This is Rincon/University High School Campus, this serves Rincon High, a Tradational High School, and Univesity High, a Seperate Accelerated Insituation. The Campus usually has around 2600 People in it total.

(Last Updated 4-22-2026)

Here is some History.

The school was built in 1958 as Rincon High with a 4 Buildings and a Powerhouse building. Univesity High came later.

There was a Pull Rod System of some sort in the school at this time, (Since there seems to be remnants of a Pull System), This System contained IBM 4030-2B Bi-Directional Horns (Paired with IBM Time Clocks, some of which still exist on campus). This system was installed the same year Simplex bought IBM’s Time Division, so this campus has been a Simplex system for its entire history.


The school, In 1958.


A Hallway in the school, Note the Red Horn near the end of it. (Circa 1970s/80s, remastered with AI.)


Simplex 4030-2B Horn in the Choir Room, 1968. A 4903-9237 has taken its place.

The Oldest device I have seen is a Simplex 4262-5 ionization smoke detector. Which was probably a holdout of this Old system. These are also present in the Air Handling units in the school’s Tunnels.

Simplex 4262-5 Smoke Detector, In the Library

After the construction of the North Gym and Auditorium, nothing really changed.


Areal Shot of the North (Right) and South (Ahead) Gyms, Circa 1967.

In 1985, University High School was moved to this Campus, thus creating RUHS.


In the Late 80’s/Early 1990s, my school district installed a replacement system(s) that Contained 4251-30 Pull stations, 2908-9201 and Wiffle Ball Smoke Detectors, and 4903-9101 Strobe Plates with 2901-9806 Horns, set to Continuous.

3 Bay 4002 Fire alarm Control Panels for controlling each respective building .(3 have been Identified). They were networked into a Simplex 2100 or 4100 Master Panel via Control and Monitor Modules on an SLC. This was done because of the existing zones from the original system, rather than making the entire campus addressable. The panel was then replaced with a 4100U in the 2000s. The Panel was then Upgraded to a 4100ES on 8/3/2026.


A 4903-9101/2901-9806 in the U Building.


Subpanel “F”, a Simplex 4002, which covers 3 large buildings with only 8 zones…


The Master 4100U in the Office


A 4903-9101/2901-9806 in the library (U Building.)


A 4903-9101/2901-9806 in the T Building.


A 4251-30 With the Break Glass Handle removed, over half of the pull stations in the school are like this.


A 4903-9101/2901-9806 in the Auto Shop (T Building)

Simplex 4002, Subpanel “D” controlling the Cafeteria and T Building.

In 2001, my district built rebuilt the Fine arts Part of the school. Reconstructing the band/choir Room, Little Theater, and the Auditorium.

These devices are 4903-9237 (Or Similar) Horn Strobes, and 4099-9003 Pull Stations, connected via a 4009 tied to the existing 4002’s.


A Simplex 4903-9237 Horn Strobe in a Cage Protector.


A Wheelock AH-24WP-R Outside the Band Room.



The Language Building, Built with the 2004 Bond Project, with the Smokestack of the Powerhouse/Engineering Building behind it.

In 2008, my school received a New Language Building, and rebuilt Science Classrooms. These Classrooms contain Wheelock NS’es, RSSes (Via a 4009 in the U Building), and Simplex 4099-9003 Pull Stations, With True Alarm Smoke/Heat Detectors out and about. Instead of connecting to the U Bdlg Subpanel, It was worked into the Master Panel SLC.



Wheelock NS and Simplex 4099-9003 in a newer Science Classroom.


A Wheelock NS in a Bathroom in the Language Building, Apparently, they have these at Concessions, too. Don’t want to be in here during a drill.


There is an ongoing issue with remote control of some sub-panels. Therefore the 4002 Subpanels will be replaced with ESNet compatible panels, if that will be a 4100ES, 4010ES, or 4007ES. When this will happen is still not yet known.

This system has some Oddities, for example, it has Wheelock 7002ts and Edwards 270 Pulls in the ELA Portables (Part of the T Building System, not the Portable System) (These Portables have been demolished as of June 15th, 2026. I will ask Administration where these devices went.)

It also has a Model L Siren Attached to the Auditorium. I’ve Never Heard it Go Off, and its just sitting there. Its fate remains Unknown, my hopes are to restore it.


System List
(NEW!! See this System in Action!)
U Building

  • Simplex 4002 3 Bay Fire Alarm Control Panel
  • Simplex 4009 NAC Extender (For Science Rooms)
  • Simplex 4903-9101 Strobe Plates
  • Simplex 2901-9806 Horns
  • Simplex Wiffle Ball Smoke Detectors.
  • Simplex 4262-5 Smoke Detector (Library Only)
  • Simplex 2908-9201 Smoke Detectors
  • Simplex 4251-30 Break Glass Pull Stations
  • Simplex 4251-20 Metal Handle Pull Station (Basement)
  • Simplex 4904 Strobes (Restrooms)
  • Wheelock NS Horn Strobes (Science Rooms)
  • Wheelock RSS (Some Science Rooms)
  • Simplex 4099-9003 Pull Stations (Science Rooms and Replacements)
  • Simplex TrueAlarm Detectors (Science Rooms)
  • Federal Signal Model 9B (Outside)

Administration Building

  • Simplex 4100ES Fire Alarm Control Panel (Master Panel, Replaced Simplex 4120 Classic CPU)
  • Simplex 4903-9101 Strobe Plates
  • Simplex 2901-9806 Horns
  • Simplex Wiffle Ball Smoke Detectors.
  • Simplex 4251-30 Break Glass Pull Stations
  • Napco Starlink Communicator

Cafeteria Building

  • Simplex 4002 3 Bay Fire Alarm Control SubPanel
  • Simplex 4903-9101 Strobe Plates
  • Simplex 2901-9806 Horns
  • Simplex Wiffle Ball Smoke Detectors.
  • Simplex 4251-30 Break Glass Pull Stations

Auditorium

  • Simplex 4002 3 Bay Fire Alarm Control SubPanel
  • Simplex 4009 NAC Expander (Primary A/V Driver)
  • Simplex 4903-9237 Horn Strobes
  • Simplex 4099-9003 Pull Stations
  • Simplex 4903-9101 Strobe Plates (Basement and Upper Lights)
  • Simplex 2901-9806 Horns (Basement and Upper Lights)
  • ETC ELTS (Emergency Lighting Transfer Switch), (Connected to System)
  • Federal Signal Model L (Outside Auditorium)

Science Labs Building

  • Simplex 4002 3 Bay Fire Alarm Control Panel
  • Simplex 4099-9003 Pull Stations
  • Gentex SHG
  • Simplex 2901-9838 (Dead)

T Building

(Controlled Via Cafeteria Sub Panel)

  • Simplex 4903-9101 Strobe Plates
  • Simplex 2901-9806 Horns
  • Simplex Wiffle Ball Smoke Detectors.
  • Simplex 4251-30 Break Glass Pull Stations
  • Simplex 4251-20 Metal Handle Pull Station

South Gym

  • Simplex 4002 3 Bay Fire Alarm Control SubPanel
  • Simplex 4903-9101 Strobe Plates
  • Simplex 2901-9806 Horns
  • Simplex Wiffle Ball Smoke Detectors.
  • Simplex 4251-30 Break Glass Pull Stations
    (Have not been there much)

Snack Bar/Training Building

(Connected to S Gym Panel)

  • Simplex 4903-9101 Strobe Plates
  • Simplex 2901-9806 Horns
  • Simplex 4251-30 Pull Stations
  • SImplex 2099-9756 Pull Stations
  • Simplex 4906-9101 Strobe
  • Simplex 4906-9217 Horn Strobe
  • Wheelock NS Horn Strobe

North Gym

  • Simplex 4002 3 Bay Fire Alarm Control Panel (Assumed, To be replaced by an ESNET Panel )
  • Simplex 4903-9101 Strobe Plates
  • Simplex 2901-9806 Horns
  • Simplex Wiffle Ball Smoke Detectors.
  • Simplex 4251-30 Break Glass Pull Stations
  • Simplex 4903-9237 Horn Strobes (Band Room Extension)
  • Simplex 4099-9003 Pull Stations (Band Room Extension)
  • Simplex 4904 Strobes (Band Room Extension)
  • Wheelock HS-24-R (Outside)

Language/Ampitheater Building

  • Simplex 4010 Fire Alarm Control Panel (Assumed since it is connected to the Network, which is the only panel the 4120 supports that is from the same time frame.)
  • Simplex 4099-9003 Pull Stations
  • Wheelock NS Horn Strobes
  • Wheelock RSS Remote Strobes
  • Simplex TrueAlarm Detectors

Portables
(This system is independent from the Legacy 4002/4120U Network and is connected on its own network run. These Buildings have been moved to the opposite end of Campus to make way for the new Building, with the devices remaining. They are Controlled Via Cafeteria Sub Panel)

  • Simplex Smartsync TrueAlerts
  • Simplex 4099-9003 Pull Stations
  • Simplex 2901-9838 Horns
  • Simplex 4009 (Tied to T Building)

After the Passage of the District of the 2023 Bond project, the district will be installing a new 3.5 million Dollar Fire Alarm System for this High School in the next 10 years. Currently, the school’s priority is HVAC. It will most likely be a Simplex Voice Evac System with Wheelock Devices (From what other High Schools in the district have), but it’s unclear. Most likely the 4002s will be replaced with 4100ESes with Voice Capability, but the network will remain. The school will also get a new building in 2027.

1 Like

See if you can save the old devices!

That’s a rebranded Statitrol detector: the same kind formerly in the Davis K-8 school in fact (which is the kindergarten school @wiley209 used to go to).

The 4903-9101 + 2901-9806 combos are definitely unique: most of the time 2901-9838s would be used with those strobe plates instead.

You didn’t put a caption for the one pull station photo, but that’s a 4251-30 with the break-glass frame removed.

The TrueAlert-series was supposedly introduced in 2001 so why the installers would have used 4903-series devices I have no idea (unless Simplex didn’t discontinue the 4903-series right away).

That’s an odd choice if you ask me, moreso in that it’s an HS-series horn & not an MT-series horn.

One word: headache.

Hmm, wonder what that would be used for (unless it’s the outdoor fire alarm signal, & even though such a thing might seem overkill at first a campus that large might need something that loud for adequate exterior warning).

Indeed: always good to do if you ask me.

Oops, but yea. Thats a 4251-30 In the North Gym.

I suppose Old Stock, but I am only assuming the building age by the design, (As these have no Records that I have Access to) it also could be late 90s, as it gives that vibe as well.

There are Cold War Era Bunkers under the Auditorium, U Building, and the North and South Gym. That Siren is close to a Bunker Entrance for the Auditorium, So I assume it was used for Civil Defense Drills of some sort.

It Looks Disconnected for a while, so idk…

I was told that there are tunnels between Buildings as well.

Its a gamble of Hope, as we don’t know when the Fire Alarm System is planned to be replaced. I think that the Mechanical Horns will be replaced with speaker strobes, but I think the NSes might stay, because they are newer and meet ADA requirements. The Bond project was voted in on the 7th, so Its going to be a while.

The 4903 series remained available for a long time (it might even be available today!)

1 Like

This looks like a metal version of an sd355

Yeah.

Ah, yeah, that might be it.

Really? I honestly figured that Simplex would have largely discontinued it once they introduced its successor the TrueAlert-series (though you are right about that last part: Simplex still sells 4903-series devices, albeit with TrueAlert horns in them, supposedly to be used as replacements for older/original 4903-series devices (along with I think some ceiling-mount applications).

It’s not: heck Statitrol made those detectors decades before the SD355 would even be designed.

1 Like

I know, I am just saying that it kind of reminds me of the sd355 a bit. Also it reminds me of one of the types of in building antennas. Something like this: Galtronics 02121304-05491U 380-6000MHz Broadband In-Building Antenna (02121304-05491U) | Solid Signal

Yea, Thats why I second Guessed that it was a smoke detector.

Gotta love TUSD and their diverse systems! Let’s hope it doesn’t go off as much as my schools system!

1 Like

After Digging Deep, I found this image from 1960 of the hallway.
Screenshot 2023-11-17 212323

Is that Black speck (Towards the end of the hall) A horn? Or am I seeing things.

Im still looking for more pictures, but whatever it is, its long gone now…

It could have been a bell the school would use for class change.

for sure wheelove fire alarms did a vid on that

Do you mean fallout shelters? In the cold-war they did not have bunkers because if you were anywhere near the spot you would certainly die, but the shelters were designed to protect from nuclear fallout hundreds of miles away from the spot.
The shelters would have signs like these
IMG_7061
Not my photo

1 Like

Yes, I meant a Fallout Shelter, “Bunker” is the term used by staff and Students, so I went with that.

And since the Fallout Shelters were designed for the just the school and not for public use, those signs were never there.

A reddit post from years ago that mentions this:

Update: Found a 4002 In the Cafeteria Building (Staff Lounge area). I’m assuming the system is now networked. Or each building has their own panel.

Hope I can save that panel…

With bond being passed, when should be able too.

Let’s hope I can get the system at TMHS!

Update: I have found another 4002 in the Auditorium Building (The Non-Condemned Section) and I realized there are RARE 3 THREE BAY 4002’s, which surprised me. I am assuming there are 4002s for the U and T Buildings as well as both gyms. I think a 4008 or 4006 is in the Language Building, but I’m unsure.

Sadly the 4002’s aren’t red, but If I’m able to salvage the system, Ill strike gold…

I will get pictures when I can, but that may be in January.

By watching your videos, I can confirm that this is NOT a 9237. u liar
This device sounds like a 9219 or something along those lines. The 9237 would sound like a truealert and it doesnt. Just some “Clarification”

No need to get mad at him and say “u liar” over a simple mistake.

2 Likes