. The Cafeteria have MASS horns
  12. The Library has a Cerberus U-HNH horn
Hansford University is set up like this.
Original System
Panel
Simplex 4002 (Continuous)
Main Components
  1. Simplex 2901-9806’s on 2903 Strobe Plates.
  2. Some of the -9806’s are mounted on 4903-9101 strobe plates w/ the strobe on the top.
  3. A mixture of 4251-20’s and 2099-9756’s.
Remote Strobes
4904-9101’s (vertical)
Building Extension
Panel
Notifier Addressable System
Main Components
  1. SpectrAlert Advance Horn/Strobes (P2R’s) set to Medium Volume Code-3 and set to 15/75cd.
  2. Notifier NBG-12LX’s
Remote Strobes
SpectrAlert Advance SR’s in bathrooms set to 15cd.
An antiquated school. Outdoor hallways with overhangs.
The main quad area in front of the school has dual Simplex 2901-9806 horns on weatherproof boxes. The office is right beside that, and it has a Simplex 2001 panel circa 1984. Signal coding is continuous. Right next to it is an older Radionics control panel from 1981. Signal coding is also continuous.
Behind that, wings of older classrooms can be found. Each hallway has a mix of MA sounders set to 800 continuous and 9806s. Both have red projectors over them. In each classroom, there are ESL 445CT smokes on the ceiling. The pulls are Fire-Lite BG-8s.
In the newer wings, Simplex 2098-9201 smokes can be found. There are also 2901-9806s in the classrooms. Pulls are 4251-30s (break glass with hammer type).
The gym has four ESL 1025C smokes, two BG-8 pull stations, and two MA sounders set to 800Hz.
The cafeteria is expanded from the old one. The old one has ESL 445CT smokes every 30 feet along the ceiling, and the new one has those 2098 smokes. Both of which have a Simplex 4051 behind a red flush grille.
In 2001, the system went through a re-do, and the smokes were all torn out. Replacing them are 449CTs, and ESL T-bars. The NAs are Wheelock AS’s set to unsynced code 3. The two 9806s at the front of the school were kept. AHWPs are now in the hallways.
The William E. Russell Elementary School in Massachusetts is set up like this:
  1. Wheelock MT horns in the hallway and areas not noted, set to continuous
  2. There is a TrueAlert in both of the kindergarten areas, set to continuous
  3. One Simplex 9838 are in the library, set to continuous
  4. There are also MASS horns, in the main office areas, somewhere around those rooms, set to continuous
  5. The special services rooms (i.e. Speech, Counseling, Psychologist, APE and Resource) have Simplex 2903-9215 horns, set to continuous
  6. ESL & RSP rooms have SpectrAlerts in Code-3
  7. The bathrooms have Wheelock AS horns, set to Code-3
  8. Mircom Select-a-Horn Strobe alarm in the Reading/Literacy room, set to Code-3.
  9. EST Genesis horn in the Nurses Station
  10. Custodial Storage has a Wheelock NS set to Code-3
  11. The Auditorium has Cerberus U-MMT horns on continuous with the “FIRE” lettering underneath them
  12. The gym has Edwards 6536-g5 set to continuous
  13. The Faculty Lunchroom has a Gentex GX90 mini-horn set to continuous
  14. The Computer Lab has Gentext GMS horns set to continuous
  15. The Technology Center has a System Sensor PA400R, set to Code-3
TODAY IS THE OFFICIAL OPENING OF A NEW CROWNE PLAZA!
I had this building system stuck in my head for a long time, so here it is.
Panel and panel components
  1. Simplex 4100U
  2. Remote Command Center
  3. A 4603-9101 was added near the elevators.
Main Components
Majority
  1. Simplex 4099-9001 pulls (some of them have Stopper IIs over them)
  2. System Sensor Spectralert Advance SPSR Speaker/Strobes (15/75cd)
Stairwells (majority)
Simplex Non-Addressable White TrueAlert Speaker/Strobes (4903-9359)
Stairwell E only
Simplex Non-Addressable Red TrueAlert Speaker/Strobes (4903-9356)
Hotel Rooms
  1. SpectrAlert Advance SPRV Speakers
  2. SpectrAlert Advance MHW’s in the bathrooms set to continuous
Suites
  1. Simplex Non-Addressable TrueAlert Remote Speakers (4902-9716)
  2. Same as #2 in “Hotel Rooms”.
7th Floor (Penthouse)
  1. SpectrAlert Advance ceiling mount System Sensor | Honeywell Building Technologies SPCW speakers
  2. SpectrAlert Advance SR strobes set to 15/75cd.
Entranceway, Pool, Front Desk, and Meeting Rooms
4099-9003’s
Lavatories in the Entranceway
SpectrAlert Advance SR strobes set to 15cd
Entranceway and Breakfast/Lunch/Dinner area
SpectrAlert Advance P4R’s set to low volume code 3 and strobe is 15/75cd.
Outdoor Signals
SRHK strobes set to 185cd (cd rating drops with temp. decrease)
Here’s the message:
Note: all strobes are synchronized
The William D. Schaefer Middle School in Maryland. Set up like this:
  1. Wheelock MT, continuous, hallways
  2. SpectrAlert, code-3, larger rooms
  3. Simplex 4903-9219, continuous, cafeteria
  4. Simplex 2903+4050, continuous, gymnasium
  5. Wheelock 31T-115, code-3, auditoruim
  6. Simplex 9001+2903-9833, continuous, regular electives
  7. Wheelock AS, code-3, bathrooms
  8. Wheelock 7002T, continuous, secondary electives
  9. Wheelock MIZ, code-3, outside near the doors
  10. Edwards 892, continuous, library
  11. EST Genesis, continuous, staff center
  12. Space Age Electronics VA4, continuous, multimedia center
I have a couple of systems.
1.Walkerville Elementary School
Panel
Edwards Custom 6500
Alarms
Edwards 8" bells doing single stroke continuous in hallways, Edwards 874-N5’s In the gym and outside(Continuous), And Edwards 892’s in the classes(Continuous).
Pull stations
Edwards 270-SPO’s
The Renovation
Panel
EST3
Alarms
Edwards Integretiys in hallways(Code 3), Edwards 4" Bells in the gym and outside(March Time), And Edwards Genesis in class rooms
(Continuous).
Pulls
Edwards 270-SPO’s And Edwards Dual action Pulls.
2.New Oaks Apartment Building
Panel
Simplex 4010
Alarms
Simplex Truealerts in the hallways(Code 3), Simplex 10" bells outside(Continuous), And Simplex GX90-4W’s in the apartments (March Time).
Pulls
Simplex T-Bars.
3.Flower Mills Food store.
Panel
Mircom FX-2000
Alarms
Mircom Select-A-Horn/Strobes Around the Grocery store(Code 3),
Wheelock MIZ in the storage room (Code 3), And weatherproof
Wheelock MTs Outside (Set to Bell).
Pulls
Mircom MS-400 and MS-700.
The Hugh S. Thompson High School in South Carolina.
  2. V33+SAE 2DCD, continuous, in-house center
  3. Gentex Commander 3, code-3, bathrooms
  4. Edward 892-2B, continuous, science labs
  5. Wheelock AS, code-3, senior center
  6. SpectrAlert Advanced, code-3, nurse’s office
  7. Simplex TrueAlert, continuous, psychologist office
  8. Wheelock MIZ, continuous, secretary suite
  9. Simplex 4903-9219, continuous, ESL Rooms
  10. Simplex 4050, continuous, computer rooms
  11. Simplex 2903+2901-9838, continuous, secondary electives
  12. Simplex 4903-9422, continuous, first electives
Robertson Middle School
Panels (tied together)
  1. Edwards Panel (unknown)
  2. Fire-Lite MS-9600
Main Alarms
Edwards 892-2B’s
Pulls
ADT 5050-001’s relabled as ESL
All Offices
SpectrAlert H12/24W set to 3000Hz Continuous
Gym
  1. System Sensor “Classic” SpectrAlerts set to Code 3 mechanical
  2. Fire-Lite BG-12L’s
Locker Rooms
Wheelock MT-24-MCW’s set to Code 3 Tone
Small Classrooms
SpectrAlert S241575 Strobes
Detention/Suspension
Wheelock MIZ horns set to Code 3
Small Meeting Rooms
Simplex 4903-9236’s
Cafeteria
SpectrAlert Advance Horn/Strobes set to High Volume Code 3 (OUCH!!)
Note: These replaced the 892’s here, in 2007, which broke.
2004 Expansion
Main Components
  1. Wheelock AS-24-MCW’s set to medium volume code 3 and strobes set to 30cd.
  2. See #2 for “Panels (tied together)”
  3. ADT BG-12LX’s
Remote Strobes
Wheelock RSS-24-MCW’s (located in bathrooms and small classrooms; 15cd)
Outdoor Signals
Wheelock ASWP’s were added all over the school
The Jeanne Shaheen Elementary School in New Hampsire.
  1. Gentex Commander 3, hallways, code-3
  2. Wheelock 7002T, library, continuous
  3. Wheelock AS, bathrooms, code-3
  4. CP MTL, resource rooms, code-3
  5. Simplex 2903+2901-9833, ESL room, code-3
  6. MA/SS, gym coaches office, continuous
  7. Wheelock MT, electives, continuous
  8. TrueAlert, OT/PT room, continuous
  9. EST Genesis, special ed rooms, continous
  10. Wheelock NS, enrichment room, code-3
  11. Mircom Select-a-Horn-Strobe, band practice, code-3
  12. SpectrAlert, teacher’s lounge, code-3
The Jackson Apartment in Jacksonville, Mississippi has the following:
Panel
EST 3 Panel and Remote Panel
Initiating Devices
EST SIGA-278
Alarms
Main Signals
Edwards Integrity Speaker/Strobes
Bathrooms
EST Genesis Remote Strobes
Apartments
Edwards Integrity Remote Speakers
Outdoor Signals
Edwards 6" Bells
Voice Evac Message
[quote] *2 Slow Whoops* There has been an emergency reported in the building. Leave the building immediately, using marked stairways and exits. Do not use elevators. *Repeats* [/quote]
Note: All strobes are synchronized
The Mills E. Godwin Jr. Junior High School in Virginia
  1. Simplex 4903-9237, continuous, hallways (except basement)
  2. Wheelock 7002T, continuous, basement hallways (the 3 floors where damaged in a fire)
  3. SpectrAlert Advanced, code-3, bathrooms
  4. Wheelock NS, code-3, gymnasium
  5. Wheelock AS, code-3, locker rooms
  6. Wheelock MT4, continuous, cafeteria
  7. Faraday U-HNH, continuous, auditorium
  8. Simplex 2901+2903-9806, continuous, band area
  9. Edwards Integrity, code-3, storage units
  10. Simplex TrueAlert, continuous, copy room
  11. CP MTL, code-3, pool room
  12. Simplex 4903-9219, continuous, conference room
  13. Simplex 4903-9846, continuous, enrichment room (which is HUGE)
  14. Wheelock MT-24-LSM, continuous, primary electives
  15. Mircom-Select-a-Horn Strobe, code-3, secondary electives
The Lucky Junior High School in Connecticut (this is where Ginger Foutley goes to school.)
Built in 1975, the panel was a Simplex 4208 set on Slow March Time.
The signals were Simplex 4050 horns on 4050-80 light plates with “FIRE” on the lens.
The pull stations were Simplex 4251-30 break-glass.
The ceiling devices were white Edwards heat detectors.
There was a 4208-style annunciator near the main entrance (pre-1979 model with red-and-black trim).
In 1999, some of the old Edwards heat detectors began going bad, so they were replaced with Simplex 2098-9201 smokes 2098-9211 bases.
In 2003, a system upgrade occurred. The 4208 was replaced with a Simplex 4005, set on Code-3.
The 4050/4050-80s were replaced with Simplex 4903-9425 TrueAlert horn/strobes, installed on metal trim plates to cover up the holes from the size of the 4050-80 plates.
The 4251-30s were mainly left intact, but a few of them broke down and were replaced with 2099-9756 dual-action pulls.
Most of the remaining Edwards heat detectors were replaced with Simplex 4098-9601 TrueAlarm smokes on 4098-9788 bases.
The annunciator was left intact.
Remote TrueAlert strobes were installed in bathrooms and in large rooms that originally did not have alarms in them.
The elementary school next door to Lucky Jr. High (where Ginger’s brother Carl goes), built in 1994, has the following alarms…
The panel is a Simplex 4002, set on March Time.
The signals are Simplex 4903-9219 horn/strobes.
Remote 4904 strobes were installed in restrooms and other places that required strobe coverage.
The pull stations are mainly Simplex 2099-9754 T-bars, with a few Simplex-rebranded Faraday Chevron pulls.
The smoke detectors are Simplex 2098-9201 smokes on 2098-9211 heads.
The DeWitt Clinton High School in New York
  1. Mircom-Select-A-Horn Strobe, code-3, hallways
  2. Wheelock MT4, continuous, computer room
  3. Wheelock NS, code-3, conference room
  4. Simplex GX90, continuous, some rooms
  5. Edwards Integrity, code-3, ESL Room
  6. EST Genesis, code-3, isolated student room
  7. Simplex 4903-9422, continuous, reading rooms
  8. Simplex 4050-85+4050, continuous, special ed wings
  9. Wheelock MT, code-3, science labs
  10. Wheelock AS, code-3 storage units
  11. Wheelock 7002T, continuous, science lab preparation rooms
  12. SpectrAlert Advanced, code-3, technology center
  13. Simplex 2901+2903-9806, continuous, copier room
  14. Wheelock MT4, code-3, book room
  15. Wheelock 7002T, staff dining room, continuous
  16. Simplex 4050-85+4040, continuous, portable building
  17. Simplex TrueAlert, continuous, gym locker rooms
  18. Faraday U-HNH, continuous, gym
  19. Simplex 2901+2903-9838, continuous, guidance office
  20. Edwards 892-2B, continuous, auditorium
The Lincoln Middle School in Wisconsin
Panels
  1. Simplex 4010 Addressable Panel
  2. Simplex 4003 Voice Evacuation Panel
Pulls
4099-9003’s
4099-9001’s in the art corridor
Hallways, Big Rooms, Gym, and Cafeteria
White Wheelock E60 Speaker/Strobes
Small Bathrooms
Wheelock square wall mount RSS’s (Red; 15cd)
Big Bathrooms
Wheelock round ceiling mount RSS’s (White; 15cd)
Entrance
Simplex TrueAlert Speaker/Strobes (4903-9357)
All Offices
TrueAlert Strobes (4904-9331)
Home Economics
SpectrAlert Speaker/Strobe
Gym Locker Rooms
Simplex 4903-9150
Medium to Small Rooms
Wheelock ET Remote Speakers
Small Rooms
Wheelock RSS’s (15cd)
Outdoor Signals (Recently Added)
System Sensor | Honeywell Building Technologies SpectrAlert Advance SPSRK Speaker/Strobes
Addition for next year (2008-2009)
SpectrAlert Advance Speaker/Strobes and SpectrAlert Advance Remote Strobes in the bathrooms.
Voice Evacuation Message
[quote] *Slow Whoop 2x* Attention, attention, attention! An emergency situation has been detected in this building. Proceed to the nearest exit and leave the building. Do not reenter the building, until directed to, by the proper authorities. *Message repeats two more times* *Cycle Repeats* [/quote]
The John Branch Jr. Elementary School in South Carolina. Split into 2 buildings. The main building and overflow building and the only way to get there is to go through a walkway under the ground in the basement.
  1. Both buildings have Mircom-Select-a-Horn/Strobes set to Code-3
  2. The computer lab in the main building has a Simplex 4903-9237 set to continuous
  3. The cafeteria has Edwards Integrities set to Code-3
  4. The library has an EST Genesis horn set to Code-3
  5. The resource room in the overflow building has an Edwards 892-2B horn on continuous
  6. The assembly room has an Edwards 792-00B horn set to continuous
  7. Some of the larger rooms in both buildings have Gentex SHGs set to continuous
  8. Both bathrooms in the overflow and the main building have Edwards 792-7A-005 horns
  9. The OT/PT room located in the overflow building has a SpectrAlert ceiling mount advanced set to Code-3.
  10. The elective rooms have Simplex 2901+2903-9838 horns.
  11. The literacy room in the overflow building has a Simplex 4903-9219.
  12. The ESL room has an older Wheelock AS on Code-3.
  13. The gymnasium has a Wheelock 7002T horn on continuous for the main building
  14. The overflow gym, on the other hand, has a Simplex TrueAlert
  15. The main atrium in the main building has a Simplex 2901+2903-9833.
OK, here’s a new one.
Name of School
Daniel Grove School (K-8)
Panel
http://www.firelite.com/products/ms10ud.html Fire-Lite MS-10 (Originally an MS-4424B system)
Pulls
  1. Fire-Lite BG-10L’s
  2. Fire-Lite BG-10 hex locks located in one hallway
  3. Fire-Lite BG-12 that replaced one of the hex lock BG-10’s (see bottom of this post for the story)
Alarms
Located in art rooms, technology room, gym, boiler room, some bigger classrooms, and the library
Wheelock 34T-24+WS-24’s
The remaining bigger classrooms, most hallways, and medium-sized classrooms
Wheelock MT-24-LSM’s (Continuous)
Locker rooms
MA/SS alarms set to 800Hz steady
Replacing some of the MT’s
Wheelock NS-24-MCW’s (code 3)
Bathrooms near the 1st, 2nd, 5th, and 8th grade hallways
Wheelock LSM strobes
Bathrooms near the Kindergarten, 3rd, 4th, 6th, and 7th grade hallways
Small Rooms
Wheelock MIZ-24-LSM
Outdoor Signals
SpectrAlert Advance P2RK horn/strobes set to High Volume Code 3
The Story
One day, one of the Hex-Lock BG-10’s had it’s hex “terminal” (IDK what you call it) drop loose, making the BG-10 35% loose causing the alarms going off. When the alarms went off, the students and teachers didn’t know what happened. Then the principal said “One of the pull stations broke loose”. Then the fire department came to check for fires, but they found out about the pull station accident. One day later, they had to open the slightly defective BG-10, and before they did, the principal told everyone in the building to disregard the fire alarms. They opened it, alarms went off, the people at the panel were ready to silence the alarms, then the alarms stopped ringing. Then they did something very odd to it. They put lots of duct tape over the contact, which worked very well. And on the layers of duct tape shows the following written in blue pen:
DO NOT REMOVE ALL OF THIS DUCT TAPE!! REMOVING ALL THIS DUCT TAPE WILL SET OFF THE FIRE ALARMS!!
Three school days later, they contacted Fire-Lite for a replacement pull. The next day (they had a planned fire drill that day), Fire-Lite came and replaced the “slightly defective” BG-10 (and the duct tape) with a brand new Fire-Lite BG-12 pull station. Why would they open the pull station and put duct tape over the contact?!
The John Smith high school was built in the late 1920’s. Old Faraday bells and Gamewell pulls were installed. In 1958, a new school district formed. It became the Bob Jones Junior High school. In 1968, some of the bells began to malfunction after a power surge, and were replaced with Edwards Vibratone horns.
In 1976, the school was remodeled and received a new addition. The Faraday system was removed, and a new Simplex 4208 system with 4050 horns and T-bar pulls was installed. Three non-operational Faraday bells still remain in the basement of the school, as well as a few Gamewell pulls that remain functional. In 1981, lighting struck part of the school. Damaged 4050’s were replaced with 2903+4050’s, and some T-bars were replaced with 4251-30s break-glass T-bars. In 1988, an outdoor horn got smashed by a football. It was soon replaced with a Simplex 6" vibrating bell.
In 1989, the school closed. Vandals broke some of the 4050’s and smashed the main panel. The school reopened in 1993, becoming a middle school. It received another addition and some minor remodeling. A new Simplex 4005 panel was put in, along with 4903 horn/strobes. Five 4051’s and two 4050’s still remain. The 6" bell was replaced with a Wheelock MT-24-LSM set to Code 3.
In 2001, a section of the school was torn down, and the school received a major new addition, bringing a new gym, cafeteria, and classrooms. Two of the old Faraday bells were removed, and 3 of the 4051’s were nixed as well. TrueAlerts and T-bars were installed, and tied in with the 4005. Due to complaints of kids not hearing the alarm, Wheelock MIZ horns were installed in all of the classrooms. In 2003, some idiots broke two TrueAlerts in a hallway. Vandal-protective grills were installed in front of the TrueAlerts, and Stopper covers were installed over most of the T-bars. In 2006, three Wheelock RSS strobes and another MT-24-LSM were added outside.